Default FP Panel/EC CABLE

Issues with EC cable, any suggestions?
Also, FP panel can't find bonding strap? Also, what are the issues with these panels, are they not safe? And should they be replaced?

Attachment 2764

Attachment 2765

Attachment 2766

Attachment 2767



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 4/11/06 at 8:45 PM..
Reply With Quote
  #2  
Old 4/11/06, 6:38 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: FP Panel/EC CABLE

Gary,

Based on that SE cable I would say right away DEFER it to an Electrical Contractor.....and possibly could have saved alot of time since it has a FP panel to defer the entire electrical for an electrical contractor to take over and remove possible missed things.

On the Cable...most certainly needs replacement ASAP.....on the FP panel...not un common to find no bonding on these old panels....in many case when i see this they actually did the bonding at the meter can...not to say this is done here.....

Were you not able to find a solid ground # 4 going from this panel to a water pipe....

Now if you ever want to.....SOME WILL CRINDGE....but I trust you...take a volt meter and put it on OHMS..or if it has a contin. feature...put one end into the mounting screw holes and the other touch the neutral bar and see if they RING out.........

Ok...Ok......so someone will say probing in the panel is not allowed....sure it is not or does not need to...BUT if you really want to see if the neutral bar is bonded to the case.....try it......

Now...if bonded to the enclosure....still does not mean their is a ground present....if you can't see it in the panel.....check at the meter base...if you can't see it their...NOTE you cant see it......and defer.....defer...defer...

Hope this helps



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #3  
Old 4/11/06, 6:56 PM
Gary Schering, II's Avatar
Gary Schering, II Gary Schering, II is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 695
Default Re: FP Panel/EC CABLE

Paul, Also this panel is rated for 100amp. This is a split panel. The top half has 100 plus 50 for the bottom half. This is maxed out correct?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #4  
Old 4/11/06, 7:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: FP Panel/EC CABLE

Quote:
Originally Posted by nbhi
Paul, Also this panel is rated for 100amp. This is a split panel. The top half has 100 plus 50 for the bottom half. This is maxed out correct?
That's irrelevant Gary.

I can't offer anything else 'cuz I see no pictures. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 4/11/06, 7:17 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: FP Panel/EC CABLE

Gary,

I have to agree in that if I were you I would defer and keep the expanded electrical comments from the client....not because you don't know because you do.....but because it raises additional liability.

As for the capacity of the panel, just being full never means it is at capacity....I most certainly can work ways around that little space issue.

In order to be able to tell someone a panel is at capacity they are going to have to physically do the MATH......calculate the loads and work of the SE profile to know what the draw is on this panel.....so I would defer...heck I will come and check it out for ya......lol..want me to look at it when I am up their in 2 weeks...thehehe...

No actually.....you could say because it is all filled and only a 100A panel that it would be in their best interest to consider a 200A upgrade in the future at which time will remove and replace the FP panel which has known issues that are documented.

Again...being MAXED out is a concept of doing the physical math and and figuring based on the loads present...not just from lack of space....however lack of space is also a issue....nothing a redesigned SUB PANEL..or as Gerry likes to call them...Distribution Panel can't solve.....

Hope this helps



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 4/11/06, 7:19 PM
Gary Schering, II's Avatar
Gary Schering, II Gary Schering, II is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 695
Default Re: FP Panel/EC CABLE

Jeff, can you see the pic's know?Attachment 2768

Attachment 2769

Attachment 2770

Attachment 2771



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 4/11/06 at 8:45 PM..
Reply With Quote
  #7  
Old 4/11/06, 7:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: FP Panel/EC CABLE

Nope.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 4/11/06, 7:21 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: FP Panel/EC CABLE

really....you cant see those.....wait..didn't you say jeff you were having issues seeing images on the boards a few weeks ago.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 4/11/06, 7:24 PM
Gary Schering, II's Avatar
Gary Schering, II Gary Schering, II is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 695
Default Re: FP Panel/EC CABLE

What can i do different Jeff?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #10  
Old 4/11/06, 7:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: FP Panel/EC CABLE

I can't see pictures that are "attached" in the body of the message using the "ATTACH" code. Only those that are inserted using the "Attachment Manager."

I've asked Chris several times about this with no reply whatsoever, so I gave up.

I usually just skip the posts where pics are attached this way. . .

Don't worry about it Gary, I'm sure Paul covered it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 4/11/06, 7:29 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: FP Panel/EC CABLE

ewww...thats not good........I like your comments on things and on images would possibly bring up some nice chats....

Are you sure you looked into your settings to see if you possibly blocked out attachments or anything in the settings...very strange..anyway I hope you eventually get it worked out.....

CHRIS....WAKE UP...........WAKE UP>>>>>>



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 4/11/06, 7:34 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: FP Panel/EC CABLE

It's possible that it is in my settings, but I'm not willing to compromise my systems to view this board (there was never a problem with the previous board) and there are many issues with this new board that are no longer compatible with my system.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 4/11/06, 7:34 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: FP Panel/EC CABLE

lol....I removed these links....lol.....no need for them NOW....

Gary....just use the Go Advanced button and choose the manage attachments feature to upload images....then jeff can view them...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 4/11/06 at 7:47 PM..
Reply With Quote
  #14  
Old 4/11/06, 7:37 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: FP Panel/EC CABLE

Those I can see.

I can always see them when they are attached like this one. . .
Attached Thumbnails
fp-panel-ec-cable-hpim6220.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #15  
Old 4/11/06, 7:45 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: FP Panel/EC CABLE

I get it now.......As long as they are uploaded you can see them...Cool....Gary...you are just posting them wrong...thehehehhee....

But I do have to admit...I like seeing the large image of the item when you click on the picture...thehehe...makes it easier than the smaller images...

Update- Jeff's does also....DANG...I give up.......I will stick to Electrical Issues....leave the computer stuff alone...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 4/11/06 at 7:49 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Interesting article from U/L on armored cable Greg Fretwell Electrical 18 2/27/07 10:02 PM
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical 5 2/16/07 1:19 PM
Did you KNOW this about NM Cable? pabernathy Electrical 0 12/19/06 9:46 AM
Hey Joe Tedesco pbolliger Electrical 7 4/11/06 1:17 AM
Ceilings falling with wires in it. jsmith3 Interior 8 3/16/06 8:24 PM


All times are GMT -4. The time now is 3:34 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts