  #1  
Old 7/14/06, 2:51 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,492
Send a message via ICQ to kshepard
Default FP Stab-lok panel: updated breakers?

House was built in 1985. Federal Pacific Stab-lok main panel, no signs of overheating and warmest breaker was 70 degrees (same as the home interior).
I could not read these tiny labels. Are upgraded breakers available for these panels? If so, might these be examples?

Just noticed too, that looks like a 12 g. wire in a 30 amp breaker.

Last edited by kshepard; 10/2/08 at 2:40 AM..
Reply With Quote
  #2  
Old 7/14/06, 3:00 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FP Stab-lok panel: updated breakers?

Quote:
Originally Posted by kshepard
House was built in 1985. Federal Pacific Stab-lok main panel, no signs of overheating and warmest breaker was 70 degrees (same as the home interior).
I could not read these tiny labels. Are upgraded breakers available for these panels? If so, might these be examples?

Just noticed too, that looks like a 12 g. wire in a 30 amp breaker.
Stab-lok is still manufactured in Canada and I guess about 40 % of new homes are stab-lok .
Do not know if they are any different then what you have in the USA
but they do not seem to be a concern here or a problem.
It is the same company who makes SQ. D.
http://www.schneider-electric.ca/www...-lok/index.htm

Roy Cooke sr ... Royshomeinspection.com
Reply With Quote
  #3  
Old 7/14/06, 3:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: FP Stab-lok panel: updated breakers?

There are breakers manufactured as "replacement" breakers for FPE Stab-lok load centers - they are specifically listed as replacement breakers and cannot be used (according to the listing) for new installations.

In any event, there are more issues with Stab-lok load centers than just the breakers. The design is inherently flawed and the contacts are easily damaged during installation.

If the FPE panels in Canada are the same Stab-lok design, they would be subject to the same potential issues although the breakers may be better than the originals (with regard to their failure rate).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 7/14/06, 4:05 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 2,027
Default Re: FP Stab-lok panel: updated breakers?

Canadian FPE Stab-Lok panels

FPE Stab-Lok panels in general

Appears there are still problems regardless of where and when they are manufactured...
Reply With Quote
  #5  
Old 7/16/06, 1:31 AM
Joey D'Adamo Joey D'Adamo is offline
New User
 
Join Date: Aug 2004
Posts: 38
Please Note: Joey D'Adamo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FP Stab-lok panel: updated breakers?

Quote:
Originally Posted by jpope
If the FPE panels in Canada are the same Stab-lok design, they would be subject to the same potential issues although the breakers may be better than the originals (with regard to their failure rate).
The bus design appears to be the same. However, I think the problem with the bus stems from the popularity of the half-size (0.5" sp/1" dp) breakers that are/were available for these panels. In my eyes the problem is that a lot of the half-size breakers wiggle a lot even with the cover on. I think the "stab" part of the breaker connection on the half-inch breakers is pretty poor. I think it gets even worse when you have high amperage 240V circuits using the 1" double pole breakers. In fact it is possible to install those breakers to the same phase because of how the bus is designed...kinda funny. I will note, however, that the bus stab mechanism for the full size breakers (1" single pole/2" double pole) is SIGNIFICANTLY better.

Aside from a recall of some 1996 FPE breakers, the FPE stuff isn't exactly generating much press up here.

My favorite breaker panel design of all time is the Sylvania/GTE panels. The breakers actually screw into the busbar. No concern of them ever falling out when taking the cover off, and as long as the screws are tight, the connection is good. Those were very popular here in homes built in the late 70s-early 80s. These were also branded up here as "Commander" and a few others.
Reply With Quote
  #6  
Old 7/16/06, 8:46 AM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FP Stab-lok panel: updated breakers?

Quote:
Originally Posted by Joey D'Adamo
T

My favorite breaker panel design of all time is the Sylvania/GTE panels. The breakers actually screw into the busbar. No concern of them ever falling out when taking the cover off, and as long as the screws are tight, the connection is good. Those were very popular here in homes built in the late 70s-early 80s. These were also branded up here as "Commander" and a few others.
Most companies manufacture bolt in style panels. Because of the higher cost they are not often used in residential applications. But they are pretty much the standard in commercial/industrial installations.
Reply With Quote
  #7  
Old 7/16/06, 11:53 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: FP Stab-lok panel: updated breakers?

Quote:
Originally Posted by Joey D'Adamo
Aside from a recall of some 1996 FPE breakers, the FPE stuff isn't exactly generating much press up here.
I know of no recalls with regard to FPE breakers or panels.

I looked at the link provided by Roy, and I can see that there have been some changes, at least to the "stabs" on the breakers.

These used to be split so that there was a "spring" effect when snapping them in. It appears that these contacts are solid now, which would be a better design.

The split contacts were easily damaged during installation which was one of the big problems with their design.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Federal Panel: test the circuit breakers? fbartlo Electrical 8 4/30/07 2:18 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bryant Panel and Gould Breakers tneumann Electrical 27 4/28/06 9:04 AM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 11:26 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts