Default FPE Angst

Howdy

The FPE panel issue is one that has me frustrated. What exactly are HI's stating about FPE's?
Reply With Quote
  #2  
Old 1/15/06, 12:25 AM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FPE Angst

I work for a company that owns about 3000 aparments all over southern N.H. and northern Ma. and 90% of them have FPE panel. in the 5+ years of maintaining them, i've not noticed anything more than "tipical" issues common in ANY panel not just FPE. just the occasional bad breaker and such. personaly i just note the general conditions and any issues as i would for any brand. i know others have had bad tastes left behind from FPEs. but then again i think Budwiser taste awfull, what do i know.
Reply With Quote
  #3  
Old 1/15/06, 6:20 AM
lewens's Avatar
lewens lewens is offline
Active Poster
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 775
Send a message via AIM to lewens
Please Note: lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FPE Angst

See what I mean?
Larry
Reply With Quote
  #4  
Old 1/15/06, 10:58 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: FPE Angst

I personaly would like to see a FPE & a Zinsco pannel photo side-by-side.

I would like to see a FPE & Zinsco braker side-by-side also.

This way I would know what each would look like. I kan reed? I would like to see them just to compair their looks. Due to the QOD 1-14-06. I have seen FPE but have yet to see Zinsco in my neck of the woods.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #5  
Old 1/15/06, 12:42 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: FPE Angst

My standard. . .

Quote:
The home is equipped with a Federal Pacific Electric (FPE) Stab-Lok brand electrical panel. FPE products are considered problematic by industry professionals due to their high failure rate as documented by the Consumer Products Safety Commission. Failure of any component within the electrical system may result in fire and/or electrocution.


The design of the Stab-Lok breakers is flawed (subject to damage during installation). These breakers have been documented to fail to open under overload conditions.

Here are a couple FPE pics. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 2/28/07 at 4:15 PM..
Reply With Quote
  #6  
Old 1/15/06, 12:48 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: FPE Angst

Jason,

Ask and you shall recieve.

Quote:
Originally Posted by jsieg
I personaly would like to see a FPE & a Zinsco pannel photo side-by-side.

I would like to see a FPE & Zinsco braker side-by-side also.

This way I would know what each would look like. I kan reed? I would like to see them just to compair their looks. Due to the QOD 1-14-06. I have seen FPE but have yet to see Zinsco in my neck of the woods.
The Pictures below are taken from the training course that I will be delivering at the NACHI convention next month.

Regards

Gerry
Attached Thumbnails
fpe-angst-fpeslide1-small-.jpg.jpg
Views:	103
Size:	57.1 KB
ID:	503   fpe-angst-zinscoslide1-small-.jpg.jpg
Views:	103
Size:	66.2 KB
ID:	504  



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #7  
Old 1/15/06, 12:51 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: FPE Angst

Nice pics Gerry. Here are a couple more Zinsco pics. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 2/28/07 at 4:15 PM..
Reply With Quote
  #8  
Old 1/15/06, 12:59 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: FPE Angst

Quote:
Originally Posted by jpope
Nice pics Gerry. Here are a couple more Zinsco pics. . .
Thanks Jeff, the copper bus pic is I believe one of your's I will go back into the slide and acknowledge it as such, funnily enough I think I have used 3 other of yours in the presentaion.

I pinch all my best Zinsco's from you thank you for allowing me to use them in this way.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #9  
Old 1/15/06, 1:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: FPE Angst

My pleasure Gerry. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 1/15/06, 9:45 PM
jcundiff's Avatar
jcundiff jcundiff is offline
Active Poster
 
Join Date: May 2005
Location: Fairview Park, OH
Posts: 251
Please Note: jcundiff is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FPE Angst

Jeff- I like your standard statement- citing the cspc is a good way to validate the concern without stating that they have been recalled or they do not meet code.
Reply With Quote
  #11  
Old 1/16/06, 12:24 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: FPE Angst

That's really the point. Because they have not been recalled and compliance is not my job (even though there is no code that says FPE is not allowed).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 1/18/06, 12:49 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: FPE Angst

Quote:
Originally Posted by gbeaumont
Jason,

Ask and you shall recieve.



The Pictures below are taken from the training course that I will be delivering at the NACHI convention next month.

Regards

Gerry
Thank You Very Much Gerry, I like the look of the slides. You can tell that you have put a lot of time into them.




Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #13  
Old 1/19/06, 12:34 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: FPE Angst

The home was equipped with a Federal Pacific Electric (FPE) Stab-Lok brand service panel. FPE components are considered problematic by industry professionals due to their high failure rate as documented by the Consumer Products Safety Commission. Failure of any component within the electrical system can result in fire and/or electrocution.
Recommend evaluation by a licensed electrician to determine safety, integrity, and performance of the service equipment.

For information about the Federal Pacific Electric breaker panel see information at
: http://www.cpsc.gov/cpscpub/prerel/prhtml83/83008.html

I like to direct the client to cpsc site and let them understand where I'm
coming from...if they want to.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #14  
Old 1/19/06, 6:11 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FPE Angst

Look here:

Russell Kirk asked a question about Zinsco's and the replies are very interesting.

http://inspectionnews.com/ubb/Forum4/HTML/000111.html
Reply With Quote
  #15  
Old 1/19/06, 6:14 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: FPE Angst

Quote:
Originally Posted by jwilliams4
Recommend evaluation by a licensed electrician to determine safety, integrity, and performance of the service equipment.

.
Ok....As Jay has stated......I also see ALOT of FPE panels and I have to tell you some I see are in great shape, installed with care and look very clean. Now, their are known issues of the FPE breakers not tripping in an overload situation.....and it has been noted....BUT...

I also have been doing this for 18 years...I have seen Square D's, Cutler Hammers, GE's and others who have the same issue doe to improper installation, faulty grade equipment ( ie:broken breakers which should not have been installed in the first place ) and so on.

As a Electrician I know that upon my evaluation I can determine with both temp tests, breaker review, stablock review and terminal block review how to recommend a panel be replaced or not...this is why you refer to electricians guys.....Now as a HI....well...wait...I do those things also which are beyond the scope but because I can offer the enhanced inspection...But if I didn't then I would note concerns that stick out....which will PROMPT further evaluation because of it....and I am talking small things....today I did a HI and the electrical panel has a # 8 AWG CU to the ground rod.....so what do you guys think I said since you know I can't fix it because I inspected it.....

Oh did I mention I pulled on the ground rod and it came up out of the ground...was cut off at 2 feet long....sorry forgot that part......

Point is.....if you see a FPE or Zinsco.....I can almost bet you will see some other violation that prompts more review...ie the bonding, grounding, connectors, open knockouts...you name it....double tapping and so on...so in my opinion for HI's...Less Is Best.....Pick out the Obvious violation of safety and refer it to a specialist in the feild......Remove the liability.

Oh....do I like FPE's.....I am waiting for someone to ask me that...NOPE....but I really have to tell you....when I look at FPE or the few Zinsco's ( nothing like Jeff See's ) I recommend them to be reviewed...but in all cases I find other supporting things to refer with it to justify it and if I am the electrician the HI ( my friends in the business refer to me ) I check every aspect of the unit...I even remove the breakers to check them......just my thing.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 5:35 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts