Had a call from a client that just moved in to their condo. He said the a/c wasn't working and the lights were flickering or dim in parts of the home. He then told me he checked all the breakers and the breaker for the outside compressor unit but didn't know what to do next. I asked him if he checked the outside main. He said "no, I will go look"

He called me back and said smoke was pouring out of the access when he opened it.

The power co came out to look and informed him the clips on the meter base had spread from heat and were arcing and the heat was cooking the wires to the main shut off. The guy bent the clips back but said its days were numbered.

I did write this up as when I looked at it a few weeks back and said it told him since it was an fpe it should be evaluated for replacement. The covers had long since dissapeared. Now everyone get a new main, yeah!
Attached Thumbnails
fpe-breaker-didnt-trip-489-c01.jpg  




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/12/11, 9:33 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FPE breaker that didn't trip

That stuff looks like it's gone beyond it's expiration date.
Reply With Quote
  #3  
Old 7/13/11, 5:27 PM
Jamie R. Wilks's Avatar
Jamie R. Wilks Jamie R. Wilks is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Southeast, Virginia
Posts: 133
Default Re: FPE breaker that didn't trip

The funny thing is (very recently) the CPSC closed its files on FPE panels and basically said they did not find a problem.
This is directly from the CPSC memo:
WASHINGTON, D.C. - The Consumer Product Safety Commission announced today that it is closing its two year investigation into Federal Pacific Electric Stab-lok type residential circuit breakers. This action was taken because the data currently available to the Commission does not establish that the circuit breakers pose a serious risk of injury to consumers.
I always mention a FPE panel and the know hazards and risks associated with these panel; and as Sean noted, have the panel examined by a experienced/Lic. electrician and be prepared to replace the panel.



Jamie R Wilks
North Star Home Inspections
VCHI #3380000351
InterNACHI #05081596
Reply With Quote
  #4  
Old 7/13/11, 5:36 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: FPE breaker that didn't trip

Oh come on, jump on it!

It's a great marketing tool.

Referring your vast knowledge toward an electrician really makes you a lot of money and allows you to post in the legal section.... !!!!

I am just certain that they will return the favor!!!!!!!!!!!!!!!

Not, just kidding!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Shunt trip breaker jfrederick Electrical Inspections 5 7/22/09 9:40 PM
What's it take to trip a breaker? jfunderburk Electrical Inspections 14 10/20/08 11:44 AM
Arching Causes Main Breaker To Trip? msylvester Electrical Inspections 10 10/22/07 3:57 PM
Electrical Guru Question? Breaker lock outs pdoane Electrical Inspections 4 9/7/07 2:05 PM


All times are GMT -4. The time now is 9:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts