Default FPE Panel - Do you open them up?

I ran into a FPE panel today & couldn't open it up without turning all the breakers off (the breakers are in the way of the cover in the on position). Of course I didn't want to turn all them off. My question is do you open up these panels or just automatically report the FPE panel and leave it at that?
Thanks,
Mark
Reply With Quote
  #2  
Old 2/6/06, 6:47 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 3,166
Michael R. Boyett .
Default Re: FPE Panel - Do you open them up?

I usually open them up but it's like playing 'pick up sticks', one wrong move and bam! off goes a breaker or more.
Reply With Quote
  #3  
Old 2/6/06, 7:28 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 6,358
David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute
Default Re: FPE Panel - Do you open them up?

FPE's!!!

I open them up, but if the cover or screws start giving me a hard time, (such as yours) I simply recommend an Electrician to evaluate.

Another note...Every FPE panel gets a "Red Flag" whether it can be accessed or not.

These panels pose a latent threat and they could be a hazard. The circuit breakers may fail to trip in the case of an overload or short-circuit. A circuit breaker that fails to trip could cause a fire or personal injury. The problem with these panels is that some double pole 220volt circuit breakers and some single pole 120volt circuit breakers may not operate as intended if overloaded. A good breaker will trip (turning off the power to that circuit) Federal Pacific breakers appear not to trip every time which could result in a fire.
Reply With Quote
  #4  
Old 2/7/06, 8:38 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 954
Erby Crofutt .
Default Re: FPE Panel - Do you open them up?

I used to. Don't anymore. Knocked out to many breakers. Now I just tell em about it, explain why I don't open them and refer to an electrician familiar with the FPE controversy.



--

Erby Crofutt
B4U Close Home Inspections
Georgetown, Kentucky

KY Lic# HI-2041
www.b4uclose.com
http://www.kentuckyradon.com
Kentucky Home Inspections
Kentucky Home Inspectors
NACHI02090301

Read my Active Rain Blog here: Erby, The Central Kentucky Home Inspector

Join Active Rain HERE and I'll get some points for your participation. Please! I did ask nice!
Reply With Quote
  #5  
Old 2/7/06, 9:34 AM
Rick J. Hinck's Avatar
Rick J. Hinck Rick J. Hinck is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Chillicothe, IL
Posts: 49
Rick J. Hinck hasn't had much positive or negative feedback
Default Re: FPE Panel - Do you open them up?

i don't have too much problem opeing up panels. I do though have copies of a handout concerning FBE "Stab-Lok" panels in the truck with me at all times. When I run across on I give one copy to the buyer and one to the RE agent and tell them to put it in their resource file for futrure use.


Rick
Reply With Quote
  #6  
Old 2/7/06, 11:12 AM
mnye mnye is offline
New User
 
Join Date: Aug 2005
Location: Cincinnati, OH
Posts: 33
mnye hasn't had much positive or negative feedback
Please Note: mnye is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FPE Panel - Do you open them up?

Quote:
Originally Posted by rhinck
i don't have too much problem opeing up panels. I do though have copies of a handout concerning FBE "Stab-Lok" panels in the truck with me at all times. When I run across on I give one copy to the buyer and one to the RE agent and tell them to put it in their resource file for futrure use.


Rick
Where can we get a copy of this?

Mike
Reply With Quote
  #7  
Old 2/7/06, 5:18 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 6,358
David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute
Default Re: FPE Panel - Do you open them up?

Here ya go Mike,




FEDERAL PACIFIC PANELS

There has been a lot of talk about the safety of Federal Pacific "Stab-Lok" circuit breaker panels and the fact that they may have inherent defects. The result of the defect has linked them to numerous electrical fires.
There is no supporting evidence from any government agency or regulatory authority stating that these FPE panels are unsafe and should be replaced and there has not been a recall by the consumer product safety commission.
If you have one of these FPE panels or intend to purchase a home that has one of these FPE panels, we suggest that you talk with your electrician and decide what is right for you and your family.
These panels are easy to identify. They usually display the FPE and/or the "Stab-Lok" logos / insignia. Typically a knowledgeable electrician will recommend replacing these panels. Replacement cost is usually about $1000.00.

As a Home Inspector, this information puts us in a very difficult situation when we perform a whole house Home Inspection. These FPE breaker panels do "perform their intended function" when performing a visual inspection. The panel does not "initiate" an unsafe condition, which leaves us in the precarious position of knowing that a latent problem may exist in a breaker panel that we check off as "performing intended function".

The following has been said about Federal Pacific Electric "Stab-Lok" panels:
These panels pose a latent threat and they could be a hazard. The circuit breakers may fail to trip in the case of an overload or short-circuit. A circuit breaker that fails to trip could cause a fire or personal injury.
The problem with these panels is that some double pole 220volt circuit breakers and some single pole 120volt circuit breakers may not operate as intended if overloaded. A good breaker will trip (turning off the power to that circuit) Federal Pacific breakers appear not to trip every time which could result in a fire.

Published reports of tests conducted on FPE two pole 220volt circuit breakers indicate that under certain conditions one leg/pole may attempt to trip the breaker. The result is a circuit that stays live, and a circuit breaker that has been compromised and when reset will not trip again under any excessive load.

In some instances the breakers have been known to fall out when the cover is removed. Loose contacts can also cause arcing which would result in a fire. These panels appear to work perfectly during normal operation allowing electricity to flow without any problems or symptoms. The real question is, what will your panel do if it has an overload?

The Consumer Product Safety Commission (CPSC) did conduct product testing of these FPE breakers and found that their failure rates were significant.

The CPSC’s advice concerning these panels is for consumers to avoid overloading circuits as well as to turn off and have examined any devices that are causing the circuit breakers to trip. (This is easier said than done and defeats the whole point for having the breaker.)
Federal Pacific electric’s statement in response to this problem is cautious in tone: "FPE breakers will trip reliably at most overload levels."

It should be noted that Federal Pacific is no longer in business. Aftermarket breakers are available for these panels. Most of these panels are large and had a lot of circuits and the cost of replacing all the breakers is often more than the cost of installing a new panel.
The Solution

The best solution is to replace the panel. Recently some companies have started making replacement breakers for FPE panels. In many cases these are manufactured with the same problematic design of the original, and there is no data that they are more reliable. Also, replacing the breakers does not address problems with the buss bars in FPE panels that are not as well documented as the circuit breaker problem.

In closing, remember that any repair work should be performed only by a licensed electrician.

Here are some interesting sites relating to this FPE issue

http://www.inspect-ny.com/fpe/fpe.html

FPE Panels - Hazard or Hype?
http://www.codecheck.com/pdf/electri...%20Nov2003.pdf

General information on the FPE panel problem:
http://www.inspect-ny.com/fpe/fpepanel.htm

CPSC test data showing that up to 2/3 of FPE breakers fail:
http://www.inspect-ny.com/fpe/CPSCsummary.
Reply With Quote
  #8  
Old 2/7/06, 6:11 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 5,795
Dale Duffy .
Default Re: FPE Panel - Do you open them up?

Quote:
Originally Posted by ecrofutt
I used to. Don't anymore. Knocked out to many breakers. Now I just tell em about it, explain why I don't open them and refer to an electrician familiar with the FPE controversy.
Ditto and Exactly.... I'm not risking my life to see the interior (ever again).

I had a mess in my hands numerous times. Junk, their just Junk.
Reply With Quote
  #9  
Old 2/7/06, 6:13 PM
Jae Williams's Avatar
Jae Williams Jae Williams is online now
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 2,838
Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information Jae Williams is very trusted source of information
Default Re: FPE Panel - Do you open them up?

For information about the Federal Pacific Electric breaker panel see information at
: http://www.cpsc.gov/cpscpub/prerel/prhtml83/83008.html



"not just an inspection, but an education"

www.homesweethomecincinnati.com
Reply With Quote
  #10  
Old 2/7/06, 6:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,976
Jeffrey R. Pope .
Default Re: FPE Panel - Do you open them up?

Found this one today. It was already opened up (the cover was missing). . .



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net

Last edited by jpope; 2/28/07 at 4:15 PM.
Reply With Quote
  #11  
Old 2/7/06, 6:28 PM
Jeffrey S. Campbell's Avatar
Jeffrey S. Campbell Jeffrey S. Campbell is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Pittston, ME
Posts: 709
Jeffrey S. Campbell is often very helpful Jeffrey S. Campbell is often very helpful Jeffrey S. Campbell is often very helpful
Send a message via AIM to jcampbell Send a message via MSN to jcampbell Send a message via Yahoo to jcampbell
Default Re: FPE Panel - Do you open them up?

I do not open them anymore... too many headaches... I explain to client why i do not and provide them ample literature and links to read to their hearts content...
Reply With Quote
  #12  
Old 2/7/06, 7:31 PM
mnye mnye is offline
New User
 
Join Date: Aug 2005
Location: Cincinnati, OH
Posts: 33
mnye hasn't had much positive or negative feedback
Please Note: mnye is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FPE Panel - Do you open them up?

Quote:
Originally Posted by dvalley
Here ya go Mike,




FEDERAL PACIFIC PANELS

There has been a lot of talk about the safety of Federal Pacific "Stab-Lok" circuit breaker panels and the fact that they may have inherent defects. The result of the defect has linked them to numerous electrical fires.
There is no supporting evidence from any government agency or regulatory authority stating that these FPE panels are unsafe and should be replaced and there has not been a recall by the consumer product safety commission.
If you have one of these FPE panels or intend to purchase a home that has one of these FPE panels, we suggest that you talk with your electrician and decide what is right for you and your family.
These panels are easy to identify. They usually display the FPE and/or the "Stab-Lok" logos / insignia. Typically a knowledgeable electrician will recommend replacing these panels. Replacement cost is usually about $1000.00.

As a Home Inspector, this information puts us in a very difficult situation when we perform a whole house Home Inspection. These FPE breaker panels do "perform their intended function" when performing a visual inspection. The panel does not "initiate" an unsafe condition, which leaves us in the precarious position of knowing that a latent problem may exist in a breaker panel that we check off as "performing intended function".

The following has been said about Federal Pacific Electric "Stab-Lok" panels:
These panels pose a latent threat and they could be a hazard. The circuit breakers may fail to trip in the case of an overload or short-circuit. A circuit breaker that fails to trip could cause a fire or personal injury.
The problem with these panels is that some double pole 220volt circuit breakers and some single pole 120volt circuit breakers may not operate as intended if overloaded. A good breaker will trip (turning off the power to that circuit) Federal Pacific breakers appear not to trip every time which could result in a fire.

Published reports of tests conducted on FPE two pole 220volt circuit breakers indicate that under certain conditions one leg/pole may attempt to trip the breaker. The result is a circuit that stays live, and a circuit breaker that has been compromised and when reset will not trip again under any excessive load.

In some instances the breakers have been known to fall out when the cover is removed. Loose contacts can also cause arcing which would result in a fire. These panels appear to work perfectly during normal operation allowing electricity to flow without any problems or symptoms. The real question is, what will your panel do if it has an overload?

The Consumer Product Safety Commission (CPSC) did conduct product testing of these FPE breakers and found that their failure rates were significant.

The CPSC’s advice concerning these panels is for consumers to avoid overloading circuits as well as to turn off and have examined any devices that are causing the circuit breakers to trip. (This is easier said than done and defeats the whole point for having the breaker.)
Federal Pacific electric’s statement in response to this problem is cautious in tone: "FPE breakers will trip reliably at most overload levels."

It should be noted that Federal Pacific is no longer in business. Aftermarket breakers are available for these panels. Most of these panels are large and had a lot of circuits and the cost of replacing all the breakers is often more than the cost of installing a new panel.
The Solution

The best solution is to replace the panel. Recently some companies have started making replacement breakers for FPE panels. In many cases these are manufactured with the same problematic design of the original, and there is no data that they are more reliable. Also, replacing the breakers does not address problems with the buss bars in FPE panels that are not as well documented as the circuit breaker problem.

In closing, remember that any repair work should be performed only by a licensed electrician.

Here are some interesting sites relating to this FPE issue

http://www.inspect-ny.com/fpe/fpe.html

FPE Panels - Hazard or Hype?
http://www.codecheck.com/pdf/electri...%20Nov2003.pdf

General information on the FPE panel problem:
http://www.inspect-ny.com/fpe/fpepanel.htm

CPSC test data showing that up to 2/3 of FPE breakers fail:
http://www.inspect-ny.com/fpe/CPSCsummary.
Thanks David!
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 5:32 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics