Default FPE?'s

There is aluminum at the panel but the breakers have the aluminum copper abbreviation. If this means they are rated for aluminum doesn't the electrician have to install a special screw to pigtail into them? The outlets also had alum.

What is the device that is wrapped around the main aluminum wires?
Attached Thumbnails
fpe-s-dsc05315.jpg   fpe-s-dsc05317.jpg  



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/8/11, 5:29 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: FPE?'s

Current transformers .


http://en.wikipedia.org/wiki/Current_transformer

2010)
In electrical engineering, a current transformer (CT) is used for measurement of electric currents. Current transformers, together with voltage transformers (VT) (potential transformers (PT)), are known as instrument transformers. When current in a circuit is too high to directly apply to measuring instruments, a current transformer produces a reduced current accurately proportional to the current in the circuit, which can be conveniently connected to measuring and recording instruments. A current transformer also isolates the measuring instruments from what may be very high voltage in the monitored circuit. Current transformers are commonly used in metering and protective relays in the electrical power industry.

I would have liked to see some Nocorode on the alum wires no pigtail required if the equipment has CO/AL on them




Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.




Last edited by rcooke; 2/8/11 at 5:37 PM..
Reply With Quote
  #3  
Old 2/9/11, 7:34 AM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: FPE?'s

Thanks Roy for the current trnformers info.

I understood that the pigtail would have to be done at the outlets even though the breakers are protected from the effects of aluminum. Am I mistaken?



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #4  
Old 2/9/11, 7:46 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: FPE?'s

Quote:
Originally Posted by rwashington View Post
Thanks Roy for the current trnformers info.

I understood that the pigtail would have to be done at the outlets even though the breakers are protected from the effects of aluminum. Am I mistaken?
It the receptacles ( plugs switches ect) are CO/AL marked no Pig tail is required .
They are ok with both copper or aluminum an anti oxidant is needed for the aluminum wire



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #5  
Old 2/9/11, 9:11 AM
Greg Keene, CPI's Avatar
Greg Keene, CPI Greg Keene, CPI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Evergreen, CO
Posts: 628
Default Re: FPE?'s

Current transformers used to determine current usage and cost.

http://www.theenergydetective.com/about-ted



Greg Keene
Clear Choice Home Inspections
Evergreen, CO
303-674-3234
greg@clearchoice-hi.com
Reply With Quote
  #6  
Old 2/9/11, 11:12 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: FPE?'s

The connections of the AL to the outlets should be inspected by an electrician, regardless of the listing of the receptacle.

The problem is with the conductor. Over time, the connections become loose due to expansion and contraction of the AL conductor. This, in turn, creates a high-resistant connection which can result in fire.

In most cases, the AL should be "pig-tailed" (at the receptacle, switch or fixture) with CU. There are several connectors manufactured for this application.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 2/9/11, 11:24 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: FPE?'s

If pig tailing is done it should only be done by an electrician

The Consumer Product Safety Commission does not recommended the use of pigtailing, as laboratory testing has shown that this method does not effectively mitigate the risk, and in some cases, may increase the risk of fire. The only CPSC approved methods of upgrading aluminum wired homes are the COPALUM method, which must be done using special tools and by electricians certified in its use, or by completely rewiring the home with copper.

http://en.wikipedia.org/wiki/Aluminum_wire



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #8  
Old 2/9/11, 11:45 AM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: FPE?'s

I agree with Roy. The wire nut method shouldn't be used. It has been found to potentially cause fires. As far as I know the older CU/AL are no longer believed to be safe and would require a Copalum pigtail. Crimping with the Cop alum is the way to go if you have non CO/ALR rated devices. The if the devices are CO/ALR I would still want an Electrician to evaluate because if there is the smallest nick in the aluminum where the insulation was striped it can cause an issue with aluminum allot faster than copper. Also the conductor should only be wrapped 2/3 to 3/4 around the screw and wire must lay flat against the plate.
Reply With Quote
  #9  
Old 2/9/11, 12:34 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: FPE?'s

Thanks for the clarification everyone. I had forgotten about the COPALUM method.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #10  
Old 2/9/11, 2:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: FPE?'s

Although the CopAlum crimp is the only connector recognized by the CPSC, there are other connectors available that serve the same purpose and create a "permanent" connection. I am not referring to "wire-nuts," even though some may be specifically listed for this purpose.

The suggestion by the CPSC that the only other remedy is to re-wire the home is ludicrous (IMHO).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 2/9/11, 2:25 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: FPE?'s

Federal Pacific Stab-Lok Panel
- Recommend Review / Replacement by Licensed Electrical Contractor..



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #12  
Old 2/9/11, 2:26 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: FPE?'s

At least there is one copper on the bus
be it a neutral....



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #13  
Old 2/9/11, 2:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: FPE?'s

http://www.alcopstore.com/

For instance...
Attached Thumbnails
fpe-s-alumcopperconnector.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/9/11, 2:57 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: FPE?'s

These pigtails are only approved until a later date when thay are no longer approved...
Problem is the wire
not the splice....



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 9:38 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts