Default Is an FPE Stab-Lok defective by definition?

Do you consider an FPE Stab-Lok panel an inherent defect and not merely a latent safety hazard and why?

Thanks

Last edited by wthacker; 3/7/09 at 11:12 AM..
Reply With Quote
  #2  
Old 3/6/09, 8:27 PM
Bobby Hamilton's Avatar
Bobby Hamilton Bobby Hamilton is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Austintown, OH
Posts: 1,246
Default Re: Is an FPE Stab-Lok defective by definition?

I would call it a defect because everytime I pull the cover off one, ya never know if the breakers will pop off with it.



Bobby Hamilton
Bloodhound Home Inspection Services
Youngstown Home Inspection
Austintown Ohio Home Inspection


Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
Reply With Quote
  #3  
Old 3/6/09, 8:35 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Is an FPE Stab-Lok defective by definition?

William...there is a difference between your question and the title of your thread.

The FPE is not as apt to be problematic as the Stab-lok would be.

FPE Stab-Lok® components have considered problematic by industry professionals due to the high trip failure rate that occurred during testing, and were the subject of scrutiny by the Consumer Products Safety Commission.

The issue is that the breakers do not make adequate contact with the service bus bar, leading to “arcing” resulting in appliance damage. Failure of any component within the electrical system can result in fire and/or electrocution.

Although there was no recall of FPE Stab-Lok® breakers, there still remains the question of the integrity of the system. Only a licensed electrician can make a determination concerning the condition of the breakers.

Refer it to an electrician...and explain why.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #4  
Old 3/6/09, 8:42 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Is an FPE Stab-Lok defective by definition?

Quote:
Originally Posted by jwilliams4 View Post
William...there is a difference between your question and the title of your thread.

The FPE is not as apt to be problematic as the Stab-lok would be.

FPE Stab-Lok® components have considered problematic by industry professionals due to the high trip failure rate that occurred during testing, and were the subject of scrutiny by the Consumer Products Safety Commission.

The issue is that the breakers do not make adequate contact with the service bus bar, leading to “arcing” resulting in appliance damage. Failure of any component within the electrical system can result in fire and/or electrocution.

Although there was no recall of FPE Stab-Lok® breakers, there still remains the question of the integrity of the system. Only a licensed electrician can make a determination concerning the condition of the breakers.

Refer it to an electrician...and explain why.
I agree
Reply With Quote
  #5  
Old 3/6/09, 8:44 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Is an FPE Stab-Lok defective by definition?

Me, too...



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #6  
Old 3/6/09, 8:51 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Is an FPE Stab-Lok defective by definition?

Quote:
Originally Posted by jwilliams4 View Post
Me, too...
as i said lol
Was that your twin?
Reply With Quote
  #7  
Old 3/6/09, 8:58 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Is an FPE Stab-Lok defective by definition?

Quote:
Originally Posted by wwilson3 View Post
as i said lol
Was that your twin?
My twin? Why, no...

It seems the State of Ohio passed a law some years back banning the existence of two of me...

So I never get to visit "Twinsburg, Ohio" though it has been my life-long dream.

Twinsburg is a really, really place, and hosts a "twins festival" each year. It is reported to be a lot of fun, but I'll never know...



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #8  
Old 3/6/09, 10:03 PM
Richard Fitzwater Richard Fitzwater is offline
InterNACHI Member
 
Join Date: Jan 2009
Location: El Paso, TX
Posts: 97
Default Re: Is an FPE Stab-Lok defective by definition?

http://www.inspect-ny.com/fpe/fpepanel.htm

This website was very informative after some breakers fell out of a panel I inspected. Breakers not tripping was only one part of the danger. The guttering for the wires in the older panels were also so packed in that it is hard to identify specific circuits. Be EXTRA careful in these panels. Look for hot spots and arcing.

Hope this helps!

Here is my wording from a report:
It is recommended that a qualified, licensed electrician further evaluate the panel. Federal Pacific panels have had a high rate of safety violations over the years. Many fires and shock hazards have originated in these panels. Stab-Lok panels are older and are a latent hazard. Replacement is usually recommended.





Richard Fitzwater
FYI Property Inspection
El Paso, TX

TREC#8317
www.el-paso-home-inspector.com
www.fyiproperty.homestead.com
Reply With Quote
  #9  
Old 3/6/09, 10:08 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Is an FPE Stab-Lok defective by definition?

Quote:
Originally Posted by rfitzwater View Post
It is recommended that a qualified, licensed electrician further evaluate the panel. Federal Pacific panels have had a high rate of safety violations over the years. Many fires and shock hazards have originated in these panels. Stab-Lok panels are older and are a latent hazard. Replacement is usually recommended.
That statement can put you into hot water. Can you cite any safety violations?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 3/6/09, 10:33 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Is an FPE Stab-Lok defective by definition?

Quote:
Originally Posted by jpope View Post
That statement can put you into hot water. Can you cite any safety violations?
I don't think there have been any "safety violations" of record, have there? That's why no CPSC recall was ever enacted.

But mostly, it's what you have posted in the past concerning the STAB-LOK and Zinsco panels that leads to such a concern about those panels.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #11  
Old 3/6/09, 10:36 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Is an FPE Stab-Lok defective by definition?

I'm not sure but what I posted in #3 I got from you a long time ago. I had a narrative on STAB-LOK for years, but the one in #3 is so much better, I use it now.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #12  
Old 3/6/09, 10:51 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Is an FPE Stab-Lok defective by definition?

It appears to be a variation of what I use.

Here it is again for anyone who is interested in using it.

Quote:
The home is equipped with a Federal Pacific Electric (FPE) Stab-lok brand electrical panel. Stab-lok load centers and their components are considered problematic by industry professionals due to their high failure rate as documented by the Consumer Products Safety Commission. Failure of any component within the electrical system may result in fire and/or electrocution. Evaluation of the panel by a qualified electrician is advised to determine its safety, integrity and performance.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 3/7/09, 2:36 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Is an FPE Stab-Lok defective by definition?

Quote:
Originally Posted by wthacker View Post
Do you consider an FPE panel an inherent defect and not merely a latent safety hazard and why?
Yes. Because the electricians here do, and the State of California considers them more knowledgeable than me about electricity by virtue of their licensing. Regretfully, I'm just a lowly home inspection/property consultant.

Maybe one could say that they are an inherent latent safety and fire hazard.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 3/7/09, 11:10 AM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Is an FPE Stab-Lok defective by definition?

Thanks for the response guys. This was not as a standard home inspection, it was a Baltimore County Rental Inspection (BCRI). Yesterday, their website was down and we used a previously saved form. Then last evening shortly after I posted this question, my CATV signal was lost until this morning. I am now able to access the BCRI form and there is a newer rev. The earlier form addressed the electrical system in this manner:

Electrical System - no apparent visual hazards. Options Pass or Fail

The new rev form addresses electrical issues with this check:

Electrical wires are not visible in living areas. Options Yes or No

However there is also a "catch all" check which reads:

Are there any other readily observable problems that in the inspector’s opinion represent an immediate threat to the health or safety of occupant? If “yes” please describe below:
Options Yes or No

There is also an newly added disclaimer:

Disclaimer: The scope of the above inspection is limited to the items listed above and has been performed to the requirements set forth by the Baltimore County Office of Code Enforcement as required under the Baltimore County Rental Licensing program. The above inspection shall not be construed to be either a home inspection as defined under Maryland law or an inspection related to one or more of the Baltimore County life and safety codes. Under Maryland law, the person completing this report for the property owner may not repair or recommend any person to repair any of the items listed above.

The form is here:
http://resources.baltimorecountymd.g...ctionsheet.pdf



Last edited by wthacker; 3/7/09 at 11:36 AM..
Reply With Quote
  #15  
Old 3/8/09, 8:16 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: Is an FPE Stab-Lok defective by definition?

Quote:
Originally Posted by jwilliams4 View Post
Refer it to an electrician...and explain why.
Jae,

There is no option to refer to an electrician on the Baltimore County Rental Inspection form. The home inspector must make the call. There is disclaimer stating this is not a home inspection or a life and safety code inspection.

So how would you other inspectors answer this form?

Regards
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Federal Noark Stab Lok charper Electrical Inspections 6 7/24/11 12:09 PM
4 Point Inspection and Stab Lock rross2 Electrical Inspections 8 2/12/09 9:44 AM
Another Federal Pacific Stab loc sfalvey Electrical Inspections 3 11/2/07 1:49 AM


All times are GMT -4. The time now is 9:38 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts