This is the same company that makes SQ D Roy Cooke
http://www.schneider-electric.ca/www/en/html/glance.htm ![]() Corporate Profile ![]() Schneider at a Glance ![]() History ![]() Career Opportunities ![]() Training ![]() Media Centre ![]() Catalogues ![]() SchneiderSPORT ![]() 1-800-565-6699 Customer Information Centre Your Complete Customer Service Connection ![]() ![]()
Roy Cooke.RHI. http://royshomeinspection.com/ Questions 613-475-1144 Roycooke@sympatico.ca " A life spent making mistakes is not only more honorable but more useful than a life spent doing nothing." George Bernard Shaw |
|
#17
|
|||
|
|||
|
Here is some more on FPE and SQ D...,. Roy
http://www.schneider-electric.ca/www...saannounce.htm Press Release Archives 2004 Press Releases 2003 Press Releases 2002 Press Releases 2001 Press Releases 2000 Press Releases 1999 Press Releases 1998 Press Releases Schneider Electric Canada and CSA Announce Voluntary Recovery of Square D and Federal Pioneer AFI Circuit Breakers New Breakers Being Shipped to Distributors TORONTO, ONTARIO - October 12, 2004 - Schneider Electric Canada today announced that it is working in conjunction with the Canadian Standards Association (CSA) on a voluntary recovery for its Square D and Federal Pioneer Arc Fault Interrupter (AFI) circuit breakers. The products may not provide arc detection capability due to the failure of a third-party supplied internal component in the electronic detection circuit. The recovery pertains to Square D QO® and Homeline ® (Canada and the USA) and Federal Pioneer Stab-lok® (Canada) 15- and 20-amp AFI circuit breakers manufactured this year between March 1 and September 23, 2004. While the breakers will continue to function like a regular circuit breaker, providing short circuit and overload protection, they may not detect a high resistance, low current arcing fault. These products are typically sold through electrical distributors and retail home improvement stores and installed in residential and light commercial applications. AFI circuit breakers are required by the Canadian Electrical Code in the bedroom circuits of new residential construction. “The safety of our people, our customers and our products is our organization’s number one priority,” said Gary Abrams, president of Schneider Electric Canada. “We accept nothing less than excellence when it comes to safety, and we are voluntarily recalling all breakers that may be affected to help ensure our customers’ safety. We are working with the CSA and provincial regulatory agencies on a corrective action plan and have sent this information to our distributors and customers. Our distributors and customers have associated our Square D and Federal Pioneer brands with industry leadership, safety, quality, reliability and innovation for over 50 years and we will act quickly and appropriately to ensure they receive the quality products and services they expect from us.” Schneider Electric has sent detailed instructions to its network of distributors, customers and retailers on how to identify and return these products. This potential arc fault issue has been corrected and the company has significantly increased the manufacturing capacity of its AFI breakers. New breakers have already begun shipping to its distributors and customers. If distributors or customers have any immediate questions, they can call toll-free 1-800-565-6699 for any additional information available. - 30 - Schneider Electric is the world’s power and control specialist, with leading brands such as Federal Pioneer, Merlin Gerin, Square D and Telemecanique. We have proven power distribution, industrial control, automation and energy management products and systems installed in utilities and industrial, commercial and residential facilities worldwide. Schneider Electric generated sales of approximately $14.2 billion in 2003 in 130 countries.Schneider Electric Canada is part of the North American Operating Division of Schneider Electric, which markets products to customers in the United States, Canada and Mexico. In North America, we are a leader in all our key market segments – residential construction, commercial and industrial construction, process automation and control, and original equipment manufacturers (OEMs). In Canada, Schneider Electric has 1,000 employees, four manufacturing facilities, 23 sales and service offices and 300 electrical distributor branches across the country. Visit us on the internet at www.schneider-electric.ca. Schneider Electric: Give the best of the New Electric World to everyone, everywhere, at any time Roy Cooke.RHI. http://royshomeinspection.com/ Questions 613-475-1144 Roycooke@sympatico.ca " A life spent making mistakes is not only more honorable but more useful than a life spent doing nothing." George Bernard Shaw |
|
#18
|
||||
|
||||
|
Quote:
Actually the report from the consumer board was not......that is an actual report made by the board who investigated the issue.... now...the online website...is also nothing more than articles written by people......and accounts that can't be totally verified.... Some will liken it to a Witch Hunt.......who's next......Square D...lol...noooooo......you know Zinsco took up that fight...lol.. Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#19
|
||||
|
||||
|
lol...yeah ROY.....the Federal Pioneer THREW me...lol
Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#20
|
||||
|
||||
|
BUT I can tell you this much.......I do not have big enough GONAD's to shake up any industry...lol.......just found it interesting is all....
I am again still one of those old school guys who say well if you are not going to do anything....atleast replace all the OCPD's for the branch circuits with newer models.......as I said I like replacing breakers that are over 30 years old....like anything......reliablility on anything that old I sometimes question...but hey...I dont make em.....I just install em..... besides...what the hell does a hick from VA know..........they probably know MUCH more up a few states north of me........ Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#21
|
||||
|
||||
|
However...since I am bringing up weird stuff tonight....how about the class action lawsuit in New Jersey...
http://www.inspect-ny.com/fpe/FPEnotice12-05.htm Ironically....some of the links do not actually go where they say they do.....and I might just contact the court as I would LOVE to read the records since no party admited any guilt.....and it only effected New Jersey residents.... Interesting stuff.... Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#22
|
||||
|
||||
|
Now some ammo from the class action side of the fence...lol
1.0 SUMMARYCalibration tests have been performed on 122 two-pole Federal Pacific Electric circuit breakers. The calibration tests were performed -in accordancewith UL Standard 489 except for or a difference in the sequence of calibrations. UL 489 is the applicable standard that the breakers are presumed to meet. In most cases, the calibration tests were repeated after 500 off-on mechanical operations of the toggle handle.. The circuit breakers tested were supplied by CPSC and came from several sources. Most were provided to CPSC by Federal Pacific Electric, some were purchased new by CPSC staff members at retail outlets, and a few were removed from existing installations. The breaker ratings tested were 30 A (30 two-pole breakers tested), 40A (35), 50A(20), 60A(7) and 80A (30). The tests include performance at 100%, 135%, and 200% of ratings, and dielectric tests. A substantial number of breakers failed the calibrations testing, both before and after the mechanical toggle operations. Failures were evident with both poles carrying current as well as with one-pole operation. Specifically, the failures are summarized as follows: FAILURE CONDITION FAILURES % (#failed/#tested) Before Mechanical Operations After Mechanical Operations No-trip: 200% of rating, both poles 0% (0/122) 1% (1/107) No-trip: 200% of rating, individual poles 1% (3/244) 10% (21/214) No-trip: 135% of rating, both poles* 25% (31/122) 36% (39/107) No-trip: 135% of rating, individual poles 51% (125/244) 65% (144/220) Trip: 100% of rating, both poles* 3% (4/122) 6% (7/111) Dielectric Breakdown (short)* 0 1% (1/111) TABLE 1 - SUMMARY OF FAILURES *UL 489 Test Conditions The failures appeared. among breakers of all ratings, none were failure-free. Most of the "no-trip' conditions were sustained for four hours well beyond the UL specification. These were not marginal failures with respect to the failure criteria. The data suggests that, on the average, the mechanical operations result in increased failures. This was .'not strictly the case on a sample-to-sample basis.The failures relate to hazardous conditions in at least two ways. First, a fault in the wiring or utilization equipment which causes excessive- current-can result in fire if the circuit is not opened by the breaker -- this is its principal functional requirement. Secondly, it was determined in these tests that some of the breakers overheat to hazardous levels when subjected to overcurrent conditions (due to their own failure to trip) for sustained periods of time. The overheating can result in incapacitation of the breaker (i.e.: it will no longer open under any condition), and the temperature can be high enough to ignite fire in the vicinity of the breaker, as evidenced by charring of the case on some samples. NOTE: this text is quoted verbatim from pages 3-5 of "Calibration and Condition Tests of Molded Case Circuit Breakers, Final Report: Contract CPSC-C-81-1429 December 30, 1982," obtained from the US Consumer Product Safety Commission as a FOIA request. Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. Last edited by pabernathy; 11/2/06 at 1:22 AM.. |
|
#23
|
||||
|
||||
|
Ok....with all that said and I am rather tired and I have NO freakin idea why I posted this to begin with...much less why I am rambling on execpt that it is 1:29AM and I had a few beers....imagine talking electricity with me after a few beers...amazing...lol...
anyway with all that said.........I like HI's to defer them to Electricians.....I dont actually believe the scare methods being used today....simply a nice it should be evaluated will do.....and I always would suggest the branch circuit breakers be upgraded.......remember the action was against the breakers....not the concept of the stablok..... Yeah they can fall out....sure....but not if you leave the cover on them...lol....so the largest concern was the possibly failure rate...however the manufacturer states it would trip in all excessive cases and it may in fact be supported by the UL tests at 200%...which probably would not melt down the conductor anyway.....but besides all the riggamarow...... I think in FPE's my own personal opinion is let them now about the option to upgrade the breakers ( or the electrician can tell them that if you dont need comfortable giving advice ) and have it evaluated.......we will check for heating, other issues and in the end you have defered your liability to the electrical contractor...... Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#24
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
LOL - Now I see why Paul has almost 3000 posts!
Paul and Roy, the FPE in Canada today is NOT the same as we had here in the 60's-80's. For some reason the FPE Canada has been very well accepted and does not have the problems the old US FPE breakers and panels did/do, even thought the design is almost identical. Roy, do your FPE breakers have the "falling out" problem? Meaning do one or two always manage to fall out of the panel when the cover is removed? |
|
#25
|
||||
|
||||
|
Paul;
In inspect them like any other panel (with the exception that I duck when I take off the dead front I also add, in the report, that there has been some question about their failure rate and breaker failure rate. Then I recommend evaluation by a licnesed and insured electrical contractor, just like they article states. Let the sparkys take the liability for saying that is OK. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#26
|
||||
|
||||
|
I left an FPE panel on a rent house that I bought to see how it would perform. Visually, it inspected okay. I even had a good friend of mine who is a licensed electrician look it over. No problem with it, he said.
Less than a year later I replaced the panel after my tenant complained. The panel was arcing. So now I always call them out for further eval by an electrician but I give them my personal recommendation to have the panel replaced. I would not live in a home with an FPE panel without replacing it first. John Onofrey Licensed Professional Inspector Houston Home Inspection Houston Home Inspector www.texasinspectors.net John Onofrey President, Grail Media, LLC "Effortless Email Marketing" www.homehintsenews.com 2007 INACHI Inventions and Innovations Award Winner Free! Inspector Email Marketing trial click here |
|
#27
|
|||
|
|||
|
Quote:
. and this is what I have in my home if I had any concerns at all I would change it immediatly. Roy Cooke.RHI. http://royshomeinspection.com/ Questions 613-475-1144 Roycooke@sympatico.ca " A life spent making mistakes is not only more honorable but more useful than a life spent doing nothing." George Bernard Shaw |
|
#28
|
||||
|
||||
|
lol.....actually Speedy I am better today.....not sure what was into me last night....guess it was the BEER......
Hey fella....my 2,000+ posts are good their buddy...lol Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#29
|
||||
|
||||
|
I like Mr. Deckers Approach....it gets the Country Hick "Paul" Electrical Award for Excellence...
JOhn, I hear ya brother........and remember you have every right to do so and with all the info out their......safety is a large concern... If you strictly go by the boards end recommendation.....then again Mr. Deckers approach is the one I would 'Endorse"....but they should be carefully inspected.....spend a little more time on them, thermal them just a little better......well thermal all brands a little better as I said I have nearly 2 dozen issues with CH, SQ D and all brands actually... IN my opinion the test results tell me something was wrong BUT remember they were under a microscope......how good would the other brands fair under the same microscope...obviously better as they are UL..... SO.......I still like my idea of atleast informing the client of a replacement option for the breakers alone.....the panel enclosure maybe fine....it's the breakers that have issues possibly.......and the branch circuit OCPD's can be upgraded for a far less cost.....adding atleast SOME level of security in a unsecure world..... Paul W. Abernathy,CMI,CEI,CEPE National Electrical Code Expert-ONLY Weekly Live Chat :http://www.theelectricalguru.com/chat.html Weekly Chat on Mondays & Wednesdays -8PM E.S.T * Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko. |
|
#30
|
||||
|
||||
|
Quote:
Other issues with these load centers include a poorly designed bus bar and breaker contacts. The article you posted. . . Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Another big update to the chapter management system | inxil | Misc. Discussion | 2 | 2/23/07 5:50 PM |
| Update to NACHI message board | inxil | Misc. Discussion | 21 | 12/5/06 8:53 PM |
| Newsletter System Update | inxil | Misc. Discussion | 1 | 4/23/06 11:48 PM |