  #31  
Old 11/2/06, 11:51 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: FPE- Stablok update from the IAEI

I have not had enough experience with FP to have an opinion. I think the state had a deal with SqD because that is about all I ever saw installed anywhere I inspected. Some of the volunteer/ranger jobs in the park system used GE and Siemens, simply because that was available at the BORG.
Reply With Quote
  #32  
Old 11/2/06, 6:45 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: FPE- Stablok update from the IAEI

Here's one from 2003 that I had never seen before. It's by Douglas Hansen for those of you who know him or have taken one of his courses.

http://www.home-inspect.com/articles...%20Nov2003.pdf



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #33  
Old 11/2/06, 8:05 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: FPE- Stablok update from the IAEI

Yeah but Douglas Hansen has FPE on the BRAIN......he would go searching for FPE issues even if none were present...lol....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #34  
Old 11/2/06, 8:30 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: FPE- Stablok update from the IAEI

Quote:
Originally Posted by pabernathy
he would go searching for FPE issues even if none were present...lol....
So he's kind of like Jeff Pope and Zinsco? Hey, Jeff!



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #35  
Old 11/2/06, 8:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: FPE- Stablok update from the IAEI

I don't go looking for them, they just seem to find me. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #36  
Old 11/2/06, 8:42 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: FPE- Stablok update from the IAEI

Yes.....I have a page on my slide dedicated to Jeff...it says donated by Jeff "Mr. ZINSCO" Pope



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #37  
Old 11/2/06, 9:56 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: FPE- Stablok update from the IAEI

Quote:
Originally Posted by pabernathy
Yes.....I have a page on my slide dedicated to Jeff...it says donated by Jeff "Mr. ZINSCO" Pope
Hey, Jeff.

It only cost me $80 to change my name two years ago. I think we here at NACHI could provide enough support to the Judge when he asks why you want to change your name.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #38  
Old 11/2/06, 10:06 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: FPE- Stablok update from the IAEI

and no it does not MEAN jeff is DEFECTIVE....thehehehehe



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #39  
Old 11/2/06, 10:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: FPE- Stablok update from the IAEI

Now, why on earth would I want to lose a label like that?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #40  
Old 11/2/06, 11:04 PM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 708
Default Re: FPE- Stablok update from the IAEI

Paul
I like the photo of the ostrich with its' head in the sand, ...er I mean the outlet, on the original link
http://magazine.iaei.org/magazine/99_c/stablok.htm

I think the author, who's name was left out of the IAEI letter, also has had his head in the sand a little too long...
( I notice that they did provide their attorneys name, in case any one has questions)
(....as if that isn't an admission that they do have some type of problem. Don't call us...call our attorney...

OK a statement in the IAEI article said that the load center was not the focus of the investigation and the complaints...
Let's assume that the load center is acceptable....and you can just replace the circuit breakers with new replacements.
I know that you can, I have seen them at Lowe's....however, for the cost of a few FPE breakers,
.... you can have a nice Siemens load center preloaded with a 200A main and a starter set 15A breakers. The additional circuit breakers for Siemens are considerably less expensive.
Pick your favorite panel brand and compare prices. It is shocking what they charge for the FPE breakers, but it is understandable. When you have a product that lacks sales volume, the price is naturally more. Simple economics.
OK so the next argument might be that the FPE breakers cost more, but you save all that labor on not installing a new panel. Sure, but most people would hire an electrician to replace all those expensive FPE breakers. That still takes some labor, and while it is less, how much are you saving?

By the way did you notice that the IAEI added this statement to the article;
"This information is neither approved nor disapproved by the International Association of Electrical Inspectors."

I don't believe they have ever made a statement about the FPE panels.

However I am not afraid to make a statement on my reports every time I find an FPE panel. And the recommendation is to always replace. Cheap insurance for everyone involved. It cost alot more when the house, the belongings, and maybe the occupants, have been burned to a crisp. Can anyone even imagine the expert witnesses coming out of the woodwork to testify how bad these panels are, and the inspector should have reported it. Gives me chills.
Reply With Quote
  #41  
Old 11/3/06, 12:02 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: FPE- Stablok update from the IAEI

Firstly...lets not confuse the POST with it being MY full stance......just thought it was neat and would bring up a good debate and educational moment.

Second.....The board did conclude to conclude nothing really....they closed the case so everyone is free to have an option and do as they wish....heck man....who am I to say otherwise...

well....you may save possibly $ 500.00 in labor...considering I could replace a panel with Replacements for about $ 850.00 including labor and cost of breakers......a total service chance I would charge $ 1,200 to $ 1,500 possibly....

But again........I tell everyone to defer a FPE and Zinsco to allow an licensed electrical contractor review them, look them over as their are known issues.....but their are also known issues with CH and Sq D...just not as wide spread.....so again while I agree the notice on FPE and Zinsco is warranted....I would not make it out as a DEATH WISH waiting to happen...let the experts evaluate it and make that call....

In the end let their BUDGET make that call........Do dont mind either way.....and you kinda have to know wire and its ability to handle issues...like in the tests....they all would have tripped possibly before it got too high and caused damage.....who knows...

The fact they LIED to get UL approval is a strong motivator to denounce them anyway.......if they feel they needed to cheat..what else are they hiding was my logic growing up.....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #42  
Old 11/3/06, 12:33 PM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 708
Default Re: FPE- Stablok update from the IAEI

Quote:
Originally Posted by pabernathy
Firstly...lets not confuse the POST with it being MY full stance......just thought it was neat and would bring up a good debate and educational moment.
Paul,
I do understand and appreciate the way you presented the information. It does bring up a good debate on the controversy that exists. I always learn alot when I read your posts, and I am sure that many others do as well. Keep up the good work!
Reply With Quote
  #43  
Old 11/4/06, 6:07 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: FPE- Stablok update from the IAEI

Hey....I feel the love brother........it's all good.....it's all good my friend....as many will tell you sometimes my posts are rambling anyway...just hope people pick the education factor out of it...lol...

Lord knows I get tons of things wrong also.....we are not perfect...lol....well...I am close...thehehehhhehehehehehe.....

Ah......Perfectly ROUND that is...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Another big update to the chapter management system inxil Miscellaneous Discussion for Inspectors 2 2/23/07 6:50 PM
Update to NACHI message board inxil Miscellaneous Discussion for Inspectors 21 12/5/06 9:53 PM
Newsletter System Update inxil Miscellaneous Discussion for Inspectors 1 4/24/06 12:48 AM


All times are GMT -4. The time now is 3:59 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts