Writing report on house I did last night. What you see is the main service wire traveling along a back outside wall from point A - Service Mast to point B - Service Meter. Would you write this up as needing replaced or would you state to monitor?
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
| Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Good Lord--Not only is it installed improperly, it's SHOT---Replace it and install it correctly, by a electrician naturally---
Dale Duffy Inspect Arizona Companies, Inc. Phoenix Home Inspectors, Inc. Scottsdale Home Inspectors, Inc. Infraspection Certified Thermographer 602.402.5305 Home Hints eNews
InterNACHI 2007 U.S.A Member of the Year National Association of Commercial Building Inspectors, Inc. |
|
#3
|
||||
|
||||
|
Dale how should the service wire be installed?
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
|
#4
|
||||
|
||||
|
Have the Buyer or Owner if they are making the upgrade ask the Electrician, your not an electrician, nor am I, and I don't know what the pictures are representing, need the full story. Large picture of the whole gig.
Sent Verizon Wireless Blackberry Dale Duffy Inspect Arizona Companies, Inc. Phoenix Home Inspectors, Inc. Scottsdale Home Inspectors, Inc. Infraspection Certified Thermographer 602.402.5305 Home Hints eNews
InterNACHI 2007 U.S.A Member of the Year National Association of Commercial Building Inspectors, Inc. |
|
#5
|
||||
|
||||
|
Short answer: In conduit....
Pictures on this inspection weren't necessarily of the conduit, but I think you get the idea. |
|
#6
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Agree it is time to replace.
All I see is some straps missing. I don't see where conduit would be called for, at least as far the the pictures show. |
|
#7
|
||||
|
||||
|
SE Cable is perfectly allowed for exterior applications...However, this SE Cable is "SHOT" and should be replaced as it presents a hazard. The Grounded conductor is exposed and it does carry current as well the ungrounded conductors I would bet are close to being exposed in some portions as you can see the insulation is nearly done as well. I can guarantee you the "insulation" properties on that ungrounded conductor is about "SHOT" as well.......since they will certainly have to replace it....you are doing them a GREAT service by informing them now.....!!!
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#8
|
||||
|
||||
|
Pics of the panel... Thanks everyone. Let me know if you see anything else. No manufacture data and no indication on the main breaker. My educated guess was corrected by a good friend to 100-125AMP MAX split buss panel. Manufacture is Cutler Hammer.
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
|
#9
|
||||
|
||||
|
Please Note:
bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Just my opinion. |
|
#10
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#11
|
||||
|
||||
|
Triple tap at feeds, Open knock out at base of panel. Upper right corner of the panel buss... I see 30 Amp but can't make out what that is all about. Wire sizing maybe wrong there..
|
|
#12
|
||||
|
||||
|
Opening in the bottom of pic 1. Looks like a double tapped breaker in pic 3. Exposed romex should be in conduit in pic. 1. Where are the grounds?
Shouldn't the cables feeding the lower bus be protected from the sharp edges of the cabinet?
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#13
|
||||
|
||||
|
Brian nice to see you wondered where you went. Yes I have a bad habit of second guessing myself. First time I've ever ran across a SE cable in such a condition as this one. Just wanted a sec opinion from the pros.
Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
| Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America) |
|
#14
|
||||
|
||||
|
Quote:
-- Where do you see exposed Romex? Guess I'm missing it. -- Not sure i see the sharp edges your talking about either. Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
|
#15
|
||||
|
||||
|
Quote:
-- Open knock out at base --- agreed -- 30 AMP I saw no problems. I can't remember exactly however it was for the furnace if I recall right could be wrong. Bill Boerner STL Home Inspection ServicesServing St. Louis/Surrounding (314) 805-2137 billy.boerner@gmail.com http://www.stlhomeinspector.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Difficult Chimneys | thance | Inspecting HVAC Systems | 2 | 1/29/08 9:16 PM |
| Two ground wires | jlybolt | Electrical Inspections | 8 | 8/10/06 3:06 PM |
| Service Panel question for board sparkies | pbolliger | Electrical Inspections | 8 | 5/14/06 10:24 AM |
| Service entrance conductor | jjackson | Electrical Inspections | 30 | 1/7/06 6:05 AM |