  #1  
Old 9/26/09, 3:53 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,196
Send a message via Yahoo to bboerner
Default Frayed Service Wires

Writing report on house I did last night. What you see is the main service wire traveling along a back outside wall from point A - Service Mast to point B - Service Meter. Would you write this up as needing replaced or would you state to monitor?
Attached Thumbnails
frayed-service-wires-jperez-018.jpg   frayed-service-wires-jperez-019.jpg  



Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #2  
Old 9/26/09, 4:08 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,058
Default Re: Frayed Service Wires

Good Lord--Not only is it installed improperly, it's SHOT---Replace it and install it correctly, by a electrician naturally---
Reply With Quote
  #3  
Old 9/26/09, 4:54 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,196
Send a message via Yahoo to bboerner
Default Re: Frayed Service Wires

Dale how should the service wire be installed?



Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
  #4  
Old 9/26/09, 5:13 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,058
Default Re: Frayed Service Wires

Quote:
Originally Posted by bboerner View Post
Dale how should the service wire be installed?
Have the Buyer or Owner if they are making the upgrade ask the Electrician, your not an electrician, nor am I, and I don't know what the pictures are representing, need the full story. Large picture of the whole gig.







Sent Verizon Wireless Blackberry
Reply With Quote
  #5  
Old 9/26/09, 5:44 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is online now
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,644
Default Re: Frayed Service Wires

Quote:
Originally Posted by bboerner View Post
Dale how should the service wire be installed?
Short answer: In conduit....

Pictures on this inspection weren't necessarily of the conduit, but I think you get the idea.
Attached Thumbnails
frayed-service-wires-gedc0053.jpg   frayed-service-wires-gedc0054.jpg   frayed-service-wires-gedc0047.jpg  
Reply With Quote
  #6  
Old 9/26/09, 5:51 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 740
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Frayed Service Wires

Agree it is time to replace.

All I see is some straps missing. I don't see where conduit would be called for, at least as far the the pictures show.
Reply With Quote
  #7  
Old 9/26/09, 8:26 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Frayed Service Wires

SE Cable is perfectly allowed for exterior applications...However, this SE Cable is "SHOT" and should be replaced as it presents a hazard. The Grounded conductor is exposed and it does carry current as well the ungrounded conductors I would bet are close to being exposed in some portions as you can see the insulation is nearly done as well. I can guarantee you the "insulation" properties on that ungrounded conductor is about "SHOT" as well.......since they will certainly have to replace it....you are doing them a GREAT service by informing them now.....!!!



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 9/26/09, 9:12 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,196
Send a message via Yahoo to bboerner
Default Re: Frayed Service Wires

Pics of the panel... Thanks everyone. Let me know if you see anything else. No manufacture data and no indication on the main breaker. My educated guess was corrected by a good friend to 100-125AMP MAX split buss panel. Manufacture is Cutler Hammer.
Attached Thumbnails
frayed-service-wires-jperez-048.jpg   frayed-service-wires-jperez-049.jpg   frayed-service-wires-jperez-050.jpg   frayed-service-wires-jperez-051.jpg   frayed-service-wires-jperez-052.jpg  




Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
  #9  
Old 9/26/09, 9:23 PM
bdoles2's Avatar
bdoles2 bdoles2 is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 3,071
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Frayed Service Wires

Quote:
Originally Posted by bboerner View Post
Would you write this up as needing replaced or would you state to monitor?
Seriously??? You can't make that call? I can't believe you actually thought about writing it up as just something to "monitor". WTF!? Hell, while your at it just tell them to wrap it with some duct tape, while standing in a puddle of water.

Just my opinion.
Reply With Quote
  #10  
Old 9/26/09, 9:24 PM
rbrady's Avatar
rbrady rbrady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Frayed Service Wires



10 (?) gauge wire connected to the main bus looks like a problem to me.
Reply With Quote
  #11  
Old 9/27/09, 12:03 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Frayed Service Wires

Triple tap at feeds, Open knock out at base of panel. Upper right corner of the panel buss... I see 30 Amp but can't make out what that is all about. Wire sizing maybe wrong there..
Reply With Quote
  #12  
Old 9/27/09, 12:19 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 7,707
Send a message via Yahoo to jfunderburk
Default Re: Frayed Service Wires

Opening in the bottom of pic 1. Looks like a double tapped breaker in pic 3. Exposed romex should be in conduit in pic. 1. Where are the grounds?

Shouldn't the cables feeding the lower bus be protected from the sharp edges of the cabinet?




“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 9/27/09, 1:15 AM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,196
Send a message via Yahoo to bboerner
Default Re: Frayed Service Wires

Quote:
Originally Posted by bdoles2 View Post
Seriously??? You can't make that call? I can't believe you actually thought about writing it up as just something to "monitor". WTF!? Hell, while your at it just tell them to wrap it with some duct tape, while standing in a puddle of water.

Just my opinion.
Brian nice to see you wondered where you went. Yes I have a bad habit of second guessing myself. First time I've ever ran across a SE cable in such a condition as this one. Just wanted a sec opinion from the pros.



Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
Find an InterNACHI certified Virginia Home Inspector (and anywhere else in North America)
  #14  
Old 9/27/09, 1:19 AM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,196
Send a message via Yahoo to bboerner
Default Re: Frayed Service Wires

Quote:
Originally Posted by jfunderburk View Post
Opening in the bottom of pic

1. Looks like a double tapped breaker in pic 3. Exposed romex should be in conduit in pic. 1. Where are the grounds?

Shouldn't the cables feeding the lower bus be protected from the sharp edges of the cabinet?


-- Panel is only grounded to earth. The entire home has no GFCI or three prong outlets.

-- Where do you see exposed Romex? Guess I'm missing it.

-- Not sure i see the sharp edges your talking about either.



Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
  #15  
Old 9/27/09, 1:24 AM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,196
Send a message via Yahoo to bboerner
Default Re: Frayed Service Wires

Quote:
Originally Posted by pbolliger View Post
Triple tap at feeds, Open knock out at base of panel. Upper right corner of the panel buss... I see 30 Amp but can't make out what that is all about. Wire sizing maybe wrong there..
-- Triple tap at feeds --- agreed

-- Open knock out at base --- agreed

-- 30 AMP I saw no problems. I can't remember exactly however it was for the furnace if I recall right could be wrong.



Bill Boerner
STL Home Inspection Services
Serving St. Louis/Surrounding
(314) 805-2137
billy.boerner@gmail.com
http://www.stlhomeinspector.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 9:16 PM
Two ground wires jlybolt Electrical Inspections 8 8/10/06 3:06 PM
Service Panel question for board sparkies pbolliger Electrical Inspections 8 5/14/06 10:24 AM
Service entrance conductor jjackson Electrical Inspections 30 1/7/06 6:05 AM