Default Fuse bypass

I haven't seen this before. Double tapping to bypass the fuses. Would like some input on this. Thanks.
Attached Thumbnails
fuse-bypass-img_1975-small-.jpg.JPG
Views:	185
Size:	39.2 KB
ID:	36492  
Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/15/10, 11:06 PM
arook arook is offline
Active Poster
 
Join Date: Jan 2006
Location: Hamilton, NJ
Posts: 256
Please Note: arook is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fuse bypass

It's incorrect, a safety hazard, and a fire hazard.

Typically happens when the fuse blows and the homeowner doesn't have any replacement fuses.
Reply With Quote
  #3  
Old 4/16/10, 1:14 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Fuse bypass

Can I assume that it's an A/C disconnect box? If so... is there an OCPD/breaker in the panel for it? If there is, the only thing that is wrong is double tapping of the wires under the lugs. Unless the wires in that BX and jumpers are undersized to the breaker. The jumpers will be replaced based upon the fact that you should call out the double taps. Another concern is the BX run...sealtite is considered the norm for outdoor applications in this instance.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #4  
Old 4/16/10, 5:02 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fuse bypass

The conductors leaving the bottom of the disconnect appear to be NM Cable (Romex) in Flexible Metallic Conduit (FMC). Notice the bare ground, which would eliminate the possibility of AC cable, and the paper filler that was once used around the conductors within NM cable. FMC was at one time permitted as a wet location wiring method if the conduit was installed so that it would drain. This is no longer permitted. NM cable or its conductors are not listed for wet locations so they cannot be used to feed the unit.

If this is an AC unit then it might be possible that the unit requires the use of fuses for ground fault and short circuit protection (hence the fused disconnect). It's hard to say if the conductors are of adequate size without knowing the Minimum Circuit Ampacity (MCA). The information from the nameplate might uncover even more problems.
Reply With Quote
  #5  
Old 4/16/10, 9:15 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fuse bypass

That will no long serve as the required disconnect until it is either corrected or replaced. It was installed to make sure the tech could ensure the power was off while they were working on the equipment. It cannot do that as currently wired.
Reply With Quote
  #6  
Old 4/16/10, 10:31 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Fuse bypass

Quote:
Originally Posted by jwicklander View Post
Can I assume that it's an A/C disconnect box? If so... is there an OCPD/breaker in the panel for it? If there is, the only thing that is wrong is double tapping of the wires under the lugs.
There is no longer a disconnect for the unit (as Jim stated). The double taps are the least of my concern.

This is just a hack job that needs correction.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 4/16/10, 10:53 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Fuse bypass

Quote:
Originally Posted by jpope View Post
There is no longer a disconnect for the unit (as Jim stated). The double taps are the least of my concern.

This is just a hack job that needs correction.

If you remove the double taps...then you are correctly replacing them with the fuses. Correct? Which repairs one concern. The other is the need for seal-tite.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #8  
Old 4/16/10, 1:18 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Fuse bypass

Quote:
Originally Posted by jwicklander View Post
If you remove the double taps...then you are correctly replacing them with the fuses. Correct? Which repairs one concern. The other is the need for seal-tite.

Jeff
The disconnect at the unit (required) has simply been bypassed or modified and is now incorrect and a potential safety hazard. Simply recommend a replacement disconnect be installed (which should be within sight of the A/C unit).
(Again presuming this services an exterior A/C or heat pump unit) Otherwise a proper junction box should be installed to contain the properly repaired splices.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
  #9  
Old 4/16/10, 2:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Fuse bypass

Quote:
Originally Posted by jwicklander View Post
If you remove the double taps...then you are correctly replacing them with the fuses. Correct? Which repairs one concern. The other is the need for seal-tite.

Jeff
So if I eliminate the "double taps" by wire-nutting the connections together, all is good. Right?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 4/16/10, 2:47 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fuse bypass

Quote:
Originally Posted by jpope View Post
So if I eliminate the "double taps" by wire-nutting the connections together, all is good. Right?
Jeff, I hope I missed the sarcasm in this. I think you were based on your post above, but wanted to clarify.

The disconnect either needs to be fixed or replaced. It is a safety hazard to anyone working on the unit it was installed for. Also if the unit calls for "Max fuse size" the fuses would be required.
Reply With Quote
  #11  
Old 4/16/10, 3:28 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Fuse bypass

Quote:
Originally Posted by jpope View Post
So if I eliminate the "double taps" by wire-nutting the connections together, all is good. Right?
Never mentioned anything about bypassing the fuse blocks.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #12  
Old 4/16/10, 3:29 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Fuse bypass

Quote:
Originally Posted by wwarner View Post
The disconnect at the unit (required) has simply been bypassed or modified and is now incorrect and a potential safety hazard. Simply recommend a replacement disconnect be installed (which should be within sight of the A/C unit).
(Again presuming this services an exterior A/C or heat pump unit) Otherwise a proper junction box should be installed to contain the properly repaired splices.

There is no need to replace the disconnect itself. What's wrong with installing the proper fuses??

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #13  
Old 4/16/10, 3:55 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 3,293
Default Re: Fuse bypass

Quote:
Originally Posted by jwicklander View Post
What's wrong with installing the proper fuses??

Jeff
Nothing if the contractor has the correct pull out block on the truck and the tension of the clamps are still good.




Submit your AWARDS NOMINATIONS here

Visit the InterNACHI Awards web portal here

Blessed are the blissfully ignorant... for they shall be easily led...
Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/16/10, 4:10 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Fuse bypass

Quote:
Originally Posted by Jim Port View Post
Jeff, I hope I missed the sarcasm in this. I think you were based on your post above, but wanted to clarify.
Sorry Jim. You missed it

My point was directed to the "issue" of the double taps. It is my opinion that the connections are irrelevant, and the bypass of the disconnect is the issue that should be addressed.

My report would not mention the improper connections.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 4/16/10, 4:20 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fuse bypass

Thanks for the clarification. Your response seemed out of character for you. You were correct that the safety issue would over-ride the wiring in the lugs.

Someone could move the handle to the OFF position and get a nasty surprise.

Quote:
Originally Posted by wwarner View Post
Nothing if the contractor has the correct pull out block on the truck and the tension of the clamps are still good.
There is no need to replace the pull out, unless the clips are bad. All you would need to do is remove the wires effectively bypassing the fuses.

You would still have the issue of the wiring in the flex, unless it is UF cable.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cartridge Fuse Color-Code? bsmith Electrical Inspections 2 12/14/08 9:13 AM
Fuse box puzzle (with photos) abolt Electrical Inspections 2 8/5/07 3:28 PM
Fuse Panel Questions pdoane Electrical Inspections 8 9/21/06 8:37 AM
FPE Fuse Panel rarmstrong1 Electrical Inspections 2 6/3/06 5:22 PM
Max fuse ratings dmacy Inspecting HVAC Systems 15 1/19/06 11:35 PM


All times are GMT -4. The time now is 9:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts