I haven't seen this before. Double tapping to bypass the fuses. Would like some input on this. Thanks.
|
| Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
Please Note:
arook is a non-member guest and is in no way affiliated with InterNACHI or its members.
It's incorrect, a safety hazard, and a fire hazard.
Typically happens when the fuse blows and the homeowner doesn't have any replacement fuses. |
|
#3
|
||||
|
||||
|
Can I assume that it's an A/C disconnect box? If so... is there an OCPD/breaker in the panel for it? If there is, the only thing that is wrong is double tapping of the wires under the lugs. Unless the wires in that BX and jumpers are undersized to the breaker. The jumpers will be replaced based upon the fact that you should call out the double taps. Another concern is the BX run...sealtite is considered the norm for outdoor applications in this instance.
Jeff Jeff Wicklander Corwick Home Services Join my business on Facebook
|
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
The conductors leaving the bottom of the disconnect appear to be NM Cable (Romex) in Flexible Metallic Conduit (FMC). Notice the bare ground, which would eliminate the possibility of AC cable, and the paper filler that was once used around the conductors within NM cable. FMC was at one time permitted as a wet location wiring method if the conduit was installed so that it would drain. This is no longer permitted. NM cable or its conductors are not listed for wet locations so they cannot be used to feed the unit.
If this is an AC unit then it might be possible that the unit requires the use of fuses for ground fault and short circuit protection (hence the fused disconnect). It's hard to say if the conductors are of adequate size without knowing the Minimum Circuit Ampacity (MCA). The information from the nameplate might uncover even more problems. |
|
#5
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
That will no long serve as the required disconnect until it is either corrected or replaced. It was installed to make sure the tech could ensure the power was off while they were working on the equipment. It cannot do that as currently wired.
|
|
#6
|
||||
|
||||
|
Quote:
This is just a hack job that needs correction. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
||||
|
||||
|
Quote:
If you remove the double taps...then you are correctly replacing them with the fuses. Correct? Which repairs one concern. The other is the need for seal-tite. Jeff Jeff Wicklander Corwick Home Services Join my business on Facebook
|
|
#8
|
||||
|
||||
|
Quote:
(Again presuming this services an exterior A/C or heat pump unit) Otherwise a proper junction box should be installed to contain the properly repaired splices. Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#9
|
||||
|
||||
|
So if I eliminate the "double taps" by wire-nutting the connections together, all is good. Right?
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#10
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The disconnect either needs to be fixed or replaced. It is a safety hazard to anyone working on the unit it was installed for. Also if the unit calls for "Max fuse size" the fuses would be required. |
|
#11
|
||||
|
||||
|
Quote:
Jeff Jeff Wicklander Corwick Home Services Join my business on Facebook
|
|
#12
|
||||
|
||||
|
Quote:
There is no need to replace the disconnect itself. What's wrong with installing the proper fuses?? Jeff Jeff Wicklander Corwick Home Services Join my business on Facebook
|
|
#13
|
||||
|
||||
|
Nothing if the contractor has the correct pull out block on the truck and the tension of the clamps are still good.
Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
| Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
My point was directed to the "issue" of the double taps. It is my opinion that the connections are irrelevant, and the bypass of the disconnect is the issue that should be addressed. My report would not mention the improper connections. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#15
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks for the clarification. Your response seemed out of character for you. You were correct that the safety issue would over-ride the wiring in the lugs.
Someone could move the handle to the OFF position and get a nasty surprise. Quote:
You would still have the issue of the wiring in the flex, unless it is UF cable. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Cartridge Fuse Color-Code? | bsmith | Electrical Inspections | 2 | 12/14/08 9:13 AM |
| Fuse box puzzle (with photos) | abolt | Electrical Inspections | 2 | 8/5/07 3:28 PM |
| Fuse Panel Questions | pdoane | Electrical Inspections | 8 | 9/21/06 8:37 AM |
| FPE Fuse Panel | rarmstrong1 | Electrical Inspections | 2 | 6/3/06 5:22 PM |
| Max fuse ratings | dmacy | Inspecting HVAC Systems | 15 | 1/19/06 11:35 PM |