Default Fuse main disconnect away from main circuit breaker panel -- 3 wires to panel (240V)

Yesterday I did an inspection in which the electrical service was unusually configured. The service entrance cable ran to a main fuse box, with bonded neutral and grounding lugs, which were connected to the grounding rod and supplemental water pipe grounding electrodes.

This ran about 15 feet to the branch circuit breaker panel with 3 wires: 2 hots (240V service) and a neutral wire. The circuit breaker panel had one neutral bus bar (which did not appear to be bonded to the panel, and to which branch circuit grounds and neutrals were connected) and the branch circuit breakers.

The neutral bus bar was very crowded, with double-tapped neutrals, and little room to work, and only had one large lug for the incoming neutral.

In any case, this does not seem proper, at least by today's standards. It appeared to have been done by a professional electrician at least 25 years ago.

My thought is that the easiest way to correct this is to install another bus bar in the breaker panel for the grounding wires, and for that bus bar to be grounded and bonded as a main panel would be.

I don't have photos here because they're on my laptop, which I rarely use for the internet. May add them to the post later.
Reply With Quote
  #2  
Old 8/16/07, 11:05 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Fuse main disconnect away from main circuit breaker panel -- 3 wires to panel (240V)

Quote:
Originally Posted by fbartlo
My thought is that the easiest way to correct this is to install another bus bar in the breaker panel for the grounding wires, and for that bus bar to be grounded and bonded as a main panel would be.
Grounding conductors should be bonded to every metal enclosure, whether it's service equipment or not.

Neutrals are to be grounded only at the service equipment. There are exceptions, but the HI should not (in most cases) try and make this determination.

Adding a grounding bus sounds like the right call.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 6:24 PM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 3:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts