#1
|
|||
|
|||
|
Yesterday I did an inspection in which the electrical service was unusually configured. The service entrance cable ran to a main fuse box, with bonded neutral and grounding lugs, which were connected to the grounding rod and supplemental water pipe grounding electrodes.
This ran about 15 feet to the branch circuit breaker panel with 3 wires: 2 hots (240V service) and a neutral wire. The circuit breaker panel had one neutral bus bar (which did not appear to be bonded to the panel, and to which branch circuit grounds and neutrals were connected) and the branch circuit breakers. The neutral bus bar was very crowded, with double-tapped neutrals, and little room to work, and only had one large lug for the incoming neutral. In any case, this does not seem proper, at least by today's standards. It appeared to have been done by a professional electrician at least 25 years ago. My thought is that the easiest way to correct this is to install another bus bar in the breaker panel for the grounding wires, and for that bus bar to be grounded and bonded as a main panel would be. I don't have photos here because they're on my laptop, which I rarely use for the internet. May add them to the post later. |
|
#2
|
||||
|
||||
|
Quote:
Neutrals are to be grounded only at the service equipment. There are exceptions, but the HI should not (in most cases) try and make this determination. Adding a grounding bus sounds like the right call. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Main disconnect at meter instead of main panel. OK? | kshepard | Electrical Inspections | 14 | 11/8/06 6:24 PM |
| Can an AFCI offer GFCI protection | gbeaumont | Electrical Inspections | 19 | 7/6/06 11:45 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |