- Does anyone recommend up grades on fuse panels?
- Does anyone recommend further review? - Can fuse lugs be double tapped? like breakers? - Should a fuse panel have a directory like breakers? (i.e. labeled) - Do insurance company's balk at fused homes? - Does anyone care? Peter Doane Realty Check Inspection Service NACHI ID# 05120681
|
|
#2
|
||||
|
||||
|
Quote:
In my area it is very hard or impossible to get insurance with a fuse panel . I always write it up with please check with you insurance company as some might not want to give insurance . Recommend immediate complete service upgrade to breaker panel... And if the rest of the home is electrical poor I add and rest of home a complete check over, repair as Required. Roy Cooke |
|
#3
|
||||
|
||||
|
Quote:
100 amp up to 24 circuits. </IMG> Vern Mitchinson_CCHI_CMI Registar AlbertaNACHI International Association of Certified Home Inspectors of Canada
|
|
#4
|
||||
|
||||
|
Quote:
</IMG></IMG> |
|
#5
|
||||
|
||||
|
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Also there is NO 24 breaker rule. The limit is 42 regardless of panel size. Many folks have misconceptions about fuses. Fuses are actually better than breakers in most cases. There is NOTHING wrong with fuses. The problems arise with equipment the age of a typical fuse service. Most often it is well beyond it's service life. This is not to say I have not seen very clean and healthy fuse panels. I have. I persoanlly think to automatically "Recommend immediate complete service upgrade to breaker panel... " of a clean and safe fuse panel is a bit reactionary. I believe the equipment should be examined and it's condition listed. |
|
#7
|
|||
|
|||
|
I have to say......I agree with Speedy on this one....
Question 1: Does anyone recommend up grades on fuse panels? Answer: If the fuse panel is in good shape and meeting the load requirements I would not recommend simply because it is a fuse panel. However, if it is less than 100A I would recommend future upgrade to meet todays electrical needs. But not just because it is a fuse panel. Question 2: Does anyone recommend further review? Answer: Sure.....in the way of saying the above information..but again NOT just because it is a fuse panel.....fuse panels are safe if not safer. Question 3: Can fuse lugs be double tapped? like breakers? Answer: Nope.....still the same as breakers.....unless listed for multiple conductors....but more than not....NOPE ! Question 4:Should a fuse panel have a directory like breakers? (i.e. labeled) Answer: Yes, can't expect the home owner to know what to cut off in a emergency and the NEC has required labeling for some time...that I would recommend. Question 5: Do insurance company's balk at fused homes? Answer 6: Depends on the insurance company.....fuses are not so bad..its the capcity that is the problem but they worry more about AL wiring than fuses. It all has to do with capacity to IF they want upgraded to breakers over fuses...which really has to do with panel size...versus a fuse versus breaker thing. Question 6: Does anyone care? Answer: I do or i would not have replied... Paul W. Abernathy Last edited by pabernathy; 9/20/06 at 8:15 PM.. |
|
#8
|
||||
|
||||
|
Thanks guys (Paul, speedy, Roy and Vern) for your posts. I just needed reassurance on those items. I dont call fuse panels out unless something is wrong but I just wanted to know what the experts thought on the lines of the questions asked. Much thanks!
Peter Doane Realty Check Inspection Service NACHI ID# 05120681
|
|
#9
|
|||
|
|||
|
No problem Peter........Thats what we are here for.....
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Fuse panel | Michael Martin | Electrical Inspections | 7 | 11/1/07 2:18 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| FPE Fuse Panel | rarmstrong1 | Electrical Inspections | 2 | 6/3/06 5:22 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |