#1
|
|||
|
|||
|
I did an inspection a few days ago, and this place had a 100 amp fusebox. It had 30 amp fuse on 20 amp rated wiring. The reason for this according to the homeowner is because of the window air conditioner would blow the fuse. I know that the start up winding draws more amps at first but enough to blow a fuse? Does this sound right?
Thanks Josh |
|
#2
|
||||
|
||||
|
A slow blow type fuse at 20amps should work.
Do they make HACR type fuses? Over sized breakers are ok on compressor circuits so maybe this is allowed? Wait on the electricians to respond I guess. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 |
|
#3
|
||||
|
||||
|
In my book, this 30 amp fuse is not allowed. I call out all 30 amp fuses on #12 AWG.
|
|
#4
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Window shakers are designed to work on the circuit that matches the line plug. David is right a general lighting circuit needs to have the right fuse for the wire. It is only dedicated hard wired circuits that get to use the 440 rules that allow bigger O/C devices than 240.4(D) allow.
The installer has no control over what a user will plug in. My guess is the window shaker is bad. |
|
#5
|
|||
|
|||
|
Quote:
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#6
|
|||
|
|||
|
When in doubt...refer it out.
Michael Barnett C.H.I. #NACHI07081803, HIF#9725A Barnett's Certified Home Inspections BL#10009708 (661) 816-4123 www.barnetts-inspections.com mbarnett@ca.nachi.org www.nachi.org |
|
#7
|
||||
|
||||
|
Greg is 100% correct here, if the AC unit is designed for a 20A circuit then it should have no problems working on the 20A circuit. My guess is that circuit is not dedicated and when the AC starts along with something ELSE probably sharing the circuit it blows the fuse....
As for someone asking are fuses HACR rated...no......that would be delayed fuses but in this case......simply does not matter...putting in 30A on a 20A circuit just to keep it from tripping is wrong...the fuse was doing it's job. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
I know you guys don't like codes and such, but here's an interesting tidbit just the same. The International Property Maintenance Code (which would make for interesting reading for any home inspector) actually requires that a fuse panel that shows evidence of overfusing be condemned.
|
|
#9
|
||||
|
||||
|
Quote:
"Normal household circuit" are standard and any deviations from the standard are wrong. Kevin Kevin M. Kenny, Sr. Kenny Home Inspections Oak Forest, Illinois 60452 Nachi #6070990 http://kennyhomeinspections.com
|
|
#10
|
||||
|
||||
|
Quote:
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#11
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
"The A/C goes out and the microwave screws up my popcorn" |
|
#12
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |