Default Fusebox Bad?

I did an inspection a few days ago, and this place had a 100 amp fusebox. It had 30 amp fuse on 20 amp rated wiring. The reason for this according to the homeowner is because of the window air conditioner would blow the fuse. I know that the start up winding draws more amps at first but enough to blow a fuse? Does this sound right?

Thanks

Josh
Reply With Quote
  #2  
Old 10/10/07, 11:04 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Fusebox Bad?

A slow blow type fuse at 20amps should work.

Do they make HACR type fuses?

Over sized breakers are ok on compressor circuits so maybe this is allowed?

Wait on the electricians to respond I guess.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 10/10/07, 11:08 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Fusebox Bad?

In my book, this 30 amp fuse is not allowed. I call out all 30 amp fuses on #12 AWG.
Reply With Quote
  #4  
Old 10/10/07, 11:39 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fusebox Bad?

Window shakers are designed to work on the circuit that matches the line plug. David is right a general lighting circuit needs to have the right fuse for the wire. It is only dedicated hard wired circuits that get to use the 440 rules that allow bigger O/C devices than 240.4(D) allow.
The installer has no control over what a user will plug in.
My guess is the window shaker is bad.
Reply With Quote
  #5  
Old 10/10/07, 1:17 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Fusebox Bad?

Quote:
Originally Posted by Greg Fretwell
My guess is the window shaker is bad.
Give it a time out...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #6  
Old 10/10/07, 3:46 PM
mbarnett mbarnett is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Lancaster, CA
Posts: 19
Default Re: Fusebox Bad?

When in doubt...refer it out.



Michael Barnett C.H.I. #NACHI07081803, HIF#9725A
Barnett's Certified Home Inspections BL#10009708
(661) 816-4123
www.barnetts-inspections.com
mbarnett@ca.nachi.org
www.nachi.org
Reply With Quote
  #7  
Old 10/10/07, 4:28 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Fusebox Bad?

Greg is 100% correct here, if the AC unit is designed for a 20A circuit then it should have no problems working on the 20A circuit. My guess is that circuit is not dedicated and when the AC starts along with something ELSE probably sharing the circuit it blows the fuse....

As for someone asking are fuses HACR rated...no......that would be delayed fuses but in this case......simply does not matter...putting in 30A on a 20A circuit just to keep it from tripping is wrong...the fuse was doing it's job.



Paul W. Abernathy
Reply With Quote
  #8  
Old 10/10/07, 5:00 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fusebox Bad?

I know you guys don't like codes and such, but here's an interesting tidbit just the same. The International Property Maintenance Code (which would make for interesting reading for any home inspector) actually requires that a fuse panel that shows evidence of overfusing be condemned.
Reply With Quote
  #9  
Old 10/10/07, 5:04 PM
kkenny's Avatar
kkenny kkenny is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Oak Forest, IL
Posts: 475
Default Re: Fusebox Bad?

Quote:
Originally Posted by pabernathy
putting in 30A on a 20A circuit just to keep it from tripping is wrong
Got agree with Paul about this. If you found a 20 Amp breaker on 15 AWG wire because the microwave and the toaster keep blowing the circuit, you would call it out. Same diagnosis.

"Normal household circuit" are standard and any deviations from the standard are wrong.

Kevin



Kevin M. Kenny, Sr.
Kenny Home Inspections
Oak Forest, Illinois 60452
Nachi #6070990

http://kennyhomeinspections.com

Reply With Quote
  #10  
Old 10/10/07, 8:35 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Fusebox Bad?

Quote:
Originally Posted by Marc D. Shunk
I know you guys don't like codes and such, but here's an interesting tidbit just the same. The International Property Maintenance Code (which would make for interesting reading for any home inspector) actually requires that a fuse panel that shows evidence of overfusing be condemned.
All i know is I love that word....."condemned"....always have.......I wanna be a slum lord when I grow up.



Paul W. Abernathy
Reply With Quote
  #11  
Old 10/10/07, 9:19 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fusebox Bad?

Quote:
Originally Posted by pabernathy
My guess is that circuit is not dedicated and when the AC starts along with something ELSE probably sharing the circuit it blows the fuse....
.
I guess that's why you make the big bucks. You are probably right on that.

"The A/C goes out and the microwave screws up my popcorn"
Reply With Quote
  #12  
Old 10/10/07, 10:20 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Fusebox Bad?

Quote:
Originally Posted by Greg Fretwell
I guess that's why you make the big bucks. You are probably right on that.

"The A/C goes out and the microwave screws up my popcorn"
When I go on service calls for a breaker that trips a lot or a fuse that blows a lot (suspected overload), I've come to think that all homeowners are liars. I ask them first thing what else goes off when the breaker kicks or the fuse blows. The answer is often "nothing". When I turn out the fuse or turn off the offending breaker, it seems like half the house goes out. "Nothing" my a55.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 3:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts