Default Garage GFCI

Here's the scenario: Attached garage. New home. Ceiling lights, automatic garage door opener, AND all GFCI outlets on SAME circuit!. If I'm in the garage, at night, running a power saw (example), and I trip the GFCI, the lights go out, and the opener shuts off. I'm stuck in the dark!! I can't find a code anywhere that says the GFCI outlest and the light/opener have to be on separate circuits. I wrote it up as a safety violation that needed service. Any thoughts? Have a code number?

Rich
Reply With Quote
  #2  
Old 8/6/07, 1:03 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Garage GFCI

Quote:
I wrote it up as a safety violation that needed service.
You should retract that completely-inaccurate statement. It is not a "violation" and it is not a "safety-concern."

It may be considered a nuisance, but there is nothing that prohibits this set-up.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 8/6/07, 1:06 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Garage GFCI

Agreeed with my friend the " POPE ".....retract that statement as it is not correct.

The NEC® tells us what is REQUIRED to be GFCI protected......thats about it.......if the client wants to put all 120V 15 & 20 Amp circuits on GFCI they are more than OK to do so.....inconvience is not a mandate of the CODE.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 8/6/07, 1:32 PM
Richard Dale Richard Dale is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Chandler, AZ
Posts: 7
Default Re: Garage GFCI

So, I (home owner) accidentally trip the GFI, my saw shuts off, I'm stumbling in the dark, I trip and fall, which spills gas from an old can of gas I use to clean stuff, I drop my saw, it causes a spark, and I go up in flames, and thats not a safety concern? (Not to mention the home inspector ends up liable for his/her death/injury because I didn't mention it).

I didn't actually write in my report that it was a "violation". I merely stated that it may be a safety concern and that they may wish to add a separate circuit so that in case a GFI is tripped, the lights and opener won't go out. Sorry to have confused you.

The ONLY answer I was looking for here was... is there a 'code' or 'standard' on an attached garage that says these circuits must or 'should' be separate? This is the first attached garage in over 400 inspections that was wired this way. So, there must be a reason the other 399 were wired separately!

I wasn't looking for someone to criticize how inaccurate I am/was. Geeze.
Reply With Quote
  #5  
Old 8/6/07, 1:51 PM
Humberto Carvajal's Avatar
Humberto Carvajal Humberto Carvajal is offline
InterNACHI Member
 
Join Date: May 2005
Location: Homestead, FL
Posts: 310
Default Re: Garage GFCI

Except for the refrigerator Paul! Don't forget the refrigerator must be by itself!..LOL



Humberto Carvajal Jr.
A Florida Inspection Company, LLC
LEED® Accredited Professional
Member USGBC South Florida Chapter

A Florida Inspection Company
Property Inspector Serving Southeast Florida
Reply With Quote
  #6  
Old 8/6/07, 1:52 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage GFCI

Quote:
Originally Posted by rdale
So, I (home owner) accidentally trip the GFI, my saw shuts off, I'm stumbling in the dark, I trip and fall, which spills gas from an old can of gas I use to clean stuff, I drop my saw, it causes a spark, and I go up in flames, and thats not a safety concern? (Not to mention the home inspector ends up liable for his/her death/injury because I didn't mention it).
Mr. Dale

Let me first say that you saw something that you feel is a danger and you should never be criticized for this.
If there is one thing that I try to teach it is;
Safety first
Safety last
Safety always

To address the code issues concerning the use of one circuit in the garage and protecting the entire circuit with GFCI, there is nothing that prohibits this.
As a matter of fact in the 2008 code cycle all the receptacles in the garage will be required to be GFCI protected.

Personally I don’t put the light on the load side of GFCI although I have ran into situations where it had to be due to the way the circuit was installed originally. Without a doubt this is what happened in this instance. The circuit was installed where it would have to have the light on the load side of the GFCI.

Let me also say that through my thinking of safety first, safety last, safety always, it would be a greater danger to be using an electrical tool around a can of gas in daylight than the way the circuit is installed.

Should this person die through the scenario you presented I would have to rule it a clear case of accidental suicide.

Reply With Quote
  #7  
Old 8/6/07, 1:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Garage GFCI

Quote:
Originally Posted by rdale
I didn't actually write in my report that it was a "violation". I merely stated that it may be a safety concern and that they may wish to add a separate circuit so that in case a GFI is tripped, the lights and opener won't go out. Sorry to have confused you.
No confusion here, I merely responded to your post, as it was written.


Quote:
Originally Posted by rdale
The ONLY answer I was looking for here was... is there a 'code' or 'standard' on an attached garage that says these circuits must or 'should' be separate?
That question was answered. The answer is "no."

Quote:
Originally Posted by rdale
This is the first attached garage in over 400 inspections that was wired this way. So, there must be a reason the other 399 were wired separately!
"Common practice" would be the reason for that. As I stated, you would certainly be justified to report it as a potential nuisance.

Quote:
Originally Posted by rdale
I wasn't looking for someone to criticize how inaccurate I am/was. Geeze.
If you stated in your report (as you "implied") that this is a "violation" and "unsafe," it was necessary to let you know that you were inaccurate (wrong), so that lesser-experienced inspectors are not misdirected.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 8/6/07, 1:58 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Garage GFCI

Quote:
Originally Posted by hcarvajal
Except for the refrigerator Paul! Don't forget the refrigerator must be by itself!..LOL
Who says...the NEC® sure does not...

It says it CAN be by itself...not that is is required to be so.....



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 8/6/07 at 2:02 PM..
Reply With Quote
  #9  
Old 8/6/07, 2:00 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Garage GFCI

Quote:
Originally Posted by rdale
So, I (home owner) accidentally trip the GFI, my saw shuts off, I'm stumbling in the dark, I trip and fall, which spills gas from an old can of gas I use to clean stuff, I drop my saw, it causes a spark, and I go up in flames, and thats not a safety concern? (Not to mention the home inspector ends up liable for his/her death/injury because I didn't mention it).

I didn't actually write in my report that it was a "violation". I merely stated that it may be a safety concern and that they may wish to add a separate circuit so that in case a GFI is tripped, the lights and opener won't go out. Sorry to have confused you.

The ONLY answer I was looking for here was... is there a 'code' or 'standard' on an attached garage that says these circuits must or 'should' be separate? This is the first attached garage in over 400 inspections that was wired this way. So, there must be a reason the other 399 were wired separately!

I wasn't looking for someone to criticize how inaccurate I am/was. Geeze.
I don't think anyone is crticizing you my friend...just trying to remove an inaccurate statement is all, This is the on going battle to help electricians and inspectors work together as if you put that in your statement the local electrician would make a comment probably that would not be in your best interest....trust me....we are only trying to be helpful.

We can't give you a code....because none exists regarding your question.

Ok...I removed my trip statement above...lol...as I dont want it to be taken the wrong way. But in your example of a series of events it would more than likely be staged......we should not store gas in open areas that could be tripped over...and should not store gas in the garage really. Depending on the floor convering I am not sure a spark would be produced really and well many things COULD happen I guess.......but they are not really a GFCI related thing.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 8/6/07 at 2:21 PM..
Reply With Quote
  #10  
Old 8/6/07, 2:17 PM
Richard A. Hayes Richard A. Hayes is offline
New User
 
Join Date: Jul 2007
Posts: 6
Please Note: Richard A. Hayes is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage GFCI

I would have put the GFCI in the recepticales not in the panel... That would solve the problem.

As far as safety- you need to store you gas better!!!!
Reply With Quote
  #11  
Old 8/6/07, 4:30 PM
Kenneth F. Miller Kenneth F. Miller is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Berkley, MI
Posts: 260
Default Re: Garage GFCI

Some municipalities may have ordinances that they enforce that go beyond the NEC. I used to run into that all the time when I was still doing remod work. Sometimes you run into a muni inspector who just misunderstands the code or ordinance and enforces it wrong.
Reply With Quote
  #12  
Old 8/6/07, 7:09 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,323
Default Re: Garage GFCI

A little off the thread

How many and what is the required spacing of garage outlets??

I assume that the one per wall and 12 ft rule does not apply

Are any required??

rlb
Reply With Quote
  #13  
Old 8/6/07, 8:02 PM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage GFCI

As the garage is not considered a habitable room there are no spacing or required receptacles.'
Reply With Quote
  #14  
Old 8/6/07, 8:25 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Garage GFCI

Agreed...heck I have seen some Muni-Inspectors require receptacles in the garage to be a minimum of 18" high.......not understanding that this applies to commercial garages and not dwelling garages...but it happens.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 8/6/07, 9:26 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: Garage GFCI

Come on Paul, they have to justify their salaries.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Installing GFCI in garage with no ground cyezza Electrical 53 11/30/07 6:05 PM
GFCI Safety Notice rcooke Electrical 1 10/30/07 1:29 PM
Shower stall light/fan on garage GFCI lprinzi Electrical 3 10/31/06 5:13 PM
The question asked on the new HI Study test here? jtedesco1 Electrical 28 10/4/06 10:31 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 7:40 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts