Default Garage GFCI on door openers NEC 2008

This question may sound a little confusing but I will try. I did an inspection of new detached garage wiring built under NEC2008 codes. There were two circuits, one went to the readily accessible receptacles and the other went to the automatic garage door openers that were also GFCI protected fropm receptacles mounted in the 10' ceiling. In this case, there was no service door or windows in the garage.

Looking at 210.8, there is no mention about readily accessible receptacles. However, if the GFCI for the garage door would trip for whatever reason there would be no access to the interior of the garage since the doors would not open.

I know there are some exceptions for receptacles that are not readily accessible. Does this apply to this situation for the garage door openers?



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/6/11, 7:52 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage GFCI on door openers NEC 2008

All 15 and 20 amp 120 volt receptacles in a garage require GFCI protection. In the 2008 NEC there are no exceptions. From the 2008 NEC:

Quote:
210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.
FPN: See 215.9 for ground-fault circuit-interrupter protection for personnel on feeders.
(A) Dwelling Units. All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through ( shall have ground-fault circuit-interrupter protection for personnel.
(1) Bathrooms
(2) Garages, and also accessory buildings that have a floor located at or below grade level not intended as habitable rooms and limited to storage areas, work areas, and areas of similar use
Reply With Quote
  #3  
Old 10/6/11, 8:07 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Garage GFCI on door openers NEC 2008

No common sense



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #4  
Old 10/6/11, 8:10 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage GFCI on door openers NEC 2008

Quote:
Originally Posted by gliebig View Post
No common sense
This rule also applies to receptacles installed in basements for sump pumps. I wouldn't want my sump pumps to be GFCI protected. The NEC requires you to trust a $100K finished basement with a sump pump to be protected by a $15 GFCI device.
Reply With Quote
  #5  
Old 10/6/11, 8:23 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Garage GFCI on door openers NEC 2008

The code did not require the electrician to put the reset inside the garage.
In that case, where no other door is available to enter, the reset should be on the exterior. On regular garages, we have electricians here putting the reset on the garage ceiling and some better ones putting the reset on a wall for the opener outlets.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #6  
Old 10/6/11, 8:25 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Garage GFCI on door openers NEC 2008

Quote:
Originally Posted by Robert Meier View Post
This rule also applies to receptacles installed in basements for sump pumps. I wouldn't want my sump pumps to be GFCI protected. The NEC requires you to trust a $100K finished basement with a sump pump to be protected by a $15 GFCI device.
I agree. Isn't that a change from the 2005 code?



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #7  
Old 10/7/11, 4:53 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage GFCI on door openers NEC 2008

Quote:
Originally Posted by gliebig View Post
I agree. Isn't that a change from the 2005 code?
Yes the 2005 has an exception for specific locations that didn't require GFCI protection. That exception was removed in the 2008. Since that change there have been many proposals to put back some of the exceptions, especially for sump pumps, but the CMP has rejected every one of them.
Reply With Quote
  #8  
Old 10/7/11, 5:35 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,109
Default Re: Garage GFCI on door openers NEC 2008

Our local AHJ does not like this ruling either. I agree with the 2008 NEC because of the location of a sump pit. I have even found legos in one pit area that was being used as a play room. Until they can find a better way this will probably not change.
That being said all sump pumps shoulds have a warning system to alert of failure just like a fire alarm and people should now how to check the GFCI regularly.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #9  
Old 10/7/11, 7:59 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garage GFCI on door openers NEC 2008

The 2011 Article 210.8 now has the requirement that the GFI be readily accessible.
Reply With Quote
  #10  
Old 10/7/11, 8:13 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Garage GFCI on door openers NEC 2008

Quote:
Originally Posted by kwood View Post
Our local AHJ does not like this ruling either. I agree with the 2008 NEC because of the location of a sump pit. I have even found legos in one pit area that was being used as a play room. Until they can find a better way this will probably not change.
That being said all sump pumps shoulds have a warning system to alert of failure just like a fire alarm and people should now how to check the GFCI regularly.
I've seen many single (dedicated) non GFCI Receptacles in the location for the sump pump. In theory, this would only allow the sump pump to be plugged in.

Quote:
Originally Posted by bking View Post
The code did not require the electrician to put the reset inside the garage.
In that case, where no other door is available to enter, the reset should be on the exterior. On regular garages, we have electricians here putting the reset on the garage ceiling and some better ones putting the reset on a wall for the opener outlets.
I really like this "work around", but it's even better to see the change in the NEC 2011 code reported by Jim Port.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #11  
Old 10/18/11, 10:58 AM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Garage GFCI on door openers NEC 2008

What many of the electrical contractors are doing around here to get around this ridiculous code is making the garage door and sump outlets Dedicated. By being a dedicated outlet they do not need to be GFCI protected.

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
  #12  
Old 10/18/11, 11:08 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Garage GFCI on door openers NEC 2008

Quote:
Originally Posted by jkeilson View Post
What many of the electrical contractors are doing around here to get around this ridiculous code is making the garage door and sump outlets Dedicated. By being a dedicated outlet they do not need to be GFCI protected.

Jim
I agree totally!



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #13  
Old 10/18/11, 12:15 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Garage GFCI on door openers NEC 2008

What's wrong with getting out of the car and walking through the main entry to access the garage and reset the GFCI?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Mississippi? Check out InterNACHI's listing of Mississippi certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 10/18/11, 12:28 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Garage GFCI on door openers NEC 2008

Quote:
Originally Posted by jfunderburk View Post
What's wrong with getting out of the car and walking through the main entry to access the garage and reset the GFCI?
If you read my original post, there is no service door to this detached garage and no windows. Kinda tough to do what you suggest in your post.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #15  
Old 10/18/11, 12:32 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Garage GFCI on door openers NEC 2008

Quote:
Originally Posted by gliebig View Post
If you read my original post, there is no service door to this detached garage and no windows. Kinda tough to do what you suggest in your post.
There's your defect. Who wants to roll up the door every time you need to enter the building?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
attached garage ghelder General Inspection Discussion 5 2/23/10 5:40 PM
Attached Garage Fire Containment. Please proof this new inspection article. gromicko General Inspection Discussion 38 8/12/09 6:55 PM
How far from the outlet can the GFCI be? kshepard Electrical Inspections 31 8/11/07 1:52 PM
UL Information about Testing of GFCIs jtedesco1 Electrical Inspections 0 2/5/06 4:38 PM


All times are GMT -4. The time now is 9:39 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts