Default garage panel sheetrock

How much sheetrock is required on walls adjacent to garage panels?

New house, has 3 feet+ on right side, top and bottom but only 1 inch at left side.

Code reference?

thanks!

added with edit: question does not pertain to working space, simply sheetrock on exterior garage walls around panels.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937

Last edited by bking; 9/15/07 at 1:11 AM..
Reply With Quote
  #2  
Old 9/14/07, 8:49 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: garage panel sheetrock

There is no electrical requirement to have any wall covering in place.
Reply With Quote
  #3  
Old 9/14/07, 9:01 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: garage panel sheetrock

Quote:
Originally Posted by Mike Whitt
There is no electrical requirement to have any wall covering in place.
The only requirement as far as wall installation is working space...

Attachment 14522

Last edited by dvalley; 10/7/07 at 5:40 PM..
Reply With Quote
  #4  
Old 9/14/07, 11:58 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: garage panel sheetrock

But my understanding is that 30" requirement is not a fixed dimension. In other words, it can be 30" from the left edge of the panel and extending out to the right. I don't think there's anything wrong with 1" clearance on the left.
Reply With Quote
  #5  
Old 9/15/07, 12:48 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: garage panel sheetrock

The question is not about working space...

Simply sheetrock around garage panels for fireblocking or cable protection issues.

Must be a code reason somewhere because even the cheapest builders will put some drywall around the garage panel, even when on an exterior wall.

Here is a discussion about this... but still no code reason to have it....
http://boards.hgtv.com/eve/forums/a/...2/m/7351097013



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937

Last edited by bking; 9/15/07 at 1:05 AM..
Reply With Quote
  #6  
Old 9/15/07, 1:01 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: garage panel sheetrock

OK then, are you saying that the rest of the garage is not rocked? Why would putting up a little sheetrock around an electrical panel provide any fireblocking? I guess I can't quite see the scenario so I'll bow out gracefully now before I confuse myself any further.
Reply With Quote
  #7  
Old 9/15/07, 1:14 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: garage panel sheetrock

Only the garage walls adjacent to the living space are covered.

Around here they put a sheet up around the panel.
Maybe just for a better fit for the panel cover?

Just thought of a good reason, this helps prevent access to the panel knockouts and discourages homeowner wiring.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #8  
Old 9/15/07, 2:40 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: garage panel sheetrock

Is there a local requirement for this? It certainly isn't required in my area.
Reply With Quote
  #9  
Old 9/15/07, 9:32 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: garage panel sheetrock

Quote:
Originally Posted by bking
Must be a code reason somewhere because even the cheapest builders will put some drywall around the garage panel, even when on an exterior wall.
I'll quote Mike here:
Quote:
There is no electrical requirement to have any wall covering in place.
If they are specifically doing it in your area then there is either a local requirement for it, or they just feel like it.
Reply With Quote
  #10  
Old 9/15/07, 5:29 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: garage panel sheetrock

It has to be for protection of the romexes leaving the panel.
Reply With Quote
  #11  
Old 9/15/07, 7:11 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: garage panel sheetrock

Quote:
Originally Posted by brian winkle
It has to be for protection of the romexes leaving the panel.
From what?????
Reply With Quote
  #12  
Old 9/15/07, 8:10 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: garage panel sheetrock

Quote:
Originally Posted by Mike Whitt
From what?????
rakes, shovels, bikes, saws, ladders, dogs, whatever you keep in the garage.

A panel mounted to the studs with no sheetrock around it would have exposed home runs. Around here it would fail a final inspection, the conductors at that height would be considered subject to damage. Also, I am certain the IRC, which is used by our local building inspectors, prohibits exposed Romex less than 7 feet from the floor.
Reply With Quote
  #13  
Old 9/15/07, 9:18 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: garage panel sheetrock

Quote:
Originally Posted by brian winkle
... Also, I am certain the IRC, which is used by our local building inspectors, prohibits exposed Romex less than 7 feet from the floor.
Then you area also certainly wrong. No such language exists in the IRC.

Feel free to call out exposed romex if it gives you warm fuzzies to do so, but it meets the letter of the NEC and the IRC. I'm sure someone's bound to point out that you're held to a different standard as home inspectors, existance of local rules, blah, blah, blah...
Reply With Quote
  #14  
Old 9/15/07, 9:43 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: garage panel sheetrock

Then it must be a local thing, I know we are never allowed exposed Romex where it is low enough to be possibly damaged. I guess our inspectors are mis interpereting 300.4

I'd sure like to know where the 7 foot rule came from, it is used by all of our county & city inspectors. I do not see it in our NEC ammendments.

P.S. I am not the guy who calls it out, I am the guy who gets called out to fix it!
Reply With Quote
  #15  
Old 9/15/07, 11:01 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: garage panel sheetrock

I believe there is a code about not having exposed wiring within 6 or 7 feet of attic stairs or scuttles.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
One panel in the garage pmagrone Electrical Inspections 30 8/2/07 6:32 PM
sheetrock dust in distribution panel jweinberg Electrical Inspections 5 10/12/06 12:43 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 1:35 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts