Should a garbage disposal receptacle be GFCI protected. It is a switched receptacle but it is also within 6 feet of the sink (though underneath). I have always worked on the assumption that it should be even though it is switched.

Sam
Reply With Quote
  #2  
Old 8/4/08, 3:28 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garbage Disposal GFCI ??

If the disposal is on a wet bar or laundry sink then it would require GFCI protection.

If the disposal is for the kitchen sink then it would not require GFCI protection.
Reply With Quote
  #3  
Old 8/4/08, 8:50 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garbage Disposal GFCI ??

Mike are you assuming cord and plug connected? (as the OP specified)
If so he is pointing out that 210.8(A)(6) <kitchen in a dwelling> only requires GFCI on the receptacles serving the countertop but (7) <laundry, utility and wet bar sinks> does not make the countertop distinction and just says where the receptacles are installed within 6 feet.
A hard wired disposal in a wet bar sink would not require GFCI
Reply With Quote
  #4  
Old 8/4/08, 11:16 PM
Mark Thorman Mark Thorman is offline
Active Poster
 
Join Date: Mar 2008
Posts: 166
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garbage Disposal GFCI ??

99 and 02 codes state: Wet Bar Sinks. Where the receptacles are installed to serve the countertop surfaces and are located within 6 ft. of the outside edge of the wet bar sink. I don't have the other code books on hand.

www.mauihomeinspections.com
Reply With Quote
  #5  
Old 8/4/08, 11:53 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garbage Disposal GFCI ??

2008 cycle
(7) Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink

You do make a point though of if it was in compliance when it was installed it is still in compliance today
Reply With Quote
  #6  
Old 8/5/08, 1:14 AM
Mark Thorman Mark Thorman is offline
Active Poster
 
Join Date: Mar 2008
Posts: 166
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garbage Disposal GFCI ??

Quote:
Originally Posted by Mike Whitt
You do make a point though of if it was in compliance when it was installed it is still in compliance today
I do and I will recommend upgrades to the current standards noting that the upgrades are not required. I also include a little blurb about the importance of GFCI protected outlets.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
More GFCI info from U/L Greg Fretwell Electrical 9 12/4/07 9:33 PM
GFCI Safety Notice rcooke Electrical 1 10/30/07 1:29 PM
Garbage Disposal Trap? bkelly2 Plumbing 1 1/17/07 3:54 AM
The question asked on the new HI Study test here? jtedesco1 Electrical 28 10/4/06 10:31 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 9:01 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts