Default Garbage Disposal Wiring

I would like an opinion on a few of these pictures. GarbageDisposal1 had the Romex properly clamped at the disposal, but there was no junction box visible (just a hole in the drywall). ..2, 3, and 4 serviced a dishwasher and the disposal. Obviously, the romex was not properly clamped, the j-box was loose. There were staples...Hummm I think that's not quite right.

Just would like to hear back how others may report these situations.

Thanks in advance for your help!
Attached Thumbnails
garbage-disposal-wiring-garbagedisposer1.jpg   garbage-disposal-wiring-garbagedisposal2.jpg   garbage-disposal-wiring-grabagedisposal3.jpg   garbage-disposal-wiring-garbagedisposal4.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowlege will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Follow Us on Facebook
Follow Us on Linked-In
Reply With Quote
Find an InterNACHI certified Maryland Home Inspector (and anywhere else in North America)
  #2  
Old 7/14/09, 8:47 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garbage Disposal Wiring

Improperly wired
I recommend a Licensed Electrician examine and evaluate .
Reply With Quote
  #3  
Old 7/14/09, 8:50 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 6,342
Default Re: Garbage Disposal Wiring

Quote:
Originally Posted by relliott View Post
Improperly wired
I recommend a Licensed Electrician examine and evaluate .

How about if the qualified professional just repairs it. You have already evaluated it as improper, n'est pas?



____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 7/14/09, 9:02 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garbage Disposal Wiring

Quote:
Originally Posted by lkage View Post
How about if the qualified professional just repairs it. You have already evaluated it as improper, n'est pas?
Same idea, as he will obviously be the one to make repairs.
Since you like detail , lets hear yours
Reply With Quote
  #5  
Old 7/14/09, 9:09 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 515
Default Re: Garbage Disposal Wiring

Electrical feeder for garbage disposal is not properly secured. This could lead to problems including electrical shorts if something would snag the cable. Recommend repairs by a licensed electrician or other qualified individual.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowlege will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Follow Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #6  
Old 7/14/09, 9:15 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garbage Disposal Wiring

I prefer.. Conductors are a fire hazard as routed and need to be reinstalled by a licensed and certified Electrician .

(damn I hate that Romex stuff)
Reply With Quote
  #7  
Old 7/14/09, 9:17 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 6,342
Default Re: Garbage Disposal Wiring

Improper and amateurish wiring noted (see photos) for dishwasher and disposal under kitchen sink. Recommend repairs by qualified professional as needed for safety.



____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #8  
Old 7/14/09, 9:31 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 359
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garbage Disposal Wiring

The cable exiting the wall is not an issue.

There should have been a cable clamp screwed into the bottom of the disposal.

Non-metallic cable is not for use with cord caps.
Reply With Quote
  #9  
Old 7/14/09, 9:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,440
Default Re: Garbage Disposal Wiring

Quote:
Originally Posted by lkage View Post
How about if the qualified professional just repairs it.
EXACTLY!!

Word it however you feel fit, but finish it with "should be repaired by a qualified electrician."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 7/15/09, 5:14 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,661
Default Re: Garbage Disposal Wiring

that guy Harry sure does get around



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #11  
Old 7/15/09, 7:30 PM
Mark Thorman Mark Thorman is online now
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 212
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Garbage Disposal Wiring

Quote:
Originally Posted by bgraham View Post
that guy Harry sure does get around

I think it's a franchize.

www.MauiHomeInspections.com
Reply With Quote
  #12  
Old 7/19/09, 12:50 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Garbage Disposal Wiring

This is actually a great thread in that those are some common things we see DIYers do. Jim is 100% correct in that those NM Cables are not Flexible Cord and that alone warrants a call out. The connection to the Disposal is incorrect as you all know and will be called out at the same time.

The way the NM Cable is run in itself is subject to physical damage as they could have routed it in a way that would be less subject in nature so that also is called out.

Report : Observations of serious electrical defects under your kitchen sink will warrant an evaluation by a licensed electrical contractor. Nonmetallic cable is being installed in areas subject to physical damage, used in an improper manner as a flexible cord to the disposal and without properly being secured to the disposal itself.



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garbage disposal acox General Inspection Discussion 37 1/10/09 10:02 AM
Garbage Disposal GFCI ?? sbenson Electrical 5 8/5/08 12:14 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 12:35 PM
Garbage Disposal Trap? bkelly2 Plumbing 1 1/17/07 2:54 AM


All times are GMT -4. The time now is 2:46 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts