There is no Bond/ground on the gas line in this home.
What the IRC or NEC code# on this? The 220 range oven was drop from teh build and a 120v gas cook top was installed. Make wonder if it is bonded anywhere. SLAB home so no crawlspace to see if it was done in a hidden areas. thoughts please. Thanks Curt Last edited by cgoyette; 2/7/08 at 9:41 PM.. |
|
#2
|
||||
|
||||
|
2003 IRC E3509.7 Bonding other metal piping. Where installed in or attached to a building or structure, metal piping systems, including gas piping, capable of becoming energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where sufficient size, or to one or more grounding electrodes used. The bonding jumper shall be sized in accordance with Table E3808.12 using the rating of the circuit capable of energizing the piping. The equipment grounding conductor for the circuit that is capable of energizing the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.
|
|
#3
|
||||
|
||||
|
The bonding is achieved through the gas valve and cabinet metal to the EGC (green wire spliced to the copper) inside the furnace.
If no furnace or equipment is present to allow for a mechanical bond to the EGC then it is incorrect. Starting in Sept. 2007, many AHJ's around here require a clamp and solid #6 copper running to the main existing grounding electrode if CSST is used. The black coated CSST (counterstrike) is exempt from this additional bonding. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#4
|
|||
|
|||
|
Please Note:
cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
In this case I dont see any bonding at the gas cook top. There is NO furnance (heat pumps) CSST I can find no Bonding of either. What would be the fix? Curt |
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#6
|
|||
|
|||
|
Please Note:
cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Whats the fix anyone? Curt |
|
#7
|
||||
|
||||
|
You can't clamp anything onto the CSST (that I know of yet)
The cooktop should have the EGC connected to the metal frame which in turn connects to the gas line. This is just not visible and makes our job hard or actually easy in this case, just report no bonding visible as is typical and recommend a safety upgrade. Note: a seperate/new ground rod placed by the gas meter and bonded to the gas pipe is not correct. It has to be what they call equipotential, which means connected to the main electrical GEC or ground rod. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#8
|
|||
|
|||
|
Please Note:
cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
In this case I may be in luck....the main ground rod is about 5 feet away. Could this be just connected here and solve this issue? I know what I am going to say but I want to know what is the right answer on this. Curt |
|
#9
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
I really wasn't trying to be flip about this. I always thought you guys were not supposed to give recommendations, only call out the issues.
|
|
#10
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
The answer to your question is in the IRC quote above:
"The equipment grounding conductor for the circuit that is capable of energizing the piping shall be permitted to serve as the bonding means." This should be all you need to know, unless a local ammendment requires an external bond. |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
||||
|
||||
|
Since we are not required to dismantle equipment and verify the bonding is really connected you can't say there is a problem, unless of course it is a new house that falls under a new code amendment that requires supplemental bonding like we have in Mecklenburg county NC and Lancaster county SC. Don't think York county SC has made any changes for CSST.
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#13
|
|||
|
|||
|
Please Note:
cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Curt |
|
#14
|
||||
|
||||
|
Quote:
|
|
#15
|
||||
|
||||
|
Nope, the gas water heater has no branch circuit EGC so it depends on the little wirenut that may be loose or forgotten inside the furnace or oven power connection box for its bonding.
This is why new codes are emerging for this, it was just a poor equipotential installation before the changes. In places that require the bonding clamp at the power meter, make sure they scraped off the heavy gray paint that is used in many cases before clamping, or the connection could be useless. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Selected Electrical Incidents and Occurrences - First Quarter | pabernathy | Electrical Inspections | 0 | 12/2/07 1:43 PM |
| 1 condensate line...... | Scott Schultz | Inspecting HVAC Systems | 2 | 11/4/07 6:18 AM |
| Size of supply line | aobrien | Inspecting HVAC Systems | 7 | 1/2/07 12:40 PM |
| Gas line & Supply Line | thejnicki | Plumbing Inspections | 2 | 9/13/06 9:24 AM |
| TPRV line and condensate line marriage | ccarrington | Plumbing Inspections | 3 | 4/29/06 7:59 AM |