Default GE 200 amp 4/0 alum main

Any issues with all of the spliced wires? They were done to hook up the generator. This is a 1978 home.
Attached Thumbnails
ge-200-amp-4-0-alum-main-dsc061925920.jpg   ge-200-amp-4-0-alum-main-dsc061915919.jpg   ge-200-amp-4-0-alum-main-dsc061905918.jpg  



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Find an InterNACHI certified West Virginia Home Inspector (and anywhere else in North America)
  #2  
Old 6/17/09, 8:05 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: GE 200 amp 4/0 alum main

55 views and no input.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #3  
Old 6/17/09, 8:11 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: GE 200 amp 4/0 alum main

Splices are ok in a panel, not really much choice when adding a generator panel.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #4  
Old 6/18/09, 10:43 AM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: GE 200 amp 4/0 alum main

thanks Bruce. just needed to confirm.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #5  
Old 6/20/09, 1:06 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GE 200 amp 4/0 alum main

Did you comment on the other issues within the panel?



Paul W. Abernathy
Reply With Quote
  #6  
Old 6/20/09, 6:15 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: GE 200 amp 4/0 alum main

Quote:
Originally Posted by pabernathy View Post
Did you comment on the other issues within the panel?
I did to a degree. Different brand of breakers installed, AC breakers are too large, no clearance in front or the sides due to cabinet, white wires being used as hot lines, antioxidant needed at mains, and wiring not done in neat workmanlike manner.

There is probably some more and that is why I am anxious to take your NACHI TV course I see that's being put together.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #7  
Old 6/20/09, 6:17 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: GE 200 amp 4/0 alum main

Also noticed that the grounds and neutrals are on the same bus bar for a few of the wires.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #8  
Old 6/21/09, 10:47 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GE 200 amp 4/0 alum main

I dont know that we covered any more than the issues you found. The video is not all encompasing so I am sure things will be left out......which is why I am doing a book and an article based thing as well.....to ask questions.

Interesting enough......."antioxidant needed at mains" is not always the case. If the manufacture states that Antioxidant is needed then it must be used and the right kind must be used. Other than that it is not always required to have antioxident on service conductors even if aluminum.

110.14 Electrical Connections.
Because of different characteristics
of dissimilar metals, devices such as pressure
terminal or pressure splicing connectors and soldering lugs
shall be identified for the material of the conductor and
shall be properly installed and used. Conductors of dissimilar
metals shall not be intermixed in a terminal or splicing
connector where physical contact occurs between dissimilar
conductors (such as copper and aluminum, copper and
copper-clad aluminum, or aluminum and copper-clad aluminum),
unless the device is identified for the purpose and
conditions of use. Materials such as solder, fluxes, inhibitors,
and compounds, where employed, shall be suitable for
the use and shall be of a type that will not adversely affect
the conductors, installation, or equipment.




Paul W. Abernathy
Reply With Quote
  #9  
Old 6/23/09, 8:35 PM
jack Davenport jack Davenport is offline
New User
 
Join Date: Jun 2009
Posts: 7
Please Note: jack Davenport is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GE 200 amp 4/0 alum main

If this is the main panel it is ok to have the neutrals and grounds on the same bar.
Only need to separate them if it's a subpanel.
Reply With Quote
  #10  
Old 6/25/09, 2:09 AM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,224
Default Re: GE 200 amp 4/0 alum main

Are those different types of breakers (newer) allowed by the manufacturer? I wish I could zoom-in on those pictures, but some look like Square D breakers? I can't see GEC. The wire nut connecting a black and white wire is a concern (near breaker #2). Is white wire being properly identified or used as a "hot"?



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book

Last edited by bgromicko; 6/25/09 at 2:12 AM..
Reply With Quote
  #11  
Old 6/25/09, 6:42 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: GE 200 amp 4/0 alum main

Quote:
Originally Posted by jack Davenport View Post
If this is the main panel it is ok to have the neutrals and grounds on the same bar.
Only need to separate them if it's a subpanel.

I'm sure he meant "same screw" not "same bus bar".

Double lugging.
Reply With Quote
  #12  
Old 6/25/09, 10:23 PM
Ben J. Gromicko's Avatar
Ben J. Gromicko Ben J. Gromicko is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Boulder, CO
Posts: 2,224
Default Re: GE 200 amp 4/0 alum main

Check out http://www.nachi.org/electrical-pane...-challenge.htm



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shut off valves required? jcahill Plumbing Inspections 11 9/2/08 1:07 AM
Neutral bus bar failed inspection Greg Moritz Electrical Inspections 18 1/19/08 1:53 PM
Main Electrical Shut-off? jpassailaigue General Inspection Discussion 10 3/24/06 2:19 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 3:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts