I have seen this upper bus bar discoloration on 3 or 4 GE panels (some interior and some exterior) and always recommend an electrician.
This time I spent some extra time and checked for abnormal heat after running some larger loads (A/C and oven) and no heat buildup was found. Townhome, 200A panel, gas heat, gas water heater. Panel is located at exterior but very clean inside. Anything else besides bad connection/heat to cause this? Note, it may look like rust in the picture but does not in person, just discoloration. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#2
|
||||
|
||||
|
Bruce , I am not a chemist but wonder if it could be a chemical reaction off the feeder.
Did you notice if they were all Aluminum? |
|
#3
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
What size is the wire into the lugs at the 200 A OCD?
Were they torqued properly? Do you wear PPE? |
|
#4
|
||||
|
||||
|
Quote:
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#5
|
||||
|
||||
|
Quote:
4/0 Didn't check torque but could not move the wires in the lugs or feel any heat with a good load. of course B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#6
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Joe Is there really any way that the torque requirement is a Home Inspector's responsibility? This is not something that any inspector should or could be looking for. Not to be a pain, but there are limits to certain items. Torqueing is performed at the time of installation. Maybe a Thermal image test can be performed...again, is that the HI's responsibility? |
|
#7
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Bruce may have looked at the instructions in his panelboard like these and if he simply mentioned the torque requirements, he would have done what anyone would expect of a professional.
I would admire that type of home inspector, and as far as the thermal image testing, some here are now becomong experts on this testing procedure and may have some images that could be included in a report, just to give another method of inspection. Burns and Other Injuries Shock-related injuries include burns, internal injuries, and injuries due to involuntary muscle contractions.Burns The most common shock-related injury is a burn. Burns suffered in electrical incidents may be one or more of the following three types:
Warning: Please be advised these images are of a graphic nature.
Photo Example Warning: Please be advised these images are of a graphic nature.
Photo Example Warning: Please be advised these images are of a graphic nature.Internal Injuries Excessive electricity flowing through the human body can cause serious damage to internal organs. Resulting medical problems include hemorrhage (or internal bleeding), tissue destruction, and nerve or muscle damage. These internal injuries may not be immediately apparent to the victim or observers; however, left untreated, they can result in death. Photo Example Warning: Please be advised these images are of a graphic nature.Involuntary Muscle Contraction Normal muscle contraction is caused by very small amounts of electricity that are created within our bodies. Muscles violently contract when stimulated by excessive amounts of electricity. These involuntary contractions can damage muscles, tendons, and ligaments, and may even cause broken bones. If the victim is holding an electrocuting object, hand muscles may contract, making it impossible to drop the object and prolonging contact with the current. Also, injury or death may result when violent muscle contractions cause workers to fall from ladders and scaffolds or inadvertently strike other objects.Photo Example Warning: Please be advised these images are of a graphic nature. Last edited by jtedesco1; 5/11/08 at 11:01 PM.. |
|
#8
|
||||
|
||||
|
Joe T.,
I'm of the opinion that the HI has no business speculating on the cause of the discoloration when he writes his report. The cause could be several things. The observed conditions only indicate that something may be wrong either now or in the past and that a qualified electrician should repair it as needed. I guess that means I now lack your admiration. Oh well. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#9
|
||||
|
||||
|
Corrosion caused by dissimilar metals. They used to coat the lugs with grease to prevent this condition.IMO
|
|
#10
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Much ado about nothing. Those GE 200 amp mains are that way from brand spanking new. Here's a pic of a brand new, never installed, one right off the shelf:
![]() Quote:
Last edited by Marc D. Shunk; 5/11/08 at 7:35 PM.. |
|
#11
|
||||
|
||||
|
Thanks Marc. Good info.
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#12
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
This publication includes information that mentions overheating and shows examples, some of which are with the same defects shown in the pictures here: NEMA Standards Publication AB 4-2003 Guidelines for Inspection and Preventive Maintenance of Molded Case Circuit Breakers Used in Commercial and Industrial Applications Published by: National Electrical Manufacturers Association |
|
#13
|
||||
|
||||
|
Maybe the discoloration was caused by the welding process where they welded the bars behind the breaker.
The interesting thing is that not all of these exact same parts have the discoloration present. I have two of these panels/mains and neither are like that. Its nothing to do with lack of dielectric grease, not needed with these SE cables anymore. Also its an AL to AL connection. Joe, I wonder if the IR camera guys know to run EACH and every load for a period of time before checking for ecessive heat. No load current = no heat, even with a bad breaker or bad connection. Since most homes have nothing available to load the 15 and 20 amp branch circuits you will have to carry a load device with you. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#14
|
||||
|
||||
|
Quote:
A professional WHAT? The inspector's responsibility is to observe and report the apparent conditions visible at the time of the inspection. I dont know why something may be discolored. I only know that it IS, and report the condition. |
|
#15
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
That's it Joe you got it!
"The inspector's responsibility is to observe and report the apparent conditions visible at the time of the inspection. I don't know why something may be discolored. I only know that it IS, and report the condition." Good Boy Joe! This is a "Statement made by a professional!" |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |