Default GE panel opinions

I have seen this upper bus bar discoloration on 3 or 4 GE panels (some interior and some exterior) and always recommend an electrician.

This time I spent some extra time and checked for abnormal heat after running some larger loads (A/C and oven) and no heat buildup was found.

Townhome, 200A panel, gas heat, gas water heater. Panel is located at exterior but very clean inside.

Anything else besides bad connection/heat to cause this?
Note, it may look like rust in the picture but does not in person, just discoloration.
Attached Thumbnails
ge-panel-opinions-may-7-2008-002.jpg   ge-panel-opinions-may-7-2008-003.jpg  



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #2  
Old 5/7/08, 5:41 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: GE panel opinions

Bruce , I am not a chemist but wonder if it could be a chemical reaction off the feeder.
Did you notice if they were all Aluminum?
Reply With Quote
  #3  
Old 5/7/08, 6:17 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GE panel opinions

What size is the wire into the lugs at the 200 A OCD?

Were they torqued properly?

Do you wear PPE?
Reply With Quote
  #4  
Old 5/7/08, 6:28 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: GE panel opinions

Quote:
Originally Posted by relliott
Bruce , I am not a chemist but wonder if it could be a chemical reaction off the feeder.
Did you notice if they were all Aluminum?
yes all AL



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #5  
Old 5/7/08, 6:30 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: GE panel opinions

Quote:
Originally Posted by jtedesco1
What size is the wire into the lugs at the 200 A OCD?

Were they torqued properly?

Do you wear PPE?

4/0

Didn't check torque but could not move the wires in the lugs or feel any heat with a good load.

of course



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #6  
Old 5/11/08, 3:02 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GE panel opinions

Quote:
Originally Posted by jtedesco1
What size is the wire into the lugs at the 200 A OCD?

Were they torqued properly?

Do you wear PPE?

Joe
Is there really any way that the torque requirement is a Home Inspector's responsibility?

This is not something that any inspector should or could be looking for.


Not to be a pain, but there are limits to certain items. Torqueing is performed at the time of installation.
Maybe a Thermal image test can be performed...again, is that the HI's responsibility?
Reply With Quote
  #7  
Old 5/11/08, 3:57 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GE panel opinions

Bruce may have looked at the instructions in his panelboard like these and if he simply mentioned the torque requirements, he would have done what anyone would expect of a professional.

I would admire that type of home inspector, and as far as the thermal image testing, some here are now becomong experts on this testing procedure and may have some images that could be included in a report, just to give another method of inspection.

Burns and Other Injuries

Shock-related injuries include burns, internal injuries, and injuries due to involuntary muscle contractions.Burns

The most common shock-related injury is a burn. Burns suffered in electrical incidents may be one or more of the following three types:
  • Electrical burns cause tissue damage, and are the result of heat generated by the flow of electric current through the body. Electrical burns are one of the most serious injuries you can receive and should be given immediate attention.
Photo Example

Warning:
Please be advised these images are of a graphic nature.
  • High temperatures near the body produced by an electric arc or explosion cause arc or flash burns. They should also be attended to promptly.

Photo Example


Warning:
Please be advised these images are of a graphic nature.
  • Thermal contact burns occur when skin comes in contact with overheated electric equipment, or when clothing is ignited in an electrical incident.

Photo Example


Warning:
Please be advised these images are of a graphic nature.Internal Injuries
Excessive electricity flowing through the human body can cause serious damage to internal organs. Resulting medical problems include hemorrhage (or internal bleeding), tissue destruction, and nerve or muscle damage. These internal injuries may not be immediately apparent to the victim or observers; however, left untreated, they can result in death. Photo Example

Warning:
Please be advised these images are of a graphic nature.Involuntary Muscle Contraction

Normal muscle contraction is caused by very small amounts of electricity that are created within our bodies. Muscles violently contract when stimulated by excessive amounts of electricity. These involuntary contractions can damage muscles, tendons, and ligaments, and may even cause broken bones. If the victim is holding an electrocuting object, hand muscles may contract, making it impossible to drop the object and prolonging contact with the current. Also, injury or death may result when violent muscle contractions cause workers to fall from ladders and scaffolds or inadvertently strike other objects.Photo Example

Warning:
Please be advised these images are of a graphic nature.

Last edited by jtedesco1; 5/11/08 at 11:01 PM..
Reply With Quote
  #8  
Old 5/11/08, 4:59 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GE panel opinions

Joe T.,

I'm of the opinion that the HI has no business speculating on the cause of the discoloration when he writes his report.

The cause could be several things.

The observed conditions only indicate that something may be wrong either now or in the past and that a qualified electrician should repair it as needed.

I guess that means I now lack your admiration. Oh well.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #9  
Old 5/11/08, 6:54 PM
klott's Avatar
klott klott is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: monroe, ga
Posts: 8,707
Default Re: GE panel opinions

Corrosion caused by dissimilar metals. They used to coat the lugs with grease to prevent this condition.IMO
Reply With Quote
  #10  
Old 5/11/08, 7:30 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GE panel opinions

Much ado about nothing. Those GE 200 amp mains are that way from brand spanking new. Here's a pic of a brand new, never installed, one right off the shelf:



Quote:
Originally Posted by bking
I have seen this upper bus bar discoloration on 3 or 4 GE panels (some interior and some exterior) and always recommend an electrician.
Probably was the prudent thing to do, but in this case it was an "oops!". The electrician probably sold them a service upgrade or panel change to get rid of their junk GE equipment.

Last edited by Marc D. Shunk; 5/11/08 at 7:35 PM..
Reply With Quote
  #11  
Old 5/11/08, 7:31 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GE panel opinions

Thanks Marc. Good info.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #12  
Old 5/12/08, 7:20 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GE panel opinions

This publication includes information that mentions overheating and shows examples, some of which are with the same defects shown in the pictures here:

NEMA Standards Publication AB 4-2003
Guidelines for Inspection and Preventive Maintenance
of Molded Case Circuit Breakers Used in
Commercial and Industrial Applications
Published by:
National Electrical Manufacturers Association
1300 North 17th Street, Suite 1847
Rosslyn, Virginia 22209
www.nema.org

Reply With Quote
  #13  
Old 5/12/08, 8:39 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: GE panel opinions

Maybe the discoloration was caused by the welding process where they welded the bars behind the breaker.

The interesting thing is that not all of these exact same parts have the discoloration present. I have two of these panels/mains and neither are like that.


Its nothing to do with lack of dielectric grease, not needed with these SE cables anymore. Also its an AL to AL connection.

Joe,
I wonder if the IR camera guys know to run EACH and every load for a period of time before checking for ecessive heat. No load current = no heat, even with a bad breaker or bad connection. Since most homes have nothing available to load the 15 and 20 amp branch circuits you will have to carry a load device with you.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #14  
Old 5/12/08, 12:34 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: GE panel opinions

Quote:
Bruce may have looked at the instructions in his panelboard like these and if he simply mentioned the torque requirements, he would have done what anyone would expect of a professional.
Joe T, we've been down this road no fewer than a couple of times before. Please explain how mentioning the torque requirements after making an observation is "what anyone would expect of a professional".

A professional WHAT?

The inspector's responsibility is to observe and report the apparent conditions visible at the time of the inspection. I dont know why something may be discolored. I only know that it IS, and report the condition.
Reply With Quote
  #15  
Old 5/12/08, 2:47 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GE panel opinions

That's it Joe you got it!

"The inspector's responsibility is to observe and report the apparent conditions visible at the time of the inspection. I don't know why something may be discolored. I only know that it IS, and report the condition."

Good Boy Joe!

This is a "Statement made by a professional!"
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 3:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts