I ran across this panel at a recent inspection. The feed wire is 10ga, coming from a 2 pole 30amp breaker in the main panel, labeled water heater which in turn feeds the water heater thru the 30 amp breaker on the left which doesn't seem to be a problem. Numerous other problems in the panel can be found and commented on but the one item of concern that I was not certain of is this:
The 50 amp breaker and wiring on the right feeds a pole barn/garage but as I see it could only receive 30 amps of power due to the 30 amp breaker in the main panel. Again, no problem?
In the pole barn however, is a generator hook-up that is set-up to back feed power thru this 50 amp connection at this panel and back up to the main panel thru the 10ga wire and 30 amp breaker.
My question is, does this 30amp breaker in the main panel protect the 10 ga wire or is there potential to overheat this wiring?
My comment was: "In my opinion, this would create an unsafe condition and I would advise that this system not be used until a qualified electrician reviews and approves this set-up."
Would welcome any comments on the generator set-up thru this panel.
Attached Thumbnails
generator-hook-up-100_0209.jpg  



Gary Bottomley
Northwest Michigan
Home Inspection Services
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/8/10, 8:42 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Generator hook-up

I think you did well, Gary. I see generator back feeds occasionally, and this is not "Professional"

By the way, we havnt met, Welcome to NACHI. How long have you been a member? We are not far out of each others districts.
Reply With Quote
  #3  
Old 9/8/10, 9:34 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator hook-up

The lack of an approved tranfer switch or interlock device is a definite safety issue.

Correction is definitely needed.
Reply With Quote
  #4  
Old 9/8/10, 8:23 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator hook-up

Quote:
Originally Posted by Jim Port View Post
The lack of an approved transfer switch or interlock device is a definite safety issue.

Correction is definitely needed.
I agree, as well as the individual conductors feeding the 50 amp CB.
Reply With Quote
  #5  
Old 9/9/10, 4:12 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Generator hook-up

It does not look like the neutrals and grounds are properly separated either.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 3:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts