A sub-panel for a generator hook up is wired into the main panel where it has a breaker for the generator subpanel. It has 3 blacks and a red going into the breaker. What are they trying to do. The sub-panel has breakers to run certain areas in-case the power goes out.
Gary Porter GLP's Home and Mold Inspections 321-239-0621 Certified Commercial Mold Inspector Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford Orange County, Seminole County, Volusia County, Osceola County www.homeandmoldinspections.com |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Where does the other end of these 4 conductors terminate, exactly? One set may go to lugs of the "normal power" end of a manual transfer switch, and the other set may go to a light bulb or something along those lines so that the HO knows when utility power is restored. Just a guess. No way to say without more information.
|
|
#3
|
||||
|
||||
|
That breaker runs into the generator sub panel. The breaker in the main box reads generator. Isn't this a double tap?
Gary Porter GLP's Home and Mold Inspections 321-239-0621 Certified Commercial Mold Inspector Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford Orange County, Seminole County, Volusia County, Osceola County www.homeandmoldinspections.com |
|
#4
|
||||
|
||||
|
Those look like Square-D breakers that are designed for two conductors.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
Thank you Jeff.
Gary Porter GLP's Home and Mold Inspections 321-239-0621 Certified Commercial Mold Inspector Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford Orange County, Seminole County, Volusia County, Osceola County www.homeandmoldinspections.com |
|
#6
|
||||
|
||||
|
I gave you a greenie.
Gary Porter GLP's Home and Mold Inspections 321-239-0621 Certified Commercial Mold Inspector Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford Orange County, Seminole County, Volusia County, Osceola County www.homeandmoldinspections.com |
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I ask, because if both pairs of conductors terminate on the same pair of lugs in the generator panel, this is an improper installation. Conductors of that small of a gauge are not permitted to be paralleled. Even if the double tap was improper (which it's not in that brand, as has been pointed out), the possible paralleled conductors are an equal or greater hazard. If one set of these conductors feeds the generator panel with 'normal power', and the other set comes from the generator inlet, this is a GIGANTIC red flag waving, jumping up and down, safety hazard. |
|
#8
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Is there a double throw switch or some sort of anti-backfeed device? Possibly a breaker interlock? How is the generator feeding the panel? |
|
#9
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
"Possibly a breaker interlock?"
Since we had Hurricane Juan here 3-4 years ago, (the older part of our city looked like a tornado hit with the number of downed 70-80-100 year old trees) many homeowners are having a generator panel installed. Every generator panel I have seen has two service conductor breaker banks (3 linked breakers for 3 conductors- two hot and the neutral). One bank of breakers is fed from the proper sized double pole breaker in the main panel and the other bank is fed from the properly sized generator. Both banks of 3 breakers are interlocked in an either/or manner- either one or the other can be "on" so that there is no possibility that power can be backfed through the house main panel to the utility lines from the generator while linemen are working on downed lines, etc. |
|
#10
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |