Default Generator suggestion

What size/type generator would you recommend that will start up and run a home that is equipped up to a 5 ton air conditioning system for a period long enough to perform a full home inspection?



Frank Magdefrau
Certified Master Inspector
DeSoto Home Inspection Services, LLC
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
InterNACHI ESOP member from 2004 to 2010

Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/22/10, 3:38 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Generator suggestion

Somewhere around 18kw to 20kw for the 5 ton AC plus whatever else the home requirements are.

http://www.allworlddieselgen.com/faq.htm



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 7/22/10, 4:12 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator suggestion

How do you plan to make the connections between the genset and the house panel?
Reply With Quote
  #4  
Old 7/22/10, 5:50 PM
Frank Magdefrau's Avatar
Frank Magdefrau Frank Magdefrau is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Hernando, MS
Posts: 3,397
Default Re: Generator suggestion

Quote:
Originally Posted by Jim Port View Post
How do you plan to make the connections between the genset and the house panel?
Back feed through the dryer plug.



Frank Magdefrau
Certified Master Inspector
DeSoto Home Inspection Services, LLC
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
InterNACHI ESOP member from 2004 to 2010

Reply With Quote
  #5  
Old 7/22/10, 5:53 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Generator suggestion

Another idea: Hook right into the panel through a breaker, Bring your own if you have to. Be sure the main disconnect is off.
Reply With Quote
  #6  
Old 7/22/10, 5:58 PM
Frank Magdefrau's Avatar
Frank Magdefrau Frank Magdefrau is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Hernando, MS
Posts: 3,397
Default Re: Generator suggestion

Quote:
Originally Posted by mroberson View Post
Another idea: Hook right into the panel through a breaker, Bring your own if you have to. Be sure the main disconnect is off.
Allot of the homes have fuse panels.



Frank Magdefrau
Certified Master Inspector
DeSoto Home Inspection Services, LLC
3152 Big Ben S
Hernando, MS 38632
(901) 486-0421

InterNACHI Member since 2002
InterNACHI message board member since 2003
InterNACHI ESOP member from 2004 to 2010

Reply With Quote
  #7  
Old 7/22/10, 6:06 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Generator suggestion

Sounds sort of risky to me. What if the power is off at the house for a valid reason and you come along and energize it. Better put 911 on speed dial!



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 7/22/10, 6:54 PM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,665
Default Re: Generator suggestion

This is an idea that could very likely end very badly so let's give Frank all the help we can. JK, lol

Frank are you seriously gonna lug a 20 kva generator around and try to back feed it into service panels? If so, pass me some of what you are smoking because I'm having trouble visualizing this.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #9  
Old 7/22/10, 7:00 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator suggestion

Quote:
Originally Posted by fmagdefrau View Post
Back feed through the dryer plug.
If the house AC and all other needs for the inspection happen to hit teh suggested 18 kW, that will be a draw of 75 amps @ 240 volts.......hopefully the 30 amp dryer breaker works as some dryer wire may get fried.

My advice: don't do it!!

Hire an electrician to do this so he will have the liability when something goes wrong!!! Have the electrician remove the meter from the meter box also......can't be too safe......the linemen will respect you!!
Reply With Quote
  #10  
Old 7/22/10, 8:37 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator suggestion

Back feeding a dryer plug is a horrible idea not to mention illegal. Forget to turn off the main and your 120/240 volt generator is sending 7200 volts back over the primary line that someone may be working on to restore the power. A transfer switch or some sort of breaker interlock is what you should use. When using an automatic transfer switch (ATS) the generator is required to be large enough to carry the entire connected load. A manual transfer switch allows the user to select loads as he chooses.

As others have advised I would suggest consulting a licensed electrician before you open yourself up to a huge amount of liability.
Reply With Quote
  #11  
Old 7/22/10, 8:44 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator suggestion

Quote:
Originally Posted by Robert Meier View Post
Back feeding a dryer plug is a horrible idea not to mention illegal. Forget to turn off the main and your 120/240 volt generator is sending 7200 volts back over the primary line that someone may be working on to restore the power. A transfer switch or some sort of breaker interlock is what you should use. When using an automatic transfer switch (ATS) the generator is required to be large enough to carry the entire connected load. A manual transfer switch allows the user to select loads as he chooses.

As others have advised I would suggest consulting a licensed electrician before you open yourself up to a huge amount of liability.
I didn't mention that as everyone on this thread should know that.......but it appeared that it was going to happen anyways......so I tried to protect the linemen.....remove the meter socket as a disconnect!!
Reply With Quote
  #12  
Old 7/22/10, 8:47 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator suggestion

Quote:
Originally Posted by Brian A. MacNeish View Post
I didn't mention that as everyone on this thread should know that.......but it appeared that it was going to happen anyways......so I tried to protect the linemen.....remove the meter socket as a disconnect!!
Yes your idea will offer protection to the linemen but IMO cutting the seal or lock off of the meter enclosure is also a poor idea when you should be installing the system correctly to begin with. Also plugging the meter back live when the utility power is restored isn't such a great idea either.
Reply With Quote
  #13  
Old 7/22/10, 8:49 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 4,965
Send a message via AIM to sstanczyk
Default Re: Generator suggestion

I thought Forest Gump was from Alabama. I guess dumb ideas transcend state borders.

Stupid is as stupid does.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/22/10, 8:58 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator suggestion

I understood that this was only for while the inspection was in progress but, there is no way to run that kind of load thru the dryer plug even if it were legal to do. Find another way to do this or disclaim it.
Reply With Quote
  #15  
Old 7/22/10, 10:03 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator suggestion

Quote:
Originally Posted by Robert Meier View Post
Yes your idea will offer protection to the linemen but IMO cutting the seal or lock off of the meter enclosure is also a poor idea when (1) you should be installing the system correctly to begin with. Also (2) plugging the meter back live when the utility power is restored isn't such a great idea either.
(1) How much will it cost to install a generator transfer switch for a 3-4 hour inspection?

(2) if the house disconnect is in the "off" position, no current will be drawn. I've seen a meter replaced by the utility with the triplex still intact at the masthead. I did not see them disconnect the triplex at the transformer.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 9:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts