  #1  
Old 7/18/10, 10:00 PM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,665
Default Generator transfer switch

I have a standard 30 amp 10 circuit manual generator transfer switch that I want to install. It's pretty straight forward having a tail that you install to the service panel with a ground wire, a neutral wire, and corresponding circuit wire pairs for the ten circuits. Red to the breaker and black to the load side.

I have two, 150 amp Square D main service panels and the loads that I want to back up are split between them. My question is; Can I just splice onto the neutral and ground tails from the transfer switch and extend them up to both service panels or do I have to move the loads that I want to back up into one service panel?

Thanks for any input.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/18/10, 10:24 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator transfer switch

Quote:
Originally Posted by jonofrey View Post
I have a standard 30 amp 10 circuit manual generator transfer switch that I want to install. It's pretty straight forward having a tail that you install to the service panel with a ground wire, a neutral wire, and corresponding circuit wire pairs for the ten circuits. Red to the breaker and black to the load side.

I have two, 150 amp Square D main service panels and the loads that I want to back up are split between them. My question is; Can I just splice onto the neutral and ground tails from the transfer switch and extend them up to both service panels or do I have to move the loads that I want to back up into one service panel?

Thanks for any input.
John:

Don't know your experience in home wiring......but in the past year, I have have called in electricians to correct items found in 2 generator panels installed by homeowners. The crazy thing is the last one was done by the realtor/husband of one of our most successful realtors- I was the inspector for the gent that bought their home.

Hell, they had money......both drove Lexus' and the barely 20 year old son drove an Audi- all very new. Why would they do this themselves??

Be wery, wery careful!!
Reply With Quote
  #3  
Old 7/19/10, 6:52 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Generator transfer switch

I believe Generators must be totally isolated when in use.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #4  
Old 7/19/10, 9:31 AM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,665
Default Re: Generator transfer switch

It looks like I'm going to have to move all of the circuits that I want backed up onto a single panel.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #5  
Old 7/19/10, 10:28 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Generator transfer switch

John
you may want to check with your local utility's some want to know if a generator is going to being used. Being isolated insures linemen do not get zapped.



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #6  
Old 7/19/10, 11:44 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Generator transfer switch

http://www.smps.us/transferswitch.html



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 7/19/10, 1:22 PM
bstenger bstenger is offline
InterNACHI Member
 
Join Date: Jun 2010
Location: cincinnati oh
Posts: 18
Default Re: Generator transfer switch

One thing to remember, u can be sued. The transfer switch should have both an elec. enterlock and a mechanical enterlock which prevents backfeed onto the utility co. lines, if wired correctly. So, the right parts, and the wiring PROPERLY INSTALLED u should be ok. Code wise, it is a sperately derived sys. so treat it as a seperate service to the building, disconnecting means, grounding and bonding etc. the first panel is the service panel, all others are sub-panels, all rules apply.



Bill Stenger
master electrician/licensed elec inspector (oh,KY)
certi. bldg inspector (I.C.C.)
Reply With Quote
  #8  
Old 7/21/10, 11:35 AM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,665
Default Re: Generator transfer switch

Got 'er did! Had to swap a total of ten circuits between panels to put all of the circuits that I wanted to back up onto a single panel.
Attached Thumbnails
generator-transfer-switch-dsc02084.jpg   generator-transfer-switch-dsc02083.jpg  



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #9  
Old 7/21/10, 11:59 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator transfer switch

OK, I see cables missing being properly secured, a panel mounted over steps resulting in improper workspace clearences. Possibly too many breakers in the panel or panels.

A missing stud.

Anyone else?

Last edited by Jim Port; 7/21/10 at 12:04 PM..
Reply With Quote
  #10  
Old 7/21/10, 12:06 PM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,665
Default Re: Generator transfer switch

Quote:
Originally Posted by Jim Port View Post
OK, I see cables missing being properly secured, a panel mounted over steps resulting in improper workspace clearences.

Anyone else?
The cables are wired clamped at the panels. The loose cables you see are actually inside the wall, I installed a door below the panels to facilitate moving circuits from one panel to another. The steps are coming out in favor of a pull down set of stairs. this arrangement is in a garage.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #11  
Old 7/21/10, 12:11 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Generator transfer switch

The cables are still required to be secured at the proper intervals. In your case it would be within 12" of the box and then no more than 4.5' for the NM cables.
Reply With Quote
  #12  
Old 7/21/10, 12:14 PM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,665
Default Re: Generator transfer switch

Quote:
Originally Posted by Jim Port View Post
The cables are still required to be secured at the proper intervals. In your case it would be within 12" of the box and then no more than 4.5' for the NM cables.
The wires are secured within 12" of the box as they are wire clamped at the panel and "J" box.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrocution by 3-Way Switch Wiring? sbarrett Electrical Inspections 4 4/20/10 8:17 PM
Flickering CFL jallingham Electrical Inspections 34 12/5/08 2:40 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Emergency Shut-off switch sfalvey Inspecting HVAC Systems 4 8/18/06 9:11 AM
3 way switches cfuoco Electrical Inspections 4 2/1/06 8:00 PM


All times are GMT -4. The time now is 9:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts