Default GFCI on 2 wire systems

Looking for some help on clarification. My understanding is a GFCI will prevent elec shock in a 2 wire system. I have seen them in bathrooms and kitchens. The part that trips me up is, a 2 wire system is still not grounded. That should be a safety concern, but not unsafe with a GFCI installed. (correct?)
Second part of question, in a home with 2 wire outlets why couldn't a person put GFCIs in all the locations? Like the living room for example. I was ask this question the other day. The occupants would be protected, correct?
Thanks folks.
Reply With Quote
Find an InterNACHI certified Tennessee Home Inspector (and anywhere else in North America)
  #2  
Old 11/9/09, 6:17 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GFCI on 2 wire systems

He can.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #3  
Old 11/9/09, 6:31 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: GFCI on 2 wire systems

I wouldn't say they prevent, but rather that they reduce the potential for someone to get shocked. People can always find ways to electrocute themselves.

Many older homes' electrical systems are not grounded, however, short of fully rewiring the house, GFCI can be an effective way of providing improved protection against shocks and maintain "code" compliance with three prong outlets (use the "no equipment ground" stickers).

As Mike said so succinctly, he can install them on most circuits for enhanced protection. Don't need to install on every outlet, just lead outlet on each circuit. Change the other outlets to three prog, install stickers and he's good to go.

Of course, I would advise him to use a qualified, licensed electrician to do the work vs. Bubba that handy guy.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #4  
Old 11/9/09, 6:34 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by cevans View Post
I wouldn't say they prevent, but rather that they reduce the potential for someone to get shocked. People can always find ways to electrocute themselves.
They prevent a fault current in excess of 5 mA from going through a person.

That is sufficient to prevent electrocution in most of the population.

Those at risk are ones that have a pathway via inter-venous lines or a compromise layer of skin.

GFCI outlets in non three wire systems need to be labeled appropriately.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #5  
Old 11/9/09, 6:36 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: GFCI on 2 wire systems

Tim a grounded system is to protect the equipt and not you.

Not sure I would want a bunch of GFCI outlets with stickers everywhere that no one will pay attention to when they plug things in.

If this place has real conduit, a switch to grounded outlets is easy.
Reply With Quote
  #6  
Old 11/9/09, 6:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GFCI on 2 wire systems

Conduit in Iowa?

Come on Bob get real.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #7  
Old 11/9/09, 6:39 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by mlarson View Post
Conduit in Iowa?

Come on Bob get real.
Do you assume Mike? or have you been there.
I have not.

For all I know they are using Tesla coils to beam it all through space.
Reply With Quote
  #8  
Old 11/9/09, 6:41 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by belliott View Post
Do you assume Mike? or have you been there.
I have not.

For all I know they are using Tesla coils to beam it all through space.
Got relies their Bob.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #9  
Old 11/9/09, 6:46 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,776
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by mlarson View Post
They prevent a fault current in excess of 5 mA from going through a person.

That is sufficient to prevent electrocution in most of the population.

Those at risk are ones that have a pathway via inter-venous lines or a compromise layer of skin.

GFCI outlets in non three wire systems need to be labeled appropriately.
True, but GFCI's are not going to protect the 60" Plasma, microwave oven, computer, fridge,...



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #10  
Old 11/9/09, 7:16 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by mgratton View Post
True, but GFCI's are not going to protect the 60" Plasma, microwave oven, computer, fridge,...
Never said they were for equipment protection.

Follow the mfgs. instructions for appliances.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #11  
Old 11/9/09, 7:49 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI on 2 wire systems

I'm sorry, but it really bugs me when people state that GFCI will reduce the risk of (or worse yet - prevent) electrical shocks.

GFCI PROTECTION DOES NOT REDUCE THE RISK OF ELECTRICAL SHOCKS!!!!!

They reduce the risk of death by electrocution, but have absolutly no affect on electrical shocks in general. A 5ma shock is still VERY painful (from what I have read).
Reply With Quote
  #12  
Old 11/9/09, 7:52 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: GFCI on 2 wire systems

Not really

Now 220 kinda bothers you.
110 just tickles.
Reply With Quote
  #13  
Old 11/9/09, 7:56 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI on 2 wire systems

Quote:
Originally Posted by belliott View Post
Not really

Now 220 kinda bothers you.
110 just tickles.
Have you ever tripped a GFCI with your body (across two fingers doesn't count)? I don't recommend trying it, but would be interested in hearing if anyone has.

From what I have heard, at least 220 will knock you off, unlike 110 which just makes your muscles hold tighter.
Reply With Quote
Find an InterNACHI certified Tennessee Home Inspector (and anywhere else in North America)
  #14  
Old 11/9/09, 8:11 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: GFCI on 2 wire systems

I have been shocked many times ,so I do not count as I may have built an immunity.

In used to experiment from the time I was a kid.

None the less I would not depend on any devise to always do its job.(haven't we all inspected bad GFCI)?
Reply With Quote
  #15  
Old 11/9/09, 8:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GFCI on 2 wire systems

Resisting going there.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 10:06 AM