Anyone ever have a GFCI circuit register normal, then when tripped with a testing device, register reverse polarity?

I had it happen to me today. All of the GFCI's (exterior, garage, bathrooms) were tied to a single GFCI in the Hall Bath, which is normal. When I intentially tripped the exterior GFCI, it went directly to registering reversed.

All of the GFCI's on that circuit registered reversed (garage and master bath). When I get up to the Hall Bath, I reset the tripped GFCI, then test it again. It registered "all green." But, once I tripped it, it went back to reversed.

Never had a GFCI do that.

Kevin



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared Thermographer®, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com
Reply With Quote
  #2  
Old 8/11/08, 7:20 PM
Joshua L. Frederick Joshua L. Frederick is online now
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 766
Send a message via AIM to jfrederick
Default Re: Gfci

I'm not sure about the whole rev pol thing, but what I wonder about is having all those outlets tied together, seems a bit crowded to me (that's definitely not "normal" in my parts).

Hope all is well over your way.
Reply With Quote
  #3  
Old 8/11/08, 7:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,756
Default Re: Gfci

Defective GFCI receptacle.

Your three-light tester "reads" it as reverse polarity, but it's actually just a bad reset. In this condition, if you had plugged in a SureTest, or some other device that needs a bit more current, the circuit would have tripped again.

http://www.nachi.org/forum/f19/do-you-write-up-open-neutral-31340/



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 8/11/08, 8:17 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,334
Default Re: Gfci

Quote:
Originally Posted by jpope
Defective GFCI receptacle.

Your three-light tester "reads" it as reverse polarity, but it's actually just a bad reset. In this condition, if you had plugged in a SureTest, or some other device that needs a bit more current, the circuit would have tripped again.

http://www.nachi.org/forum/f19/do-you-write-up-open-neutral-31340/
Thanks, Jeff.

Definitely wrote it up as defective, but wanted to see if anyone else came across this scenario.

Thanks again for the info....your always here to help

Kevin



Kevin A. Richardson
Level III Infraspection Institute Certified Infrared Thermographer®, #7493
Infraspection Institute Thermography Instructor
BPI Certified Building Performance Analyst
RESNET Level II Home Energy Survey Professional
Maryland Licensed Home Inspector, #29727
InterNACHI Certified Professional Inspector, #04091175


301-942-4610
www.richnspect.com
www.infrared-diagnostics.com
www.thehomegreenteam.com
Reply With Quote
  #5  
Old 8/11/08, 8:26 PM
rshuey rshuey is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Mar 2007
Posts: 198
Please Note: rshuey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gfci

Quote:
Originally Posted by jfrederick
I'm not sure about the whole rev pol thing, but what I wonder about is having all those outlets tied together, seems a bit crowded to me (that's definitely not "normal" in my parts).

Hope all is well over your way.
Actually, some GFCI's are tested and rated to allow up to 12 outlets downstream from one GFCI. You would have to turn on all the bath lights, receptacles, plug in a heater in the garage and runn a swimming pool motor off the circuit before a problem existed. (i am making a point, not quite literal)
Reply With Quote
  #6  
Old 8/11/08, 9:10 PM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is online now
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: Gfci

yes, it is happened to me, then I reset it and try again and it usually is ok...




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 9:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 1:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 10:31 AM


All times are GMT -4. The time now is 3:47 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts