Tested a GFCI receptacle and the lights on my tester showed everything to be okay. Pushed the button on tester and the gfci did not trip and the tester lights changed to reverse polarity. Can anyone explain? Thanks.
Jason R.
Reply With Quote
Find an InterNACHI certified Montana Home Inspector (and anywhere else in North America)
  #2  
Old 10/16/09, 4:58 PM
ccurrins's Avatar
ccurrins ccurrins is offline
Active Poster
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,234
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI

You have a faulty GFCI.
Reply With Quote
  #3  
Old 10/16/09, 5:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: GFCI

Defective GFCI receptacle. . .

This is common for GFCI receptacles manufactured prior to the "lock-out" type that are manufactured currently. I'm guessing the receptacle was manufactured in the '80's to early '90's.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 10/16/09, 8:45 PM
Jae Williams's Avatar
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 3,859
Default Re: GFCI

Quote:
Originally Posted by jrider View Post
Tested a GFCI receptacle and the lights on my tester showed everything to be okay. Pushed the button on tester and the gfci did not trip and the tester lights changed to reverse polarity. Can anyone explain? Thanks.
Jason R.
I find that in about half of the pre-2000 homes I inspect. Jeffy's correct--GFCI don't work so good.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #5  
Old 10/17/09, 4:37 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: GFCI

always double check your "Tester" in a different plug to verify it is working and if it is then regardless of what it could be, it is clear the receptacle has some sort of problem be is defective or reverse polarity....either way note it as abnormal and defer to licensed electrical contractor.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
More GFCI info from U/L Greg Fretwell Electrical 9 12/4/07 9:33 PM
GFCI Safety Notice rcooke Electrical 1 10/30/07 1:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical 28 10/4/06 10:31 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 11:07 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts