Default Re: gfci

Quote:
Originally Posted by llosciale View Post
What I'm saying is that with "a D a m n Ground", if the down stream outlets don't trip the GFCI how do you KNOW they're protected.
If your 3-light tester indicated the non-gfci outlet is grounded, and you push the gfci test button on the 3-light but nothing trips it's not protected.

Quote:
Originally Posted by llosciale View Post
... when the GFCI trips there's no power but will a ground fault in those down stream outlets cause it to trip?
Yes ... a GFCI detects a difference between the hot and neutral wires. If there is fault and current starts flowing from the hot wire, it should detect the hot-neutral current difference and trip.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 8/4/11, 6:15 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: gfci

You know, when you do step# 1.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 8:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM
UL Information about Testing of GFCIs jtedesco1 Electrical Inspections 0 2/5/06 4:38 PM


All times are GMT -4. The time now is 9:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts