Default Re: Gfci in bedroom?

Quote:
Originally Posted by ccurrins View Post
I'd also question why it's only 15 amp serving a bedroom.
How much power do you think the normal bedroom requires? A couple of lamps, an alarm clock and a TV.
Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 10/14/10, 2:53 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Gfci in bedroom?

Quote:
Originally Posted by Jim Port View Post
How much power do you think the normal bedroom requires? A couple of lamps, an alarm clock and a TV.
Not sure about exact amperage, but including light (ceiling fan) and 4 -6 rec. in an average room I'm used to seeing 20 amp. Actually most all circuits for rec. are on 20 amp.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #18  
Old 10/14/10, 2:56 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Gfci in bedroom?

Quote:
Originally Posted by pnarron View Post
When I was testing outlets in 2 bedrooms I hit the button to trip the gfci and it cut the power to the outlets in each bedroom. The house was built in 2002 and I checked the panel and found the 2 breakers in the attached photo. Are these GFCI breakers? Why would they have GFCI breakers for a bedroom?
I love the Red Pipe Cleaner in the Picture, clever.
Reply With Quote
  #19  
Old 10/14/10, 11:14 PM
pnarron pnarron is offline
InterNACHI Member
 
Join Date: Jan 2010
Posts: 74
Default Re: Gfci in bedroom?

Thanks for all your help. I do test AFCI breakers at the panel. I trip them then go check the outlets and I have not had any trip with the GFCI tester before. As far as the 15 amp the house was built in 2002. I think I will invest in a plug in tester.
Reply With Quote
  #20  
Old 10/14/10, 11:24 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Gfci in bedroom?

I hate to spoil the party but I am not convinced that Jeff's image proves anything.
http://www.hardwareandtools.com/Squa...r-1311612.html
Reply With Quote
  #21  
Old 10/14/10, 11:34 PM
pnarron pnarron is offline
InterNACHI Member
 
Join Date: Jan 2010
Posts: 74
Default Re: Gfci in bedroom?

Thanks for all the help.
Reply With Quote
  #22  
Old 10/14/10, 11:45 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Gfci in bedroom?

Yours has a white button Bob.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #23  
Old 10/15/10, 12:16 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Gfci in bedroom?

Quote:
Originally Posted by jpope View Post
Yours has a white button Bob.
Hmmm true but we sure need more info.
Good thread as I never gave it a second thought before.
Seems they are always labeled.
Reply With Quote
  #24  
Old 10/15/10, 5:18 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gfci in bedroom?

Phil, RE: the plug-in tester. UL only recognizes the built-in test button as a valid test.
Reply With Quote
  #25  
Old 10/15/10, 11:38 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Gfci in bedroom?

Quote:
Originally Posted by belliott View Post
Hmmm true but we sure need more info.
I originally posted a response in this thread based on my personal experience as an inspector. I have run across this condition on numerous occasions where the installer mistakenly placed GFCI type breakers where AFCI type breakers are required.

I fact-checked my response by researching the specific breaker as pictured in the initial post.

Subsequently, I have no doubt that the breakers pictured in the original post are GFCI type, and not AFCI type breakers.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #26  
Old 10/15/10, 11:48 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Gfci in bedroom?

Quote:
Originally Posted by jpope View Post
I originally posted a response in this thread based on my personal experience as an inspector. I have run across this condition on numerous occasions where the installer mistakenly placed GFCI type breakers where AFCI type breakers are required.

I fact-checked my response by researching the specific breaker as pictured in the initial post.

Subsequently, I have no doubt that the breakers pictured in the original post are GFCI type, and not AFCI type breakers.
By need more info, I am referring to wishing to know what physical characteristic a GFCI vs AFCI might have on the casing.
Reply With Quote
  #27  
Old 10/15/10, 12:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Gfci in bedroom?

That would be too easy



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #28  
Old 10/15/10, 12:23 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Gfci in bedroom?

Quote:
Originally Posted by pnarron View Post
As far as the 15 amp the house was built in 2002.
What difference does that make?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #29  
Old 10/15/10, 2:56 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gfci in bedroom?

Quote:
Originally Posted by ccurrins View Post
Not sure about exact amperage, but including light (ceiling fan) and 4 -6 rec. in an average room I'm used to seeing 20 amp. Actually most all circuits for rec. are on 20 amp.
You could use a 15 amp or a 20 amp circuit. This is a design issue not a code issue. IMO for a bedroom, 20 amp is overkill.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 8:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM
UL Information about Testing of GFCIs jtedesco1 Electrical Inspections 0 2/5/06 4:38 PM


All times are GMT -4. The time now is 9:46 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts