Default GFCI below the main panel

Is the circuit dedicated for the GFCI below the main panel allowed to have other circuits added? The exterior and numerous basement receptacles were added to this circuit.

I would think the only problem would be tripping the GFCI under the panel if overloaded.
Attached Thumbnails
gfci-below-main-panel-105007-048-small-.jpg.jpg
Views:	188
Size:	36.6 KB
ID:	14467   gfci-below-main-panel-105007-025-small-.jpg.jpg
Views:	236
Size:	80.1 KB
ID:	14468  
Reply With Quote
  #2  
Old 9/13/07, 11:10 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GFCI below the main panel

Quote:
Originally Posted by dmacy
Is the circuit dedicated for the GFCI below the main panel allowed to have other circuits added? The exterior and numerous basement receptacles were added to this circuit.

I would think the only problem would be tripping the GFCI under the panel if overloaded.
Any oulets added downstream of the GFCI would also be protected so I don't see any problems with this.
Any overloads would trip the circuit breaker not the GFCI.
Of course any leakage current of devices plugged into this circuit would be additive and should trip the GFCI if the sum is above it's trip level(5 mA)

Is that a wire staple I see securing the doubled NM?

Looks like there may also be neutrals and grounds under the same screw on the bus.

Last edited by mlarson; 9/13/07 at 11:13 AM..
Reply With Quote
  #3  
Old 9/13/07, 11:14 AM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: GFCI below the main panel

Quote:
Originally Posted by mlarson

Is that a wire staple I see securing the doubled NM?
Yes it is. Is that a problem?
Reply With Quote
  #4  
Old 9/13/07, 11:17 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GFCI below the main panel

Quote:
Originally Posted by dmacy
Yes it is. Is that a problem?
I don't have my code book handy but I believe they need a saddle of some type not just a wire staple only.
Reply With Quote
  #5  
Old 9/13/07, 11:27 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: GFCI below the main panel

We don't have basements here, but our exterior receptacles are almost always tied into the garage GFCI. It is no issue.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #6  
Old 9/13/07, 11:36 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GFCI below the main panel

Quote:
Originally Posted by dmacy
Yes it is. Is that a problem?
A better answer is: depends.

Insulated vs.
Non-insulated Staples


Many local codes permit use of UL Listed non-insulated staples driven by staple guns as an alternative to hammer-in insulated staples, because of the gun’s controlled staple driving depth. NO DAMAGE TO THE WIRE!


I normally see them with a sadle or an insulator under the staple in my area. The uninsulated ones require special tools.


NEC 2005 code 334.30 that reads in part "nonmetallic-sheathed cable shall be secured by staples designed and installed so as not to damage the cable."


Acme Staples
Reply With Quote
  #7  
Old 9/13/07, 11:44 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI below the main panel

Methods of securing wiring methods are not really spelled out in the NEC. Without actually having the box the staple came in it is hard to say if it is listed for 1 or 2 cables. The same goes for the clamp in the box. Generally if it looks secure, it is. Mr Larson is right about not damaging the cable. A properly driven staple is not squeezing the wire, it is only holding it laterally.

Last edited by Greg Fretwell; 9/13/07 at 11:48 AM..
Reply With Quote
  #8  
Old 9/13/07, 12:00 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI below the main panel

Quote:
Originally Posted by mlarson
Any oulets added downstream of the GFCI would also be protected so I don't see any problems with this.
Quote:
Originally Posted by mlarson
Any overloads would trip the circuit breaker not the GFCI.
I agree

Quote:
Originally Posted by mlarson
Is that a wire staple I see securing the doubled NM?
Not a problem
Reply With Quote
  #9  
Old 9/13/07, 3:44 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI below the main panel

Most NM staples ARE approved for two cables. Some are actually approved for three cables.
Reply With Quote
  #10  
Old 9/13/07, 4:54 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: GFCI below the main panel

I guess for an existing home inspection, it really doesn't matter much unless you can clearly see that the staple is damaging the wire. After all, for every one you can see there are probably a hundred or more that you can't



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #11  
Old 9/13/07, 4:55 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: GFCI below the main panel

Quote:
Originally Posted by fnewman
I guess for an existing home inspection, it really doesn't matter much unless you can clearly see that the staple is damaging the wire. After all, for every one you can see there are probably a hundred or more that you can't
Good point Frank. I agree 100%
Reply With Quote
  #12  
Old 9/14/07, 9:04 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: GFCI below the main panel

What about use of Romex on the exterior of a wall?

A garage has a bunch of junk that will potentially damage unprotected nonmetallic wiring.

Protect from physical damage: NEC {336-6b}

Last edited by dandersen; 9/14/07 at 9:09 AM..
Reply With Quote
  #13  
Old 9/14/07, 9:10 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI below the main panel

The size of the box looks undersized for the number of conductors installed. Assuming 14 Ga. conductors this box would need to have at least 14 cu. in capacity. 2 cables x 2 +2 for device + 1 ground = 7, 7*2=14
Reply With Quote
  #14  
Old 9/14/07, 7:59 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI below the main panel

Physical damage is a local call. In Md it was vert common to see Romex on running blarrds exposed in garages and utility rooms. In Florida it all has to be in pipe if it is exposed up to 6'6 or to the ceiling. They used to require EMT behind sheetrock on 3/4" furred block walls too (in most places) but that went away. Now they let them use "stackers" to get the 1.25" laterally. I think it was a bad decision. I guy "probing" for a furring strip to hang a picture can still get that wire.
Reply With Quote
  #15  
Old 9/21/07, 6:14 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: GFCI below the main panel

Quote:
Originally Posted by dmacy
Is the circuit dedicated for the GFCI below the main panel allowed to have other circuits added?
Yes ... there are terminals/connectors on GFCI receptacles specifically for that purpose.

Quote:
Originally Posted by dmacy
The exterior and numerous basement receptacles were added to this circuit.
Thats okay as long as those downstream exterior/basement receptacles are wired correctly to the "load" terminals of the GFCI device, which will provide the required GFCI protection. If they are wired to the "line" terminals of the GFCI device, there would be no GFCI protection.

An easy way to check this is to press the "test" button on the GFCI device. If the exterior/basement receptacles then shut off they have GFCI protection.
Attached Thumbnails
gfci-below-main-panel-gfci-receptacle-terminals.jpg   gfci-below-main-panel-gfci-wiring-diagram.jpg  



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Safety Foundation International Links jtedesco1 Electrical Inspections 5 12/8/07 3:10 PM
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
GFCI electrical panel hmcbride Electrical Inspections 3 3/25/07 6:02 PM
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 6:24 PM