InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Electrical

Notices

Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera.

Reply
 
LinkBack Thread Tools
  #1  
Old 6/16/07, 1:48 AM
Al D. Bolt Al D. Bolt is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Twin Falls, ID
Posts: 87
Default GFCI breaker

Is this GFCI breaker wiring OK?
Attached Thumbnails
gfci-breaker-hpim0924-small-.jpg.JPG
Views:	156
Size:	74.5 KB
ID:	12377  
Reply With Quote
  #2  
Old 6/16/07, 9:01 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker

I have seen GFI breakers that have two tails. One for the line neutral connection to the bar, and another to splice to the load neutral.

Did you follow both wires? I don't see a screw for the load neutral.
Reply With Quote
  #3  
Old 6/16/07, 9:21 AM
Al D. Bolt Al D. Bolt is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Twin Falls, ID
Posts: 87
Default Re: GFCI breaker

My concern was the neutral and tail in the same slot on the breaker.
Reply With Quote
  #4  
Old 6/16/07, 10:20 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker

Quote:
Originally Posted by abolt
My concern was the neutral and tail in the same slot on the breaker.
It's manufactured that way. They are not under a screw.
They are both factory tails.
Reply With Quote
  #5  
Old 6/16/07, 10:41 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker

One of those tails is white (line) and one is white with a black stripe (load).

Looks like rust discoloration on the breaker. Water infiltration? Condensation? Damp ambient?
Reply With Quote
  #6  
Old 6/16/07, 1:47 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker

Quote:
Originally Posted by Marc D. Shunk
Looks like rust discoloration on the breaker. Water infiltration? Condensation? Damp ambient?
Marc, do you mean the brown spots? To me that looks like (factory) epoxy to seal the unused holes in the breaker.
Reply With Quote
  #7  
Old 6/16/07, 1:53 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker

Quote:
Originally Posted by Speedy Petey
Marc, do you mean the brown spots? To me that looks like (factory) epoxy to seal the unused holes in the breaker.
Yeah, that's what I was seeing. Looks like rust blobs to me. I've only seen maybe a half-dozen of this style GFCI ever, so epoxy didn't enter my mind. On second look, that's what it seems to be; epoxy.

Say, do you recognize the brand? I don't. Late 70's GE would be my guess.
Reply With Quote
  #8  
Old 6/16/07, 7:52 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker

ITE Gould. I'd say mid-late 80's.
Reply With Quote
  #9  
Old 6/17/07, 12:04 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: GFCI breaker

lol...the only problem I see is....
Attached Thumbnails
gfci-breaker-hpim0924-20-28small-29.jpg  



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 6/17/07, 7:25 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,027
Default Re: GFCI breaker

Quote:
Originally Posted by pabernathy
lol...the only problem I see is....
I call those out on 90% of the homes I inspect.

I'm getting tired of explaining why they neutrals need to be separated and why only one per screw.
Reply With Quote
  #11  
Old 6/17/07, 8:26 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,078
Default Re: GFCI breaker

Quote:
Originally Posted by dvalley
I call those out on 90% of the homes I inspect.

I'm getting tired of explaining why they neutrals need to be separated and why only one per screw.
You and me both, brutha'



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #12  
Old 6/18/07, 10:09 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: GFCI breaker

lol...thats why you set up a "PRE" done verbiage in your reports...one click...whamo....don't need to personally explain it again....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 6/18/07, 10:16 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: GFCI breaker

You know....Speedy made a good educational point here that I would LOVE Marc and Greg and Peter as well as others to chime in on for sake of...well.....because I am waiting to fly to florida and hell I like typing.

What if that GFCI pictured ( which does have the older style two legs for the grounded conductor ) did not have a pigtail on the grounded conductor coming back from the 120V branch...and both the white and the white with black stripe were placed onto the grounded buss bar.....

Do you think it would possible have an effect on the GFCI breaker or not....and if you do not think so....why is that now they all feed through the breaker first before going to the grounded bussbar.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 6/18/07, 10:47 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,027
Default Re: GFCI breaker

Quote:
Originally Posted by pabernathy
lol...thats why you set up a "PRE" done verbiage in your reports...one click...whamo....don't need to personally explain it again....
You can have all the boiler plate verbiage you want on your report, but you're still going to continuously get the majority of your clients asking "Why".

I don't know about the rest of you, but I have my client's walk right next to me and I talk them through the entire inspection on all of my inspections. They have lots of questions and I always supply them with the exact information they are seeking.

Answering my client's questions is my passion.
Reply With Quote
  #15  
Old 6/18/07, 10:55 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: GFCI breaker

Ahhh....good point...

I was kinda refering to the report only having to explain it but you are right...many times they are right up in your face wanting to know so yep it is good to know why it is a problem.

Hey I got an idea...do a pre-recorded message on a digital recorder and play it for them while you keep on inspecting..thehehehe...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI Safety Notice rcooke Electrical 1 10/30/07 1:29 PM
Double tapped GFCI breaker sspradling Electrical 6 12/9/06 11:51 AM
The question asked on the new HI Study test here? jtedesco1 Electrical 28 10/4/06 10:31 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM
GFCI breaker in service panel cobarr Electrical 11 4/17/06 10:59 PM


All times are GMT -4. The time now is 12:54 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts