Is this GFCI breaker wiring OK?
|
|
#2
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
I have seen GFI breakers that have two tails. One for the line neutral connection to the bar, and another to splice to the load neutral.
Did you follow both wires? I don't see a screw for the load neutral. |
|
#3
|
|||
|
|||
|
My concern was the neutral and tail in the same slot on the breaker.
|
|
#4
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
They are both factory tails. |
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
One of those tails is white (line) and one is white with a black stripe (load).
Looks like rust discoloration on the breaker. Water infiltration? Condensation? Damp ambient? |
|
#6
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Say, do you recognize the brand? I don't. Late 70's GE would be my guess. |
|
#8
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
ITE Gould. I'd say mid-late 80's.
|
|
#9
|
||||
|
||||
|
lol...the only problem I see is....
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#10
|
||||
|
||||
|
Quote:
I'm getting tired of explaining why they neutrals need to be separated and why only one per screw. |
|
#11
|
||||
|
||||
|
Quote:
- Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#12
|
||||
|
||||
|
lol...thats why you set up a "PRE" done verbiage in your reports...one click...whamo....don't need to personally explain it again....
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#13
|
||||
|
||||
|
You know....Speedy made a good educational point here that I would LOVE Marc and Greg and Peter as well as others to chime in on for sake of...well.....because I am waiting to fly to florida and hell I like typing.
What if that GFCI pictured ( which does have the older style two legs for the grounded conductor ) did not have a pigtail on the grounded conductor coming back from the 120V branch...and both the white and the white with black stripe were placed onto the grounded buss bar..... Do you think it would possible have an effect on the GFCI breaker or not....and if you do not think so....why is that now they all feed through the breaker first before going to the grounded bussbar..... Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#14
|
||||
|
||||
|
Quote:
I don't know about the rest of you, but I have my client's walk right next to me and I talk them through the entire inspection on all of my inspections. They have lots of questions and I always supply them with the exact information they are seeking. Answering my client's questions is my passion. |
|
#15
|
||||
|
||||
|
Ahhh....good point...
I was kinda refering to the report only having to explain it but you are right...many times they are right up in your face wanting to know so yep it is good to know why it is a problem. Hey I got an idea...do a pre-recorded message on a digital recorder and play it for them while you keep on inspecting..thehehehe... Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| GFCI Safety Notice | rcooke | Electrical | 1 | 10/30/07 1:29 PM |
| Double tapped GFCI breaker | sspradling | Electrical | 6 | 12/9/06 11:51 AM |
| The question asked on the new HI Study test here? | jtedesco1 | Electrical | 28 | 10/4/06 10:31 AM |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical | 0 | 7/7/06 1:24 PM |
| GFCI breaker in service panel | cobarr | Electrical | 11 | 4/17/06 10:59 PM |