#16
|
|||
|
|||
|
According to our electrician here in florida the white reset was typical to the pop-o-matic breakers used before GFCI came to pass. He says from the 60's and 70's.
By the 80's GFCI were improved and the button became red by standard. He also says that it appears the original expoy has deteriorated and is allowing moisture to rust the connection points. He says continual over heating causes this. |
|
#17
|
|||
|
|||
|
Quote:
On the overheating.....if no signs of moisture within the enclosure I would venture to not believe the statement of rust as it pertains to THIS picture in question...but in Florida depending on where you live it could be possibly a salt issue and corrosion....just not sure but I dont think it is the case in this image shown. The original posted is from Idaho I believe. Paul W. Abernathy |
|
#18
|
|||
|
|||
|
Please Note:
brepanshek is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#19
|
||||
|
||||
|
Quote:
Pleeeease don't get me started on the double lugged neutrals! - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#20
|
||||
|
||||
|
Quote:
It's very simple....408.21 specially states "each grounded conductor [neutral] shall terminate within the panelboard in an individual terminal that is not also used for another conductor". Double lugging neutrals is not be permitted, PERIOD. Last edited by dvalley; 6/20/07 at 6:55 AM.. |
|
#21
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Just bear in mind 408.21 is fairly new. It may not have been adopted when the house was built.
|
|
#22
|
||||
|
||||
|
Greg, while that is true, it's my understanding the compliance with UL67 for panel boards has always been that way.
|
|
#23
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Calling this as a 110.3 is not as common as one would expect and it is very likely that you would see double lugged neutrals before the 2002 code made it clear it was illegal. It was very common to see the ground and neutral for a particular circuit under one lug.
|
|
#24
|
||||
|
||||
|
Quote:
|
|
#25
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
That is the luxury of your job. You are just there to voice concerns, not to enforce code. A code inspector can't really complain about things like light switches behind doors and receptacles in inconvenient places as long as they meet code. You are there for the buyer.
Personally I don't see double lugged neutrals as a huge concern until harry homeowner starts poking around in the panel but it could be an indicator of unlicensed/unpermitted work in a newer home. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| GFCI Safety Notice | rcooke | Electrical Inspections | 1 | 10/30/07 12:29 PM |
| Double tapped GFCI breaker | sspradling | Electrical Inspections | 6 | 12/9/06 10:51 AM |
| The question asked on the new HI Study test here? | jtedesco1 | Electrical Inspections | 28 | 10/4/06 9:31 AM |
| GFCI breaker in service panel | cobarr | Electrical Inspections | 11 | 4/17/06 9:59 PM |