Will a GFIC breaker still function as a standard breaker that is as a circuit protector, if the common conductor (white) is not connected to the neutral bus bar?
Thank you |
| Need a home inspection in Nevada? Check out InterNACHI's listing of Nevada certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
I have a few of these and will try it out tomorrow on my shop panel.
edit: checked it out on the GE type GFCI breakers. Both white wires on the breaker must be connected to the neutral bus to get any current flow since the neutral current passes through the breaker. The GFCI feature will work/test ok with the branch neutral wire disconnected and the pigtail neutral connected but the load will not work. So the answer is "no" it won't function as a breaker but it has no need to since a load will not work anyway. B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 Last edited by bking; 8/31/10 at 2:58 PM.. Reason: more info |
|
#3
|
|||
|
|||
|
I had a GFCI today that tripped as soon as I plugged my tester in it today, same problem?
Randy McKay InterNACHI member CanNACHI - CMHI Infrared Certified IAC2 Certified Mr. Home Inspection Services Inc Calgary, Alberta www.MrHomeInspections.ca |
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Is the branch circuit neutral connected to the breaker?
|
|
#5
|
|||
|
|||
|
the branch circuit wasn't identified, I couldn't start to turn off breakers.
Randy McKay InterNACHI member CanNACHI - CMHI Infrared Certified IAC2 Certified Mr. Home Inspection Services Inc Calgary, Alberta www.MrHomeInspections.ca |
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Without the neutral pigtail on the CB connected the GFCI function should not work. It should still function as an overcurrent protection device. A 2 pole GFCI CB with no load neutral will still provide GFCI protection if the CB neutral pigtail is connected to the neutral bus.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| Outlets protected by GFCI circuit breaker? | Nathan W. Swilling | Electrical Inspections | 7 | 4/11/08 1:02 PM |
| More GFCI info from U/L | Greg Fretwell | Electrical Inspections | 9 | 12/4/07 8:33 PM |
| Double tapped GFCI breaker | sspradling | Electrical Inspections | 6 | 12/9/06 10:51 AM |