Default GFCI breaker in service panel

Would someone please give a short primer on GFCI breakers in the main service panel. Function, test, protection of labeled circuit in place of GFCI receptacles.
Thank you.
Reply With Quote
  #2  
Old 4/16/06, 9:48 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: GFCI breaker in service panel

Chris;

A GFCI circuit breaker will protect the entire branch circuit. It should have a dedicated neutral (follow manufacturer's instructions) and have a neutral pig tail to the neutral buss.

Test by pushing the button on the breaker.

Make sure to check all the things plugged into that circuit though. You might de-energize a clock radio or TV or something and have to re-set it.

Hope this helps.

Feel free to call or e-mail me if you have ant other questions



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #3  
Old 4/16/06, 9:55 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker in service panel

Quote:
Originally Posted by cobarr
Would someone please give a short primer on GFCI breakers in the main service panel. Function, test, protection of labeled circuit in place of GFCI receptacles.
Thank you.
Underwriter's Laboratories provide the following information

http://www.ul.com/consumers/groundfault.html
Reply With Quote
  #4  
Old 4/16/06, 10:05 PM
cobarr cobarr is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Port Charlotte, FL
Posts: 90
Default Re: GFCI breaker in service panel

Thanks Will,

In other words, one must go to the GFCI protected circuit(I.E. kitchen,etc.), and confirm power off to that circuit. Then return and reset the GFCI breaker. Is this correct?
Happy Easter, HE is risen.
Reply With Quote
  #5  
Old 4/16/06, 11:13 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker in service panel

also keep in mind that if you have a gfci breaker, you should NOT have any other gfci outlets on that cercuit. if you do, than it's in need of correction. i did an inspection once were the breaker was gfci, and then there was a gfci outlet in the kitchen counter. the sellers told me that the HI who inspected it when they bought it 3 years ago, told them that they needed it. one will cancell out the other, and be a neucance to reset both. especialy when resetting one sometimes trips the other.
Reply With Quote
  #6  
Old 4/17/06, 7:06 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: GFCI breaker in service panel

Quote:
Originally Posted by Jay Moge
also keep in mind that if you have a gfci breaker, you should NOT have any other gfci outlets on that cercuit. if you do, than it's in need of correction. i did an inspection once were the breaker was gfci, and then there was a gfci outlet in the kitchen counter. the sellers told me that the HI who inspected it when they bought it 3 years ago, told them that they needed it. one will cancell out the other, and be a neucance to reset both. especialy when resetting one sometimes trips the other.
I would disagree with that based simply on logic. I don't see how they could possibly cancel out each other. If a GFCI outlet is wired properly and working properly, and let's say that there are no downstream outlets, then it seems to me that a problem at that GFCI outlet would only trip that GFCI outlet and not the GFCI breaker in the electrical panel. To me it looks like two-layer protection, which might be overkill, but I don't see any harm with it.

I look forward to some electricians weighing in here. Paul? Joe?



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #7  
Old 4/17/06, 8:29 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,757
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker in service panel

I have seen it, and they still operate. Life safety is never a nuisance.
Reply With Quote
  #8  
Old 4/17/06, 10:28 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker in service panel

Members:

I too agree that there is no problem with the two devices that control the function of the GFCI receptacle and CB operation.

It is not a usual practice, and may be a nuisance to some once in a while when the device is called upon to do its job.

If you want to get an expert opinion about any Listed or Labeled product call UL at 1-800-595-9844

JT Member of Committee:

UL Standard for Safety for Ground-Fault Circuit-Interrupters, UL 943
Reply With Quote
  #9  
Old 4/17/06, 1:55 PM
rmoore's Avatar
rmoore rmoore is offline
Active Poster
 
Join Date: Feb 2004
Location: Seattle, WA
Posts: 113
Please Note: rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker in service panel

I've run into the situation a number of times...that is GFCIs being fed by other GFCIs. Ground fault protection itself is not an issue. In fact, you could look at it as "back-up" protection for that part of the circuit.

However, a ground fault (or a tester) on a downstream GFCI (or a receptacle further downstream) wlll sometimes trip the downstream GFCI, sometimes the upstream, and sometimes it will trip both. The test button will always trip that GFCI, but can also trip an upstream device. With modern "lock-out" GFCIs you have to reset them in the right order...upstream first. So...yes it's a slight nuisance and can be a little confusing for the homeowner. The only "safety" issue I see is that it may result in the homeowner being less likely to test the GFCIs on a regular basis (like any actually do that!).

The added "back-up" safety may outweigh the nuisance factor(?). Personally, I don't feel it's a "repair" situation and I've taken the approach of informing the client of what feeds what, what can happen, the locations that might need to be reset, and that they have the option of removing all but the upstream device...and leaving it at that.

Last edited by rmoore; 4/17/06 at 2:06 PM..
Reply With Quote
  #10  
Old 4/17/06, 10:48 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker in service panel

RR, Ben, Richard, and Joe T. thanx for the input and education, but my point was that the HI befor me told them that they had to put gfci outlets on the counter tops, but then he opened the panel and tested the breaker (it was good) and still told them they needed more. i was meerly saying that if the breaker is gfci protected, then you don't need more gfci downstream. Thanx.
Reply With Quote
  #11  
Old 4/17/06, 10:49 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 6,525
Default Re: GFCI breaker in service panel

Must be an ASHI guy.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #12  
Old 4/17/06, 10:59 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI breaker in service panel

Quote:
Originally Posted by wdecker
Must be an ASHI guy.
My thinking too.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Safety Foundation International Links jtedesco1 Electrical 5 12/8/07 4:10 PM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical 13 2/8/07 2:18 PM
Service wire size to breaker panel sfalvey Electrical 12 10/31/06 5:28 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 5:38 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts