Title says it all. What would cause this? Tested with a standard plug in style GFCI tester.
Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. |
| Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Sounds like the GFCI receptacle is ungrounded. Did you try testing with the TEST button?
|
|
#3
|
||||
|
||||
|
Line/Load reversed.
|
|
#4
|
||||
|
||||
|
Quote:
Quote:
Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. |
|
#5
|
||||
|
||||
|
A test light will not indicate a line/load reversed wiring.
|
|
#6
|
||||
|
||||
|
|
|
#7
|
||||
|
||||
|
Thanks for the input gentlemen.
Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. Last edited by dredding; 6/11/10 at 11:43 PM.. |
|
#8
|
||||
|
||||
|
Darin...don't want to just leave you hanging. Here's some more information and also know newer (>'06) GFCI's have built-in protection to detect & indicate when the Line/Load is reversed.
From www.ecmweb.com : Quote:
|
|
#9
|
||||
|
||||
|
YES! Thanks Michael. Exactly what I needed.
Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. |
|
#10
|
||||
|
||||
|
In addition to Michael's great info here is a link to a Power Point explaining GFCI function and installation.
Note this quote related to your discovery. If the branch circuit conductors from the panelboard are connected to the GFCI “load” side terminals and downstream receptacles are connected to the “line” terminals ... what happens?
When the test button is pushed ... it trips. •When a tester is plugged into the downstream receptacles after the trip… they are de-energized. •When a tester is plugged into the GFCI receptacle… it is NOT de-energized.. Even though the GFCI has tripped. Downstream receptacles are protected/GFCI receptacles are not protected This is why there is a label covering the load terminals. Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Last edited by ccurrins; 6/12/10 at 1:50 AM.. |
|
#11
|
|||
|
|||
|
Darin -
I think the important thing to remember and report is: The GFCI is not working properly, have a licensed and competent electrician service and repair this. |
|
#12
|
||||
|
||||
|
Thanks Chris for the Powerpoint.
That's what I will put in my report Dan. As we are generalists I don't want to put too much in the report and sound like an electrical expert. Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| GFCI won't trip by tester | rstufflebeem | Electrical Inspections | 22 | 3/22/08 8:10 PM |
| More GFCI info from U/L | Greg Fretwell | Electrical Inspections | 9 | 12/4/07 8:33 PM |
| Ungrounded downstream GFCI | scosta | Electrical Inspections | 17 | 3/9/07 8:00 AM |
| GFCI trip or not to trip | abishop | Electrical Inspections | 11 | 5/24/06 6:43 PM |