Alright, guys! At inspection yesterday and it is new construction. Testing the exterior outlets, no GFCI, testing the bathroom outlets, no GFCI, testing the kitchen outlets at the sink, no GFCI. Well the wonderful seller/builder who informs me is a contractor tells that the whole house is wired with ground fault protection. Not with GFCI breakers or outlets, the entire panel. Well obviously I am not educated b/c I didn't such a thing existed and told him in my six years inspected I had not seen such a thing. Playing dumb, what in the hell is he talking about? THANKS!
Reply With Quote
  #2  
Old 3/25/07, 5:40 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCI electrical panel

well all I can say is....you inspected the panel I am sure and did you see a panel full of GFCI breakers.......chances are NOT...lol....

For a dwelling......I would not get near the downstream SMOKE of what that contractor is smokin..

But hey..maybe it is just me who has never installed a whole house GFCI system...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #3  
Old 3/25/07, 5:43 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI electrical panel

In Great Britian, they do use GFCI mains, called "RCD's". I've never seen it in the US, and if it existed at a 5ma level as would be required here, it would nuisance trip with great regularity. I'm agreeing with Paul.... that builder's sorely misinformed.
Reply With Quote
  #4  
Old 3/25/07, 7:26 PM
Harry V. McBride, III's Avatar
Harry V. McBride, III Harry V. McBride, III is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Alachua, FL
Posts: 196
Default Re: GFCI electrical panel

Thanks, guys! I knew this guy was trying to cover his butt for not installing the GFCI's.
Reply With Quote
  #5  
Old 3/25/07, 7:33 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCI electrical panel

lol....tell the contractor to get his head out his......and buy some freakin $ 9.00 GFCI's and feel good at night about saving a few lives.

Is this your contractor?



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 3/25/07, 8:11 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI electrical panel

It is easy to call his bluff. Plug your tester into a grounded outlet and push the button. It should get real quiet in there. The proper response is "what's that noise?"
Reply With Quote
  #7  
Old 3/25/07, 9:26 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,713
Default Re: GFCI electrical panel

Quote:
Originally Posted by Greg Fretwell
It is easy to call his bluff. Plug your tester into a grounded outlet and push the button. It should get real quiet in there. The proper response is "what's that noise?"
I would go further.

Trip a receptacle (fi you can) and when the whole house goes dark, have him call his "electrician" and find out where the reset button is located.

That way, you educate (and humiliate) them both.

Let us know what happens. PLEASE!!!!



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #8  
Old 3/25/07, 10:53 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: GFCI electrical panel

Okay...

I'm playing devil's advocate here...

What about a split style panel, with a 2-pole GFCI sitting at the position that feeds the convenience circuits at the lower half of the panel?

Hokey, maybe. Stupid, maybe. But do-able?

Isn't this what is planned for AFCI protected convenience circuits in the ENTIRE dwelling? Isnt something like this being discussed for the 2008 NEC?

Of course, we're not speaking of what may or may not be installed in this particular dwelling; but the question goes to whether a house's circuits can ALL be GFCI protected, and how many GFCIs would, theoretically, be required.

Okay, sparkys... jump in anytime.
Reply With Quote
  #9  
Old 3/25/07, 11:20 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI electrical panel

Quote:
Originally Posted by jfarsetta
What about a split style panel, with a 2-pole GFCI sitting at the position that feeds the convenience circuits at the lower half of the panel?.
There are tiny leakages in most every electrical device. The more equipment on the same GFCI, the more tiny leakages that will add and quickly get to the 5ma trip threashold. Code wise, it would be compliant. Design wise, it would be a complete disaster, as the nuisance tripping would be unbearable.
Reply With Quote
  #10  
Old 3/26/07, 1:06 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI electrical panel

I don't think you can still get a split bus panel can you?
Reply With Quote
  #11  
Old 3/26/07, 1:29 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: GFCI electrical panel

Hey a regular breaker has ground fault protection. Maybe that's what he meant.

Reply With Quote
  #12  
Old 3/26/07, 2:44 AM
alarsen1's Avatar
alarsen1 alarsen1 is offline
Active Poster
 
Join Date: Aug 2006
Location: Abbotsford, BC
Posts: 233
Please Note: alarsen1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI electrical panel

Was the panel labeled like this?
gfci-electrical-panel-allan-089-small-.jpg.jpg
Views:	119
Size:	61.9 KB
ID:	10291
Sure beats those crappy nuisance paper legends that peel off all the time!
Reply With Quote
  #13  
Old 3/26/07, 10:10 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCI electrical panel

Joe,

Firstly I have to agree with Marc on this as it would be a disaster the way it is setup right now. Sure, you could have a entire panel on GFCI and be code complaint....take a pool panel that is fed from lets say a 60A s-pole breaker....entirely possible.

Not the case in THIS situation as this is why I said in the original post the OP would have inspected the panel FIRST to determine anything weird like this.

Second, It was a new construction and a someone stated a split buss setup is not going to happen...so it makes that question moot.

Third, The AFCI on all the circuits is still being ironed out as when I spoke with Eaton on this they said they are still doing testing in regards to the questions me and greg had on the heat issues....they admitted and I am sure the other manufacturers have as well that they are still testing this issue...the jury is still out on the 2008 ROC.......at the last minute it could be ratified....who knows really until the final draft is out....and I am not sure it is yet but I could be wrong.

But I guess the issue is in the OP's original question...no room to play the DEVIL in that one fella...lol......it is just a contractor filling his head with mumbo jumbo.....

HOWEVER.....since I told the OP that he would know by looking in the panel.......You can't have a GFCI setup unless you have a way to TEST the function and RESET the function so a simple look in the panel and in this case if you go by what the contractor stated ( giving him/her the benefit of the doubt here ) do you see those two items on the main breaker.....?



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #14  
Old 3/26/07, 12:17 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI electrical panel

Quote:
In Great Britian, they do use GFCI mains, called "RCD's". I've never seen it in the US, and if it existed at a 5ma level as would be required here, it would nuisance trip with great regularity. I'm agreeing with Paul.... that builder's sorely misinformed.
These are great but you need very good wiring. A scratch in the insulation has been known to trip these because of the tiny level of leakage. Our wiring puts US wiring to shame.

Not to mention the benefits of 240V. Gas dryers? Why?
Reply With Quote
  #15  
Old 3/26/07, 12:39 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI electrical panel

Ian, we have plenty of 240v equipment, basically anything more than about 1500w. We don't have those 240v tea kettles but a household water heater will be 240, as will most fixed electric heat and A/C units, except the small window shakers.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 72 3/12/08 12:19 AM
GFCI electrical panel hmcbride Electrical Inspections 3 3/25/07 7:02 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 2:48 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 11:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts