Default GFCI for Hot Tub

I know a hot tub nees to be protected by a GFCI. But I also thought it needed to be within reach/sight of the tub. I can't find that requirement anywhere. Am I wrong?



Greg Keene
Clear Choice Home Inspections
Evergreen, CO
303-674-3234
greg@clearchoice-hi.com
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/16/10, 5:54 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: GFCI for Hot Tub

See no reason it would be required.
Cut off switches for workers is what you may be mixing it up with.
Reply With Quote
  #3  
Old 12/16/10, 5:55 PM
Greg Keene, CPI's Avatar
Greg Keene, CPI Greg Keene, CPI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Evergreen, CO
Posts: 628
Default Re: GFCI for Hot Tub

Thanks Bob - maybe I confused it with an A/C or furnace service switch.



Greg Keene
Clear Choice Home Inspections
Evergreen, CO
303-674-3234
greg@clearchoice-hi.com
Reply With Quote
  #4  
Old 12/16/10, 5:58 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: GFCI for Hot Tub

Beginning with the 2008 NEC (2009 IRC), the GFCI for a hydromassage bathtub has to be "readily accessible". That means that you can get to it without having to remove a panel (such as the access panel provided for the motor). You'll often see the GFCI in an adjacent closet or water closet to meet this requirement.

(It does not have to be within sight.)



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com



Last edited by jfunderburk; 12/16/10 at 6:29 PM..
Reply With Quote
  #5  
Old 12/16/10, 6:06 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI for Hot Tub

Do you mean a hot tub or a hydromassage tub? There seems to be some confusion in this thread and the answer may be different depending on which one you're referring to.
Reply With Quote
  #6  
Old 12/16/10, 6:08 PM
David Hays David Hays is online now
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: GFCI for Hot Tub

680.41 A clearly labeled emergency shutoff or control switch for the purpose of stopping the motor(s) that provide power to the recirculation system and jet system shall be installed at a point readily accessible to the users and not less than 1.5 m (5ft) away, adjacent to, and within sight of the spa or hot tub. This requirement shall not apply to single-family dwellings.



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
  #7  
Old 12/16/10, 6:10 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: GFCI for Hot Tub

Related Info:

DWELLING UNIT
120 volt GFCI Protected Outlets - REQUIRED LOCATIONS

5c. Indoor spa or hot tub, receptacles within 10 feet for pump motor.

Attached Files
File Type: pdf GFCI_requirement_page2.pdf (10.5 KB, 92 views)



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 12/16/10, 6:24 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: GFCI for Hot Tub

Quote:
Originally Posted by ccurrins View Post
Related Info:

DWELLING UNIT
120 volt GFCI Protected Outlets - REQUIRED LOCATIONS

5c. Indoor spa or hot tub, receptacles within 10 feet for pump motor.

That is just saying that any outlet within 10' of an indoor spa or hot tub has to be protected. (Like any outlet within 6' of a laundry tub has to be protected.)

Note that in the code, a spa or hot tub is different from a hydromassage bathtub. An indoor spa/hot tub is little or no different from an outdoor spa/hot tub (the water is not usually drained after each use). Whereas a hydromassage bathtub is permanently fixed, usually drained after each use, and is what we normally encounter in the master bathroom. We should be as professional as possible and use the correct terms in our reports.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 12/16/10, 6:27 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: GFCI for Hot Tub

Quote:
Originally Posted by dhays View Post
680.41 A clearly labeled emergency shutoff or control switch for the purpose of stopping the motor(s) that provide power to the recirculation system and jet system shall be installed at a point readily accessible to the users and not less than 1.5 m (5ft) away, adjacent to, and within sight of the spa or hot tub. This requirement shall not apply to single-family dwellings.
Does not apply to hydromassage bathtubs (what we find in bathrooms).



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #10  
Old 12/16/10, 6:29 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: GFCI for Hot Tub

Quote:
Originally Posted by gkeene View Post
I know a hot tub nees to be protected by a GFCI. But I also thought it needed to be within reach/sight of the tub. I can't find that requirement anywhere. Am I wrong?
Greg, are you talking about a spa/hot tub or a hydromassage bathtub?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 12/16/10, 6:38 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: GFCI for Hot Tub

Quote:
Originally Posted by jfunderburk View Post
That is just saying that any outlet within 10' of an indoor spa or hot tub has to be protected. (Like any outlet within 6' of a laundry tub has to be protected.)

Note that in the code, a spa or hot tub is different from a hydromassage bathtub. An indoor spa/hot tub is little or no different from an outdoor spa/hot tub (the water is not usually drained after each use). Whereas a hydromassage bathtub is permanently fixed, usually drained after each use, and is what we normally encounter in the master bathroom. We should be as professional as possible and use the correct terms in our reports.
I understand, why included:
Quote:
Related Info:



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 12/16/10, 8:11 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI for Hot Tub

Both hot tubs and hydromassage tubs require a disconnecting means. The emergency shutoff for hot tubs is a separate requirement.
Reply With Quote
  #13  
Old 12/16/10, 8:22 PM
Greg Keene, CPI's Avatar
Greg Keene, CPI Greg Keene, CPI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Evergreen, CO
Posts: 628
Default Re: GFCI for Hot Tub

This is an outdoor hot tub. It is at the back of the hosue and the GFCI 50amp breaker is in the main panel,. in the garage , at the front of the house. The hot tub is properly protected, but I had thought (and installed for my own hot tub) a shut off within sight of the hot tub. Taht was the question, within sight?



Greg Keene
Clear Choice Home Inspections
Evergreen, CO
303-674-3234
greg@clearchoice-hi.com
Reply With Quote
Need a home inspection in West Virginia? Check out InterNACHI's listing of West Virginia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/16/10, 9:08 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI for Hot Tub

A hot tub falls under the same rules as a permanently installed pool which requires this:

Quote:
680.12 Maintenance Disconnecting Means.
One or more means to simultaneously disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting. Each means shall be readily accessible and within sight from its equipment and shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool, spa, or hot tub unless separated from the open water by a permanently installed barrier that provides a 1.5 m (5 ft) reach path or greater. This horizontal distance is to be measured from the water's edge along the shortest path required to reach the disconnect.
Reply With Quote
  #15  
Old 12/16/10, 11:32 PM
Greg Keene, CPI's Avatar
Greg Keene, CPI Greg Keene, CPI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Evergreen, CO
Posts: 628
Default Re: GFCI for Hot Tub

House built in 96 = not sure when the hot tub was installed - When was the above put into the NEC?



Greg Keene
Clear Choice Home Inspections
Evergreen, CO
303-674-3234
greg@clearchoice-hi.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 8:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM


All times are GMT -4. The time now is 9:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts