  #1  
Old 10/21/10, 3:43 PM
lhood lhood is offline
InterNACHI Member
 
Join Date: Jul 2010
Posts: 10
Default GFCI Installation

I recently inspected an older home with a 2 wire system.In lieu of providing a new 3 wire system the contractor installed GFCI outlets through out the house. The bathroom and kitchen both have reset buttons,but would not trip at the outlet or at the panel breaker.I used a 3 prong tester without any success.How to I confirm that the system is working correctly,and can AFCI be provided on the same system in the bedrooms.Any advice would be appreciated.
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/21/10, 4:20 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Installation

The 3 light tester will not trip a GFI installed on a two wire setup. The correct way to test is the TEST button on the device. If the power goes off it is working. The 3 light works by sending some current to the ground pin. Since the ground pin is floating it will not complete the circuit to trip the device.

The fix provided by installing the GFI receptacle or breaker is a code compliant method. The "No Equipment Ground" sticker should have been applied to the coverplates.

AFAIK the AFCI breaker can be installed without problems if the panel will accept the breaker.
Reply With Quote
  #3  
Old 10/22/10, 9:02 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: GFCI Installation

You can also test this gfci with a voltage tester. Just put 1 lead in the jot side and the other in the ground, the gfci should trip is the plug is properly wired and grounded.
Reply With Quote
  #4  
Old 10/22/10, 9:38 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Installation

Quote:
Originally Posted by jkeilson View Post
You can also test this gfci with a voltage tester. Just put 1 lead in the jot side and the other in the ground, the gfci should trip is the plug is properly wired and grounded.
I'm not sure how that would works since this receptacle is ungrounded. However as James pointed out you can use a voltage tester and go from the receptacle hot to a known grounded source like a water pipe and depending on the type of tester it will trip the GFCI.
Reply With Quote
  #5  
Old 10/24/10, 10:53 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: GFCI Installation

I've tested this same setup with a *Wiggy* solenoid type tester, for the down stream outlets.

This is likely what you're talking about, just to clarify.

I generally don't see the required *GFCI Protected* AND *NO Equipement Ground* stickers provided on the outlets to let me know what I'm looking at.... I end up stumbling across a GFCI in a sleeping or living area and go from there.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #6  
Old 10/24/10, 12:28 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Installation

Quote:
Originally Posted by tspargo View Post
I've tested this same setup with a *Wiggy* solenoid type tester, for the down stream outlets.

This is likely what you're talking about, just to clarify.

I generally don't see the required *GFCI Protected* AND *NO Equipement Ground* stickers provided on the outlets to let me know what I'm looking at.... I end up stumbling across a GFCI in a sleeping or living area and go from there.
According to the NEC, GFCI protected stickers are not required, but the no equipment ground are.

You're correct about the Wiggy solenoid style tester. They will generate enough of an imbalance to trip the GFCI protection provided you're testing to a solidly grounded object.. Many electronic testers or DMM's will not.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Shooting to begin on comprehensive new roofing courses kshepard Inspection Education & Training 4 11/7/09 2:59 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 8:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM