Default GFCI in Manufactured Homes

Are the GFCI requirements the same for a Manufactured home as a regular home? We inspected a 2000 home that had GFCI's on some kitchen outlets but not on the ones over 6 feet from the sink. This would be required on a regular home but we were wondering if there are different rules for manufactured homes.

Thanks in advance for your help,
Jessica Glickman
Reply With Quote
  #2  
Old 5/31/07, 9:24 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCI in Manufactured Homes

Barry,

Should not be different basically.....are you sure the ones that were within 6' were not controlled from the other GFCI within the kitchen?

Anyway.....GFCI's really don't effect the 6' of the kitchen sink thing.....GFCI's should protect all counter top receptacles so if you know that the ones near the sink are not on the other GFCI in the kitchen, call it out as a Safety Enhancement and report it as such.


550.13(B) Ground-Fault Circuit Interrupters (GFCI).
All 125-
volt, single-phase, 15- and 20-ampere receptacle outlets installed
outdoors, in compartments accessible from outside
the unit, or in bathrooms, including receptacles in luminaires
(light
fixtures), shall have GFCI protection for personnel.
GFCI protection for personnel shall be provided for
receptacle outlets serving countertops in kitchens, and receptacle
outlets located within 1.8 m (6 ft) of a wet bar
sink.



Exception: Receptacles installed for appliances in dedicated

spaces, such as for dishwashers, disposals, refrigerators,
freezers, and laundry equipment.




Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 5/31/07 at 11:29 PM..
Reply With Quote
  #3  
Old 5/31/07, 10:03 PM
bglickman bglickman is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Bend, OR
Posts: 9
Default Re: GFCI in Manufactured Homes

Thanks Paul for the quick reply,

There were two receptacles near the sink that were GFCI and one on the island. There were two that were further away from the sink and these would not trip with the SureTest. If there is no difference for a manufactured home, then yes we will definitely write this up.
Thanks again,
Jessica Glickman
Reply With Quote
  #4  
Old 5/31/07, 10:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCI in Manufactured Homes

Remember Barry.....just because the Suretest does not trip them does not mean they are not GFCI protected.

The best way to check this is TRIP them with the GFCI test button on the GFCI receptacle and then go to those receptacles and plug in your SureTest or any 3 light tester for that matter......

Suretest and other testers ( as discussed here before ) could be misleading sometimes if lets say the GROUND to that receptacle has gone SOUTH....probably not the case here in a 2000 home but wanted to just give you that general reminder....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #5  
Old 5/31/07, 10:56 PM
bglickman bglickman is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Bend, OR
Posts: 9
Default Re: GFCI in Manufactured Homes

Thanks! Good reminders that there is still so much to learn in this profession.

Barry
Reply With Quote
  #6  
Old 5/31/07, 11:02 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCI in Manufactured Homes

Thats what we are all here for my brother......Livin and Learnin...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Learn the Differences: Site-Built, Modular, Manufactured/Mobile Homes jsieg General Inspection Discussion 10 12/23/07 12:20 AM
Toxic Gas in Mobile Homes jbushart Miscellaneous Discussion for Inspectors 0 11/12/07 9:31 PM
Grab Your Checkbooks - For sale: 2 million empty homes jburkeson1 Miscellaneous Discussion for Inspectors 2 10/26/07 8:22 PM
Water heater strapping in manufactured homes ilpowell Plumbing Inspections 10 2/24/06 6:20 PM


All times are GMT -4. The time now is 12:17 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts