Default GFCI near whirlpool

Gonna make someone's hair curly. House built 1989 so does fall under the 1996 NEC change which prohibits outlets within the space of showers or tubs.

What do you guys think?

I think I will write it up as a safety issue but not a requirement based on the age of the home.
Attached Thumbnails
gfci-near-whirlpool-dscn2762.jpg  



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.

Last edited by dredding; 2/5/12 at 9:17 PM..
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/5/12, 9:28 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,109
Default Re: GFCI near whirlpool

This will help.
Attached Files
File Type: pdf _GFCI_requirement_page-2008[1].pdf (14.1 KB, 64 views)



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #3  
Old 2/5/12, 9:30 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: GFCI near whirlpool

I would agree with that. They will probably remove the plug and change it to a light with a pull chain.



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #4  
Old 2/5/12, 9:33 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: GFCI near whirlpool

Quote:
Originally Posted by rernst1 View Post
I would agree with that. They will probably remove the plug and change it to a light with a pull chain.
And that would be safer?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #5  
Old 2/5/12, 11:11 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: GFCI near whirlpool

Quote:
Originally Posted by rernst1 View Post
I would agree with that. They will probably remove the plug and change it to a light with a pull chain.
Or replace it with a switch for the lighting fixture above...



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #6  
Old 2/5/12, 11:12 PM
Darin Redding's Avatar
Darin Redding Darin Redding is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: GFCI near whirlpool

Thanks all for your comments. There is no overhead light fixture served by this outlet. Instead, this GFCI feeds an outlet located inside the tub enclosure that provides power to the pump (which is not bonded, incidentally).



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #7  
Old 2/5/12, 11:34 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: GFCI near whirlpool

Quote:
Originally Posted by mgratton View Post
Or replace it with a switch for the lighting fixture above...
That's not allowed either, at least in the U.S.A.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 2/6/12, 12:03 AM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: GFCI near whirlpool

Christopher it's sarcasm.



Nevada Inspector of Structures #1730
Nevada Energy Auditor #30
www.homecsi.com
Reply With Quote
  #9  
Old 2/6/12, 12:11 AM
Cameron C. Anderson Cameron C. Anderson is online now
InterNACHI Member
 
Join Date: Nov 2011
Location: Peoria, IL
Posts: 881
Default Re: GFCI near whirlpool

For the most part, when it comes to electrical I don't consider what year the house was built as compared to the NEC changes. It's my butt on the line if something electrical kills someone. I know contractors sometimes argue against my reports by bringing that up and they throw around the "grandfathering" term. When that happens I encourage my clients to request a letter from the contractor stating "This issue is not a safety hazard." As expected, they go ahead and fix it after that.



Cameron Anderson
Bachelor of Architecture, U of I, Urbana IL
Illinois Licensed Inspector
www.aaintegrityhomeinspection.com
Reply With Quote
  #10  
Old 2/6/12, 12:29 AM
Darin Redding's Avatar
Darin Redding Darin Redding is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: GFCI near whirlpool

Quote:
As expected, they go ahead and fix it after that.
Yes I suppose they would

I agree - I usually make a strong recommendation for safety when it comes to electrical issues. I might says things such as "while the home MIGHT not have required X when it was built, for the safety of the building occupants it is strongly recommended that you modify/install/upgrade blah blah".



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #11  
Old 2/6/12, 8:06 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI near whirlpool

Quote:
Originally Posted by dredding View Post
Thanks all for your comments. There is no overhead light fixture served by this outlet. Instead, this GFCI feeds an outlet located inside the tub enclosure that provides power to the pump (which is not bonded, incidentally).

Just curious about the pump not being bonded, what do you mean?
Reply With Quote
  #12  
Old 2/6/12, 8:08 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: GFCI near whirlpool

Quote:
Originally Posted by ccurrins View Post
That's not allowed either, at least in the U.S.A.
Not allowed in Canada either; it must be a minimum of 3 feet from the tub.



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #13  
Old 2/6/12, 8:31 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI near whirlpool

Since it was said this GFI protects the tub, this should be changed to a dead-front GFI. Problem solved.

Marcel, in the NEC as long as the switch is outside the footprint of the tub or shower it would meet the code.

The bonding may not be an issue. Most tubs have non-metallic piping that does not require bonding.
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 2/6/12, 8:21 PM
Darin Redding's Avatar
Darin Redding Darin Redding is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: GFCI near whirlpool

Quote:
The bonding may not be an issue. Most tubs have non-metallic piping that does not require bonding.
Thanks for that.



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
  #15  
Old 2/6/12, 8:32 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI near whirlpool

Quote:
Originally Posted by Jim Port View Post

The bonding may not be an issue. Most tubs have non-metallic piping that does not require bonding.

Quote:
Originally Posted by dredding View Post
Thanks for that.
Jim brings up a good point about the bonding. There's quite a bit of confusion as to what is required to be bonded on a hydromassage tub. Often I see bonding jumpers from the pump to the metallic hot/cold water pipes supplying the tub. The NEC does not require this although the wording in 680.74 is a little confusing. It looks like the NEC CMP has tentatively accepted a proposal for the 2014 NEC to change the wording of this section to make it clear that only the metallic piping in contact with the circulating water is required to be bonded to the pump enclosure.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Outlet tester jshishilla Electrical Inspections 17 11/9/11 2:13 PM
GFCI and whirlpool tub thowell Electrical Inspections 4 8/25/09 8:16 AM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 8:33 PM