Default GFCI with no ground

Yesterdays inspection was on a 200+ year old home. House has combo of both 2 and 3 wire electric. I found 2 outlets that were GFCI, both did not have grounds (upgrades from 2-prong which by "code" is acceptable from my understanding).

They tested properly per the test and reset buttons which would indicate they are acceptable per the manufacturer, but when using my tester, they would not trip.

Is it acceptable if it tests properly using the device test buttons? and if so, how can it be acceptable if it will not trip with an outside source?

Thanks,



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 8/5/08, 8:04 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: GFCI with no ground

Quote:
Originally Posted by sfalvey
Yesterdays inspection was on a 200+ year old home. House has combo of both 2 and 3 wire electric. I found 2 outlets that were GFCI, both did not have grounds (upgrades from 2-prong which by "code" is acceptable from my understanding).

They tested properly per the test and reset buttons which would indicate they are acceptable per the manufacturer, but when using my tester, they would not trip.

Is it acceptable if it tests properly using the device test buttons? and if so, how can it be acceptable if it will not trip with an outside source?

Thanks,
Scott,

An ungrounded GFCI "Is Acceptable". A GFCI does not need a ground wire in order to trip properly. A GFCI simply trips when a fault is detected on the neutral wire. An ungrounded outlet will not trip using your tester. In this situation, I simply apply pressure to the GFCI test button in order to check its operation. And this outlet should be labled "GFCI protected / NO Equipment ground".

Last edited by dvalley; 8/5/08 at 8:07 AM..
Reply With Quote
  #3  
Old 8/5/08, 8:09 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: GFCI with no ground

Your tester uses the grounding conductor to test and since there is no grounding conductor your 3 light tester does not work. But, like David says, the integrated test button will test its functionality.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 8/5/08, 7:29 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI with no ground

Seems like I recall some home inspectors making a "special tester" for this purpose, with the third prong on their GFCI tester going to a long wire with an alligator clip they clip on the nearest radiator or water spiggot. That rig probably is helpful for testing the ungrounded load side receptacles. I'm not that clear, myself, on how safe it might or might not be. Obviously, the UL hasn't given their blessing to such a home brew gizmo.
Reply With Quote
  #5  
Old 8/5/08, 7:41 PM
Robert J. Wind Robert J. Wind is offline
InterNACHI Member
 
Join Date: May 2007
Location: Lacey, WA
Posts: 115
Default Re: GFCI with no ground

If no ground; then the outlet must be labled saying that the GFCI is not grounded. They sell the stickers at any of the home improvement stores.
Reply With Quote
  #6  
Old 8/6/08, 10:07 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI with no ground

I think the stickers are a joke. When my wife was building houses they had to go around putting "GFCI protected" stickers on to get the 305 and the first thing the owner did when they moved in was peel the stickers off.
The only one I have that actually survived was behind the door in the bathroom. All the ones in the kitchen came off within a month of normal cleaning.
Reply With Quote
  #7  
Old 8/6/08, 11:46 AM
Robert J. Wind Robert J. Wind is offline
InterNACHI Member
 
Join Date: May 2007
Location: Lacey, WA
Posts: 115
Default Re: GFCI with no ground

If you are inspecting a older home before GFCI and a GFCI outlet was installed then it should have the sticker. If the sticker is on the outlet then no issue. If you were conducting a code inspection (and i know that HI's do not do this) then it is requiered to have the sticker
Reply With Quote
  #8  
Old 8/6/08, 12:42 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 613
Default Re: GFCI with no ground

I have a comment that states something to the effect of:
"The receptacle is not grounded and it has GFCI protection. Ungrounded GFCI receptacles should be labeled indicating lack of grounding."

On all open ground 3-prong and 2-prong receptacles, make sure you test for reverse polarity with an indicator probe.

gfci-no-ground-p8060010.jpg



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #9  
Old 8/7/08, 5:43 PM
Eric Hyde Eric Hyde is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Broken Arrow, OK
Posts: 32
Please Note: ehyde is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI with no ground

I'm still confused on this issue as well. I read a post in this forum from 2006 that said that an NFPA official claimed that in Oct of that year the new GFCI's would not work without a grounding conductor.

I don't have access to the NEC or the NFPA codes, can anyone affirm or deny this claim?
Reply With Quote
  #10  
Old 8/7/08, 7:24 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: GFCI with no ground

Quote:
Originally Posted by ehyde
I'm still confused on this issue as well. I read a post in this forum from 2006 that said that an NFPA official claimed that in Oct of that year the new GFCI's would not work without a grounding conductor.

I don't have access to the NEC or the NFPA codes, can anyone affirm or deny this claim?
http://www.mikeholt.com/mojonewsarch...1~20020102.htm



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #11  
Old 8/7/08, 10:02 PM
Eric Hyde Eric Hyde is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Broken Arrow, OK
Posts: 32
Please Note: ehyde is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI with no ground

Thanks Larry,

I appreciate the reply, but the link you provided didn't answer the question. Do you have one that does?
Reply With Quote
  #12  
Old 8/7/08, 10:49 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI with no ground

Quote:
Originally Posted by ehyde
I'm still confused on this issue as well. I read a post in this forum from 2006 that said that an NFPA official claimed that in Oct of that year the new GFCI's would not work without a grounding conductor.

I don't have access to the NEC or the NFPA codes, can anyone affirm or deny this claim?
The NEC nor the NFPA would publish any thing like this it would be a NRTL such as UL.

The statement that a GFCI will not work without an equipment grounding conductor is just not true.
The EGC plays no role in how a GFCI works.
Reply With Quote
  #13  
Old 8/7/08, 11:20 PM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI with no ground

Quote:
Originally Posted by dvalley
Scott,

An ungrounded GFCI "Is Acceptable". A GFCI does not need a ground wire in order to trip properly. A GFCI simply trips when a fault is detected on the neutral wire. An ungrounded outlet will not trip using your tester. In this situation, I simply apply pressure to the GFCI test button in order to check its operation. And this outlet should be labled "GFCI protected / NO Equipment ground".
From "How Stuff Works":

A GFCI monitors the amount of current flowing from hot to neutral. If there is any imbalance, it trips the circuit. It is able to sense a mismatch as small as 4 or 5 milliamps, and it can react as quickly as one-thirtieth of a second.

http://ecmweb.com/mag/electric_gfcis_work/
Reply With Quote
  #14  
Old 8/8/08, 9:11 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: GFCI with no ground

Quote:
Originally Posted by ehyde
Thanks Larry,

I appreciate the reply, but the link you provided didn't answer the question. Do you have one that does?
I was thinking it would be helpful regarding how gfci's do work.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM
More GFCI info from U/L Greg Fretwell Electrical 9 12/4/07 9:33 PM
Installing GFCI in garage with no ground cyezza Electrical 53 11/30/07 6:05 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM


All times are GMT -4. The time now is 1:06 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts