Default GFCI protection

I inspected a house yesterday that had the washer dryer stack adjacent to the lav sink. The receptacle at the sink was protected but the receptacles front the washer and dryer (240) , were about 2 ft away from the lav. Should these outlets have protection as well? Opinions requested.
Thanks in advance.
Tony C
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/12/13, 9:57 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,118
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI protection

It's not required for the electric dryer since the receptacle is 240 volts.
Reply With Quote
  #3  
Old 1/12/13, 10:06 AM
Anthony Cavaliero Anthony Cavaliero is offline
InterNACHI Member
 
Join Date: Sep 2012
Posts: 11
Default Re: GFCI protection

Why does the fact that its 240 volt disqualify it for GFCI protection when it's accessible from the sink.
Reply With Quote
  #4  
Old 1/12/13, 11:04 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,818
Default Re: GFCI protection

There's just no "requirement" for it. The requirement only extends to the 120V circuits. Additionally, the requirement only extends to 15 and 20 amp circuits.

Adding GFCI protection to a 240V circuit is not prohibited, it's just not required.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 1/12/13, 11:04 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,118
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI protection

The required GFCI protection for 15 and 20 amp, 120 volt receptacles is not to protect the appliance it there to protect the user, someone who may plug a portable tool into the 120 volt receptacle. The title of the GFCI protection section {210.8} in the NEC is:

Quote:
210.8 Ground-Fault Circuit-Interrupter
Protection for Personnel
Reply With Quote
  #6  
Old 1/12/13, 11:17 AM
Anthony Cavaliero Anthony Cavaliero is offline
InterNACHI Member
 
Join Date: Sep 2012
Posts: 11
Default Re: GFCI protection

Ok, I understand about the dryer receptacle . But the washer receptacle (120)is as close or closer to the lav than the required gfci receptacle .

This is not an issue?
Reply With Quote
  #7  
Old 1/12/13, 11:34 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 2,118
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI protection

If the 120 volt, 15 or 20 amp receptacle is within 6' of the laundry sink it requires GFCI protection.

Quote:
210.8(A)(7) Sinks — located in areas other than kitchens where receptacles are installed within 1.8 m (6 ft) of the outside
edge of the sink
Reply With Quote
  #8  
Old 1/12/13, 10:47 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,505
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI protection

Quote:
Originally Posted by Robert Meier View Post
If the 120 volt, 15 or 20 amp receptacle is within 6' of the laundry sink it requires GFCI protection.
This is a relatively new code change and that house may pre-date that requirement.
Reply With Quote
  #9  
Old 1/12/13, 11:17 PM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,816
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI protection

Still does not matter as we report them anyways as a Electrical safety issue.
We don't report 240 as this is never used but 120 V can be used as Robert pointed out.
Reply With Quote
  #10  
Old 1/19/13, 8:45 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 729
Default Re: GFCI protection

I don't know where the OP is located, but in Ontario if the outlet is behind the washing machine it does not need to be a GFCI since it's not considered available for use by any other appliance.
Reply With Quote
  #11  
Old 1/19/13, 9:20 PM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,816
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI protection

You are correct John! Because of the advent of stackable wash machine and dryers it is next to impossible to plug into some but I still mention they should have GFCI protection within 6 feet of a sink.
Guess why?
Reply With Quote
  #12  
Old 1/19/13, 10:20 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 729
Default Re: GFCI protection

Quote:
Originally Posted by kwood View Post
You are correct John! Because of the advent of stackable wash machine and dryers it is next to impossible to plug into some but I still mention they should have GFCI protection within 6 feet of a sink.
Guess why?
You've got me Kevin. Why.
Reply With Quote
  #13  
Old 1/19/13, 10:41 PM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,816
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI protection

On many occasions you find that someone uses the bottom portion to plug in an extension cord. That cord generally is under the sink ready to do its duty. At least if they plug it into a GFCI receptacle it will protect someone if used for a Hair dryer, humidifier or any type of appliance other than Washmachine.
That being said there should be one on the wall for Ironing purposes located high beside the sink. This is a judgement call depending on where the GFCI would be located IMO.
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/20/13, 11:18 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,818
Default Re: GFCI protection

Quote:
Originally Posted by kwood View Post
This is a judgement call depending on where the GFCI would be located IMO.
It is not a judgement call. The code is very specific as to where they are required.

I can't, for the life of me, understand why a hairdryer would be used in the laundry room. I think that's the same argument you made about the closet...



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 1/20/13, 11:26 AM
kwood kwood is offline
Banned
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 11,816
Please Note: kwood is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI protection

Yes sir and I did ask about it!
CODE is CODE if you live by it you will eventually die from it if you rise above you have a better chance of staying alive.
End of argument.
I think someone on another MB said The minimum codes are a stepping stone to reach for a better solution or something like that.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Just found this about GFCI protection..just some FYI rhensel Electrical Inspections 10 6/24/12 12:51 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 10:51 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 9:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 1:29 PM
double GFCI protection rperkerewicz Electrical Inspections 11 10/9/07 7:06 PM

All times are GMT -4. The time now is 6:16 PM.
no new posts