  #1  
Old 12/13/06, 4:30 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default GFCI question

Just finished an inspection on a home built in '91. The bathrooms both have countertop receptacles - and are on the same circuit as the GFCI in the garage. If the bathroom outlet trips, you have to go to the garage GFCI and reset it. Is this acceptable?
Thanks.



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.

Last edited by acox; 12/13/06 at 4:34 PM..
Reply With Quote
  #2  
Old 12/13/06, 4:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: GFCI question

I think it is permitted but that doesn't make it "best practice".
At least your in FL where the garage floors stay warm.
No worse than using a GFCI breaker in the distribution panel which is also allowed.
Reply With Quote
  #3  
Old 12/13/06, 5:19 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCI question

Are you talking about todays wiring..no it is not permitted since 1996....but then again if the home is prior to that time frame it is really something that is not retroactive....you cant turn BACK the code....

As long as it is GFCI protected I would not worry about it to be honest with you.....but today it simply can't be done that way.



Paul W. Abernathy
Reply With Quote
  #4  
Old 12/13/06, 7:09 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: GFCI question

Thanks for clarifying the appropriate dates Paul.
Reply With Quote
  #5  
Old 12/13/06, 9:35 PM
Ralph Morella Ralph Morella is offline
New User
 
Join Date: Nov 2006
Location: Marietta, GA
Posts: 17
Please Note: Ralph Morella is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI question

Quote:
Originally Posted by acox
Just finished an inspection on a home built in '91. The bathrooms both have countertop receptacles - and are on the same circuit as the GFCI in the garage. If the bathroom outlet trips, you have to go to the garage GFCI and reset it. Is this acceptable?
Thanks.
I almost thought you were inspecting my house. That is exactly how mine is set up. My home was built in 1992.

We had a power outage a year ago that tripped the GFCI..I went all over the house checking all the GFCIs before remembering there was one in the garage and, yup..that was the right GFCI for the bathroom outlets.

I wholeheartledly believe we should be identifying what outlets are supported by what GFCI for our clients.

Ralph
Reply With Quote
  #6  
Old 12/13/06, 9:58 PM
Andrew Cox Andrew Cox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,064
Default Re: GFCI question

I'm not worried about it, but I did mention it to the client. He is a retired plumber, and his son is an electrician. I'm going to write it up as acceptable prior to 1996, but not the recommended practice today. He said he wasn't too thrilled with it, and would have his son fix it. I told him I was more concerned that there was a GFCI, and he knew where to reset it! He agreed.
Thanks for the help.



Andy Cox
http://www.CoxInspections.com
Kissimmee, FL
You’re Your Own Job Security.
Reply With Quote
  #7  
Old 12/14/06, 9:47 AM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: GFCI question

I typically write it up as nuisance design installation.
My friends in the Electrical industry tell me they usually design the GFCI circuitry as follows-

Kitchen Area / Min.of 2 circuits, resetable within the area
Bath(s)/ 1 circuit, resetable, w/ max.3 extensions or individual, resetable within each bath
Exterior(s)/ 1 circuit, resetable, w/ max.3 extensions or individual, resetable at each waterproof location
Garage/Basement/ 1 circuit, resetable in each location (extensions within, optional)
Other Area(s)/ as design requires

These are design standards in our area(s). NEC and/or local codes can/will override.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI Question jvogan Electrical Inspections 4 8/25/07 2:28 PM
Another GFCI Question rnewland Electrical Inspections 2 6/16/07 2:25 PM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical Inspections 13 2/8/07 1:18 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM