Default GFCI Question

During an inspection today I tripped the GFCI in the Bathroom upstairs. When It would not reset. I went down to the GFCI in the downstairs bathroom and it was also tripped. I reset it there. When I went back upstairs I could then reset that one. I tested this several times with the same outcome. Is this a problem?



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
  #2  
Old 2/4/06, 11:14 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

yes. if you have more than one GFI in line with each other than the latter cancels the first and the first protects the ladder. so i would recommend removing the outlet down stream, and the whole circut still be protected by the upstream outlet and negate the need for the second one. or so thay say.
Reply With Quote
  #3  
Old 2/4/06, 11:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: GFCI Question

Problem? No.

Nuisance? Yes.

Redundancy is not necessarily a problem.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 2/4/06, 11:46 PM
gporter's Avatar
gporter gporter is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Orlando, fl
Posts: 3,281
Default Re: GFCI Question

Thanks



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
  #5  
Old 2/4/06, 11:46 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

not a "safty" or "code" or "fire" problem. nuisance, yes, and i think that a nuisance is a problem. thou you are right Jeff, by that it doesn't HAVE to be fixed, but i always recommend it.
Reply With Quote
  #6  
Old 2/5/06, 12:48 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: GFCI Question

As do I. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 2/5/06, 1:18 AM
rmoore's Avatar
rmoore rmoore is offline
Active Poster
 
Join Date: Feb 2004
Location: Seattle, WA
Posts: 113
Please Note: rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

Had to put this in a report just last week...(older home...pre "bathroom code")

Improve: The GFCI receptacle at the west side of the roof deck is fed by the GFCI receptacle at the east side of the roof deck which in turn is fed from the GFCI receptacle at the master bathroom vanities. There is nothing inherently wrong with this arrangement (although new code would require the deck to be on a separate circuit). However, it is “overkill” and a little confusing. In the current configuration the master bathroom GFCI is all that is needed and you could remove the GFCI’s at the deck and replace them with normal receptacles.

As others said...not a safety issue, but a probable nuisance.
Reply With Quote
  #8  
Old 2/5/06, 10:16 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

Shows it was installed by a non professional. If they wanted an additional GFCI in the other bath, they should move the load wires on the first one to the line side.
Reply With Quote
  #9  
Old 2/5/06, 2:47 PM
rmoore's Avatar
rmoore rmoore is offline
Active Poster
 
Join Date: Feb 2004
Location: Seattle, WA
Posts: 113
Please Note: rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Question Re: GFCI Question

Quote:
Originally Posted by brian winkle
Shows it was installed by a non professional. If they wanted an additional GFCI in the other bath, they should move the load wires on the first one to the line side.
Where's the smiley to show that you are just kidding? That's just wrong!
Reply With Quote
  #10  
Old 2/5/06, 3:42 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

what I meant was, the original config most likely had one gfi to serve both baths. Someone decides they want a gfi in each bath for whatever reason. Fine, but now open the first gfi and move the load wires to the line side so you're only protecting that location, your new one will protect the second bath and when one trips you won't have to run back and forth to reset everything. If there are additional loads needing protection they can feed from the second receptacle, or they too can have point of use protection by adding another gfi.
Reply With Quote
  #11  
Old 2/6/06, 7:06 PM
rmoore's Avatar
rmoore rmoore is offline
Active Poster
 
Join Date: Feb 2004
Location: Seattle, WA
Posts: 113
Please Note: rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

Brian...if you reverse the line/load on the first GFCI, then that receptacle will only protect outlets downsteam. The fisrt GFCI receptacle itself will have NO PROTECTION! It will be hot even when tripped. Actually, if it's a newer (semi-idiot-proof) GFCI, you also wouldn't be able to reset it once tripped.

It's possible that I'm misunderstanding your use of the word "first". Probably better to use upstream and downstream. But in any case...

If you want to get rid of a GFCI that is protected from elsewhere, fine. Replace it with a normal receptacle. Suggesting that someone should deliberately reverse-wire a GFCI is wrong, wrong, wrong!

Last edited by rmoore; 2/6/06 at 7:15 PM..
Reply With Quote
  #12  
Old 2/6/06, 8:37 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

No I never said to reverse the line & load. I said to move the downstream load wires to the line side along with the incoming line, in other words, leave the load terminals empty. Then the downstream receptacle can be replaced with a GFCI and each will trip individually without affecting the other.
Reply With Quote
  #13  
Old 2/6/06, 8:52 PM
rmoore's Avatar
rmoore rmoore is offline
Active Poster
 
Join Date: Feb 2004
Location: Seattle, WA
Posts: 113
Please Note: rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

OK...got it. Sorry for the misunderstanding and the lecture.
Reply With Quote
  #14  
Old 2/6/06, 9:21 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

no problemo senior....as an electrician I am always on the lookout for any clues as to who did the work. When I see evidence of non professional work it tips me off to check things closely and to be extra careful, non professional methods can be dangerous when disassembling!
I guess as a home inspector when you guys see evidence of poor workmanship it would be a clue to recommend furthur evaluation.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Chicago GFCI question mthomas2 Electrical Inspections 10 8/28/07 9:37 AM
GFCI Question jvogan Electrical Inspections 4 8/25/07 2:28 PM
Another GFCI Question rnewland Electrical Inspections 2 6/16/07 2:25 PM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical Inspections 13 2/8/07 1:18 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM


All times are GMT -4. The time now is 3:04 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts