Default GFCI Question

I know there is no functional reason for doing it but can anyone tell me specifically what the electrical code states about 2 GFCI outlets being wired on the same branch circuit. I've been flagging it in the building I'm working in but the electrican is telling the GC it's O.K.

Last edited by aquarles; 5/1/07 at 12:34 PM..
Reply With Quote
  #2  
Old 5/1/07, 3:32 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

More than one GFCI receptacle on a branch circuit is an acceptable practice. As a matter of fact, one GFCI receptacle installed upstream can protect other receptacles in the same circuit. If you have been flagging bathrooms which are sharing one GFCI circuit, then you are right to do so, since common sense says that Mom and Sis using hair dryers at the same time will cause nuisance tripping. NEC says, one each for the kitchen, laundry, each bath, exterior, and garage. Sometimes I step out there when I don't have "the book" handy, like right now, so maybe someone can step in and confirm the above...it may be ok to combine exterior and garage on one circuit.
Reply With Quote
  #3  
Old 5/1/07, 4:37 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: GFCI Question

Quote:
Originally Posted by jbreazeale
If you have been flagging bathrooms which are sharing one GFCI circuit, then you are right to do so,
Actually, that is not correct. Bathrooms can (and commonly do) share a GFCI protected circuit. The NEC does not say "one each" for the areas you listed. It simply says that these circuits shall have GFCI protection.

The original question asks about multiple GFCI receptacles on a single circuit, to which the NEC makes no comment. Other than creating a nuisance, there is nothing that prohibits this practice.

I will often recommend removing additional GFCI receptacles when I run across this condition.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 5/1/07, 4:45 PM
aquarles aquarles is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Upper Marlboro, MD
Posts: 6
Default Re: GFCI Question

Thank you both for your response.

The particular issue was in the master bathroom. There are only two outlets and they are both GFCIs and they are on the same circuit.
Reply With Quote
  #5  
Old 5/1/07, 5:14 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

Quote:
Originally Posted by aquarles
The particular issue was in the master bathroom. There are only two outlets and they are both GFCIs and they are on the same circuit.
No violation or hazard... just wasteful of material. No big deal. It is possible that even though they are both on the same circuit, they are each "pigtailed". This way, if one GFCI tripped or failed, the other GFCI would remain functional. If the second GFCI is, indeed, installed downstream of the first (on the load side), it's just wasteful but not hazardous.
Reply With Quote
  #6  
Old 5/1/07, 5:23 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

How about four GFIs on one circuit?
My home was wired with two bath receptacles and two outside receptacles on one GFI breaker. Not the best layout but perfectly legal for the day.

I did not like the thought of going out to the garage to reset a tripped GFI breaker so I installed GFI devices, all wired to the line side, at each location.
Reply With Quote
  #7  
Old 5/1/07, 10:46 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

Ocassionally you will see one gfci protecting another, is this what you mean? I heard once that this setup will cause nuisance tripping, but I have never verified it. It is usually done in error by a non qualified installer.
Reply With Quote
  #8  
Old 5/2/07, 6:52 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

Quote:
Originally Posted by brian winkle
Ocassionally you will see one gfci protecting another, is this what you mean? I heard once that this setup will cause nuisance tripping, but I have never verified it. It is usually done in error by a non qualified installer.
It won't cause nuisance tripping, but it certainly doubles your possible chances of having a nuisance trip, since there's twice as many GFCI devices protecting that second receptacle. When I find "double GFCI protection", there's usually already a GFCI breaker in the panel, and the homeowner installed GFCI receptacles in the common places, thinking they were making some enhancement. Many people don't realize that GFCI breakers exist, and they're used to seeing the more popular point-of-use GFCI protection.
Reply With Quote
  #9  
Old 5/2/07, 11:12 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

I use "doubled up" protection all the time these days. I an the new dock master in my community and when I am working on the docks I use homeowner's outdoor receptacles for my power tools but I always use my GFCI adapter on the cord.
Reply With Quote
  #10  
Old 5/2/07, 5:36 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

Quote:
Originally Posted by Greg Fretwell
I use "doubled up" protection all the time these days. I an the new dock master in my community and when I am working on the docks I use homeowner's outdoor receptacles for my power tools but I always use my GFCI adapter on the cord.
In the construction trades, it is company policy for many companies that their workers use the GFCI pigtails at the head end of their cords. This is without regard to whether the workman believes he is plugged into a GFCI protected receptacle. Makes good sense, particularly when it's your life on the line. You can be reasonably sure of the condition and status of your own GFCI pigtail cord, but you can't always be certain of the condition of an existing GFCI receptacle or bother to take the time to check. Use you own, and you're covered.

Reply With Quote
  #11  
Old 5/2/07, 6:05 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

"You can be reasonably sure of the condition and status of your own GFCI pigtail cord, but you can't always be certain of the condition of an existing GFCI receptacle or bother to take the time to check. Use you own, and you're covered."

Good advice, Mark.

With 23+ years in inspection, I've generated my own report and appendix. In the Appendix GFCI section, I now recommend that before using a GFCI protected receptacle, trip and reset it a couple times, even if you have to walk to the panel or other location to do it.

Why? Over the years, as they get older, I find more and more not tripping (especially outdoor units) when tested although they show themselves to be energized and properly wired with my Suretest. It must be internal corrosion seizing up the trip mechanism. Just because there's power does not mean the unit will trip when needed.

The other thing that happens is that they will trip once and not be able to be reset.......maybe close to a failure waiting to happen.

That's why the manufacturer's say: TEST MONTHLY
Reply With Quote
  #12  
Old 5/2/07, 6:59 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCI Question

Quote:
Originally Posted by Speedy Petey
but perfectly legal for the day.
Thats the OPTIMUM verbage for that statement...lol...legal for the DAY...or that period in time...



Paul W. Abernathy
Reply With Quote
  #13  
Old 5/2/07, 7:16 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

Quote:
Originally Posted by pabernathy
Thats the OPTIMUM verbage for that statement...lol...legal for the DAY...or that period in time...
Customers look at me goofy when I show up to troubleshoot a non-working garage or outdoor receptacle and I ask them to show me where all their bathrooms are. Back in the day, the GFCI that was protecting the whole shebang could be anywhere. As was pointed out, it was legal to do so then.
Reply With Quote
  #14  
Old 5/2/07, 7:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCI Question

Yep....and why I said......Legal for the Day or that period in time....I was not yankin on Speedy...I AGREED with him.

I see this all the time as well....



Paul W. Abernathy
Reply With Quote
  #15  
Old 5/2/07, 7:44 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Question

Quote:
Originally Posted by pabernathy
Yep....and why I said......Legal for the Day or that period in time....I was not yankin on Speedy...I AGREED with him.
..
I know, I was just adding some extra commentary. I have a fat head, and if I don't type a certain amount of information each day, my head will explode. It's just a health concern.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GFCI Question jvogan Electrical Inspections 4 8/25/07 2:28 PM
Another GFCI Question rnewland Electrical Inspections 2 6/16/07 2:25 PM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical Inspections 13 2/8/07 1:18 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM
GFCI Question gporter Electrical Inspections 13 2/6/06 9:21 PM


All times are GMT -4. The time now is 9:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts