Default GFCI Question

At todays inspection I had GFCI outlets on both sides of the kitchen sink. Each had it's own test/ reset buttons. Using my tester, I tested the one on the right and it worked fine. When I tested the one on the left, it tripped the one on the right. Seems like it would have tripped itself. Is this a common setup or is it a defect? When I think about it, it doesn't seem to be a problem. First time I ran into this one.



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Reply With Quote
Find an InterNACHI certified Rhode Island Home Inspector (and anywhere else in North America)
  #2  
Old 10/6/09, 12:31 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: GFCI Question

As long as one tripped somewhere I wouldn't be concerned.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 10/6/09, 12:41 AM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 1,624
Default Re: GFCI Question

Quote:
Originally Posted by jfunderburk View Post
As long as one tripped somewhere I wouldn't be concerned.
Thx Joe. It did its job



Robert Newland
Tyrone, GA 30290
NACHI05101290

http://www.CertifiedHI.com
http://www.HomeInspectorTyroneGa.com

Reply With Quote
  #4  
Old 10/6/09, 12:43 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: GFCI Question

I've run into similar situations in the past. The trouble seems to be in resetting them.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #5  
Old 10/6/09, 1:36 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 448
Default Re: GFCI Question

Probably just a brain-fart when they installed it. They just slaved a GFI off another GFI. Could've saved $10.00 and installed a regular receptacle.

Jeff



Jeff Wicklander
Corwick Home Services
224-715-0457
Reply With Quote
  #6  
Old 10/6/09, 1:42 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 690
Default Re: GFCI Question

Quote:
Originally Posted by jwicklander View Post
Probably just a brain-fart when they installed it. They just slaved a GFI off another GFI. Could've saved $10.00 and installed a regular receptacle.

Jeff
Yep, second one is redundant. Either one could trip first when the downstream device is tested.
Reply With Quote
  #7  
Old 10/6/09, 1:48 AM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is online now
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 2,826
Send a message via AIM to sstanczyk
Default Re: GFCI Question

How old is the house? With modern homes there are supposed to be 2 small appliance circuits. If there are only 2 GFCI's and they are both on the same circuit, does that mean there is only 1 circuit or is the 2nd circuit not GFCI protected or is there a 3rd GFCI in the kitchen protecting the 2nd circuit?




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
Structural Pest Inspectors License # 71043
Vice-President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #8  
Old 10/6/09, 2:16 AM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: GFCI Question

A tip I have learned the hard way:

If you trip a GFCI and it won't reset, there is a chance that you tripped a second, redundant GFCI upstream. If they both trip at the same time, the downstream one won't reset until the upstream one is reset.
That is one reason it is best to use the test button on the receptacle instead of the one on your tester.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #9  
Old 10/6/09, 12:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: GFCI Question

Quote:
Originally Posted by rbrady View Post
That is one reason it is best to use the test button on the receptacle instead of the one on your tester.
Sorry to disagree.

Although most manufacturers say that this is how it should be done, I have run across many GFCI's that will "trip" with their test button, but will remain energized.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 10/6/09, 12:32 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: GFCI Question

Quote:
Originally Posted by jpope View Post
Although most manufacturers say that this is how it should be done, I have run across many GFCI's that will "trip" with their test button, but will remain energized.
Will these same GFCI's de-energize when tripped with the external tester? I always try my tester if it doesn't trip with the test button, but I can't recall one that worked with one and not the other.

My main point in using the test button on the receptacle was to avoid tripping a redundent GFCI, which you may not be aware of, then trying to chase it down. I have had that happen a few times.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #11  
Old 10/6/09, 12:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: GFCI Question

No, they don't de-energize even though the test button "trips." I understand the nuisance of redundant GFCI's, and I report them as a "nuisance."

I'm saying, make sure you've got a tester plugged into the receptacle to check for voltage - just because the internal tester trips, doesn't mean the GFCI is functional.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #12  
Old 10/6/09, 12:57 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: GFCI Question

Quote:
Originally Posted by jpope View Post
No, they don't de-energize even though the test button "trips." I understand the nuisance of redundant GFCI's, and I report them as a "nuisance."

I'm saying, make sure you've got a tester plugged into the receptacle to check for voltage - just because the internal tester trips, doesn't mean the GFCI is functional.
I agree.
I always have my tester/indicator plugged in when I push the receptacle test button. It can make it difficult to get to the button.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Installing GFCI in garage with no ground cyezza Electrical 53 11/30/07 6:05 PM
Ungrounded GFCI srinner Electrical 29 11/30/07 11:15 AM
GFCI Question mdavis5 Electrical 4 9/12/07 9:22 PM
Chicago GFCI question mthomas2 Electrical 10 8/28/07 10:37 AM
GFCI Question jvogan Electrical 4 8/25/07 3:28 PM


All times are GMT -4. The time now is 5:03 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts