I tested a GFCI installed in the garage. The down stair's bath receptacle
was also tied to it. It took 20 min to reset upon being tripped. Is this acceptable? David An Ounce of prevention is better than a pound of cure :} |
| Need a home inspection in Michigan? Check out InterNACHI's listing of Michigan certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Assuming the load that tripped the GFCI is no longer applied, it should reset immediately. If not, report it as defective.
Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#3
|
||||
|
||||
|
20 min to reset, does that include time it took you to find it?
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#4
|
||||
|
||||
|
Quote:
E3703.4 Bathroom branch circuits. A minimum of one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets. Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with Section E3702. Commentary: This section requires a dedicated branch circuit for the bathroom receptacle outlet(s). Section E3901.6 provides rules for the location of the receptacle(s). Two choices are available for the branch circuit serving the bathroom(s) in the house. 1. One 20-ampere-rated circuit may serve the required receptacle(s) in all the bathrooms in the house. In this case, no other outlets may be served by this circuit. The bathroom lighting and any fan or heat lamps would be served by a distinct general purpose branch circuit. 2. A 20-ampere circuit may serve only one bathroom. For additional bathrooms in the house, additional separate circuits would be run. The one circuit for the single bathroom supplies the required receptacle(s) and is also permitted to serve lighting and equipment in the bathroom such as an exhaust fan and/or heat lamp. Because this circuit is subject to the provisions of Section E3702, the load of the other equipment can be a maximum of 50 percent of the rating of the branch circuit. The bathroom receptacle must be Ground Fault Interrupters (GFCI) protected, but lighting and other equipment is not required to be GFCI protected unless otherwise stated as a condition of the listing of a fixture or equipment. Some electricians supply the luminaires and fans in a bathroom from a GFCI protected circuit to provide additional safety for the occupants who come in contact with the luminaires, fans and switches. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#5
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
That section posted by JF is the current requirement. Back in the 80s it was common for one GFI to protect areas outside the bathroom like the exterior and garage receptacles. This was fine at the time.
|
|
#6
|
||||
|
||||
|
Quote:
Thanks An Ounce of prevention is better than a pound of cure :} |
|
#7
|
||||
|
||||
|
Quote:
An Ounce of prevention is better than a pound of cure :} |
|
#8
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
David, you ignored the part that this was acceptable under certain older code editions. You may be writing up something unnecessararily. It would depend on the code cycle at the time of the install.
|
|
#9
|
||||
|
||||
|
Quote:
Thanks Jim. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#10
|
||||
|
||||
|
But that does not take away from the fact that the unit may be defective, thus, reportable.
Location is secondary to function. If it is installed, it must function properly. Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#11
|
|||
|
|||
|
I have had a few hesitate to reset. I do not know why; maybe gunk or paint around the reset button. They seem to be older models. I often recommend updating to newer devices as a precaution. New GFCI are perhaps better than old and old is better than none. Interesting Wiki article.
http://en.wikipedia.org/wiki/GFCI I did not proof it but it was an interesting read. |
|
#12
|
|||
|
|||
|
Product Safety Tips:
GFCIs -- A SMALL INVESTMENT, A BIG LIFESAVER UL Recommends Regular Testing of GFCIs December 20, 2003: Underwriters Laboratories periodically revises requirements in its Standards for Safety to harmonize with international requirements, address code and safety issues, and accommodate new product developments as applicable. UL has adopted new and revised requirements for Ground-Fault Circuit-Interrupters (GFCIs) that become effective January 1, 2003. Among others, these requirements include enhanced requirements for immunity to voltage surges, resistance to moisture and corrosion, reverse line-load miswiring, and resistance to environmental noise. Though products meeting these revised requirements will soon enter the marketplace, they are not required to have any special markings to distinguish them from models made prior to January 1, 2003. Models of GFCIs Listed by UL that were manufactured and labeled prior to January 1, 2003 still may appear in the marketplace after January 1, 2003, and until such time as old stocks of GFCIs become exhausted. Ground fault circuit interrupters (GFCI) can help prevent electrocution inside and outside the home. GFCIs are an effective means of protecting against electrical shock, however, they must be tested regularly -- UL recommends once a month -- to verify they are working properly. "Ground faults" are often the result of damaged appliance cords or consumers who use electrical products in wet environments, such as bathrooms or swimming pool decks. By installing GFCIs in every home in the United States, the U.S. Product Safety Commission (CPSC) estimates that more than two-thirds of the approximately 300 electrocutions occurring each year could be prevented. The advantage of using GFCIs is that they detect even those amounts of electricity too small for your fuse or circuit breaker to activate and shut off the circuit. Like all products, GFCIs can be damaged. GFCIs damaged by lightning or electrical surges may fail to provide adequate protection. A simple test once a month and after any violent thunderstorm should be conducted. To properly test GFCI receptacles in your home:
"GFCIs are proven lifesavers, however, consumers need to take a few minutes each month to do this simple test. By taking action, you can help protect your family from the risk of electric shock," says John Drengenberg, UL Consumer Affairs Manager. Several types of GFCIs may be installed in/around your home. Look for the UL Mark on GFCIs when purchasing them or when specifying the product to your electrician. Wall Receptacle GFCI -- This type of GFCI -- the most widely used -- fits into a standard outlet and protects against ground faults whenever an electrical product is plugged into the outlet. Wall receptacle GFCIs are most often installed in kitchens, bath and laundry rooms, and out-of-doors where water and electricity are most likely to be in close proximity. Circuit Breaker GFCI -- In homes equipped with circuit breakers, this type of GFCI may be installed in a panel box to give protection to selected circuits. Circuit breaker GFCIs should also be checked monthly. Keep in mind that the test will disconnect power to all lights and appliances on the circuit. Portable GFCI -- A portable GFCI requires no special knowledge or equipment to install. One type contains the GFCI circuitry in a self-contained enclosure with plug blades in the back and receptacle slots in the front. It can then be plugged into a receptacle, and the electrical products are plugged into the GFCI. Another type of portable GFCI is an extension cord combined with a GFCI. It adds flexibility in using receptacles that are not protected by GFCIs. Portable GFCIs should only be used on a temporary basis and should be tested prior to every use. Underwriters Laboratories Inc. (UL) is an independent, not-for-profit product safety certification organization that has been testing products for more than a century. More than 16 billion products bearing the UL Mark enter the marketplace every year. An oldie but goodie.... Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Four Point Inspection Question (Electrical) | khunt | Florida Inspectors | 43 | 12/18/11 4:26 PM |
| GFCI won't trip by tester | rstufflebeem | Electrical Inspections | 22 | 3/22/08 8:10 PM |
| GFCI Question | mdavis5 | Electrical Inspections | 4 | 9/12/07 8:22 PM |
| Chicago GFCI question | mthomas2 | Electrical Inspections | 10 | 8/28/07 9:37 AM |
| UL Information about Testing of GFCIs | jtedesco1 | Electrical Inspections | 0 | 2/5/06 4:38 PM |