Default GFCI Show Hot/Neutral Reverse

Hey Guys-

This was on an older house that had some of the electrical re-done. New panels that were all romex but half the receptacles in the house had no grounds. On this exterior GFCI, the tester showed it had a ground. But when I pushed the button on the tester to trip it, the lights switched to Hot/Neutral Reverse and would not trip. When I pushed the test button on the GFCI it tripped fine. Does that mean it has a false ground? Thanks.

Kenny
Attached Thumbnails
gfci-show-hot-neutral-reverse-img_7616.jpg   gfci-show-hot-neutral-reverse-img_7617.jpg  



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/5/10, 3:03 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: GFCI Show Hot/Neutral Reverse

Probably.
Reply With Quote
  #3  
Old 5/5/10, 3:52 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: GFCI Show Hot/Neutral Reverse

Not a false ground, NO ground. Your three-light tester cannot trip an ungrounded GFCI. Disregard the light-display when you pushed the test button.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 5/5/10, 3:55 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: GFCI Show Hot/Neutral Reverse

If it's wired with the older 2-conductor cable but on a GFCI, it's okay correct? But if it's wired with a false ground it's incorrect? Why?

I can understand a false ground on a standard 3-prong receptacle being wrong since it gives a false sense of grounding. But on a GFCI, does it make a difference?

Hope that makes sense...thanks.

Kenny



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #5  
Old 5/5/10, 4:41 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Show Hot/Neutral Reverse

Quote:
Originally Posted by krigler View Post
If it's wired with the older 2-conductor cable but on a GFCI, it's okay correct? But if it's wired with a false ground it's incorrect? Why?

I can understand a false ground on a standard 3-prong receptacle being wrong since it gives a false sense of grounding. But on a GFCI, does it make a difference?

Hope that makes sense...thanks.Kenny
Yes a GFCI receptacle can be used a replacement for an ungrounded receptacle. According to the NEC the ungrounded device should have a sticker that states "no equipment ground".

Quote:
406.3(3) Non–Grounding-Type Receptacles. Where attachment to an equipment grounding conductor does not exist in the receptacle enclosure, the installation shall comply with (D)(3)(a), (D)(3)(b), or (D)(3)(c).
(a) A non–grounding-type receptacle(s) shall be permitted to be replaced with another non–grounding-type receptacle(s).
(b) A non–grounding-type receptacle(s) shall be permitted to be replaced with a ground-fault circuit interrupter-type of receptacle(s). These receptacles shall be marked “No Equipment Ground.” An equipment grounding conductor shall not be connected from the ground-fault circuit-interrupter-type receptacle to any outlet supplied from the ground-fault circuit-interrupter receptacle.
One other thing to note, had you been grounded and contacting bare metal you could have received a shock by holding open the metallic cover and pressing the test button.
Reply With Quote
  #6  
Old 5/5/10, 4:53 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: GFCI Show Hot/Neutral Reverse

Quote:
Originally Posted by jpope View Post
Not a false ground, NO ground. Your three-light tester cannot trip an ungrounded GFCI. Disregard the light-display when you pushed the test button.
I'm with you Jeff that the tester cannot trip an ungrounded GFCI. But usually when there is no ground, only the middle light is on. In this case however, both the middle and right lights were on indicating that there was a ground.



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #7  
Old 5/5/10, 7:02 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Show Hot/Neutral Reverse

Not sure if this is germane to this example, but. To the OP, are you aware of what a bootleg ground is or the dangers associated with them?

A bootleg ground is where a jumper is installed between the neutral and grounding terminal. It will fool a 3 light tester and show as grounded. The danger comes as there is now neutral current on the metallic path all the way back to the panel.
Reply With Quote
  #8  
Old 5/5/10, 10:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: GFCI Show Hot/Neutral Reverse

My bad, I mis-read your post. I'd say the GFCI is defective or mis-wired. Even a false ground will trip the GFCI.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 5/6/10, 1:54 PM
Kenny Rigler Kenny Rigler is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Hays, KS
Posts: 255
Default Re: GFCI Show Hot/Neutral Reverse

Is there a difference between a false ground and a bootleg?



Rigler Home Inspections
Hays, KS 67601
785-656-0272
Reply With Quote
  #10  
Old 5/6/10, 2:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: GFCI Show Hot/Neutral Reverse

No difference. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 5/6/10, 6:31 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: GFCI Show Hot/Neutral Reverse

Kenny -

IMHO, you're thinking too hard. Like JP said, "It be broke OR not doing its thing properly. Service and correct".

Then move on down the road ..................
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM


All times are GMT -4. The time now is 9:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts